I'm trying to determine which wires to connect to which

Customer Question
Hello I'm trying to...

Hello I'm trying to determine which wires to connect to which connectors on my new thermostat

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Specific to the wiring, that's my theory I'm I have white rodgers type 1E35-910 and I'm switching to a honeywell lyric T5

Contractor's Assistant: Do you plan on doing the work yourself?

Yes until I troubleshoot as far as I can go

Contractor's Assistant: Anything else we should know to help you best?

On the white rodgers I have green connected on top left, red on bottom left and white on bottom right. I'm trying to determine if two or all of them are swapped that would cause the honeywell thermostat not to power on.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
9/6/2017
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago
Webb-Guy
Webb-Guy, HVAC Mechanic
Category: HVAC
Satisfied Customers: 3,026
Experience: maitenance tech at casto
Verified

Hello, and welcome to just answer. My name is ***** ***** I will be the one to assist you. Scroll down to the bottom of this link . You are needing to find your ground wire these instructions may help

https://www.lowes.com/pd/Honeywell-Black-Lyric-T5-Thermostat-with-Built-In-WiFi/1000142915

Ask Your Own HVAC Question
Customer reply replied 8 months ago
ok I believe the white wire is the ground wire
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

ok use the diagram at the bottom of that link to make sure everything is in its place and let me know if its powers on.

Ask Your Own HVAC Question
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

if so Please note that we here at JustAnswer are on an honor system. I am only credited for my time in the event you rate with 3-5 stars at the top. I do hope that I have earned a 5 star rating from you today. Rating does not stop you from getting back to me in the event you need me.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
ok do I need to do anything special with an R5 wire?
Customer reply replied 8 months ago
This thing is not powering on
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

you should not need to and this may be helpful as well

https://inspectapedia.com/heat/White_Rodgers_Thermostat_Wiring_Guide.php

also note that your new thermostat does not accept jumper wires

Ask Your Own HVAC Question
Customer reply replied 8 months ago
ok so I have white green and red, I've plugged them into all the right slots, the white rodgers thermostat indicates that the green was connected to a yellow connector, is it possible that my green wire needs to be plugged into the green slot?
Customer reply replied 8 months ago
sorry typo is it possible that my green wire needs to be plugged into the yellow slot?
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

that is a possibility lets give it a go let me know what happens

Ask Your Own HVAC Question
Customer reply replied 8 months ago
ok
Customer reply replied 8 months ago
no joy :(
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

I will open this up to see if anyone else may have another idea for swapping this out.

Ask Your Own HVAC Question
HVAC Technician: HvacmanSean, HVAC Technician replied 8 months ago
HvacmanSean
HvacmanSean, HVAC Technician
Category: HVAC
Satisfied Customers: 237
Experience: Owner HVAC company
Verified
Good evening,Im sean., Look forward to helping you.So I read thru everything we need to start back k at beggining. Do you have all the wires.labeled
From where they were on old thermostat ? And what wires do you have
Ask Your Own HVAC Question
Was this answer helpful?
Ask HvacmanSean Your Own Question
HvacmanSean
HvacmanSean
HvacmanSean, HVAC Technician
Category: HVAC
Satisfied Customers: 237
237 Satisfied Customers
Experience: Owner HVAC company

HvacmanSean is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a white rodgers 1F80-361. The thermostat will no longer
I have a white rodgers 1F80-361. The thermostat will no longer turn on and keeps flashing the time and 79 degrees. When I lower the temp to 75 it will not turn on. I have tried to reset it and still i… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
York P3HUD20N10401C gas furnace with White Rodgers 50A50-241
York P3HUD20N10401C gas furnace with White Rodgers 50A50-241 control board. Last Wednesday furnace would not maintain flame, cleaned flame sensor with steel wool and furnace worked fine until sometime… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
White Rodgers 1F95-1277 thermostat not working properly.
White Rodgers/Emerson 1F95-1277 thermostat has begun misbehaving. It began with the interior temp reading at "--" then the outside temp began to fluctuate. I changed the AA batteries. Now it flashes r… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
My white rodgers thermostat 4875B has only up and down
My white rodgers thermostat 4875B has only up and down buttons. How do I switch to air from heat ?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an old white rodgers thermostat that is used for air
i have an old white rodgers thermostat that is used for air conditioner it is an outside unit nothing in the house it only has three wires 1 red and 2 green want to change i with a honeywell … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a white Rodgers heat only thermostat, mod.1e78-140.
I have a white Rodgers heat only thermostat, mod.1e78-140. it is not working, does it run on batt. or is the power wired from home. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a White-Rodgers 1 F81-261 Programmable thermostat.I
I have a White-Rodgers 1 F81-261 Programmable thermostat.I want to operate it manually. Please help. It has reset at 62 degrees. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a White-Rodgers thermostat with the flap that opens
Hi, I have a White-Rodgers thermostat with the flap that opens to the menu. All of a sudden the temp of the room that the display shows on the left is not showing the temperature in Fahrenheit, but it… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My white rodgers 1f78 non-prgm thermostat won't work. The
My white rodgers 1f78 non-prgm thermostat won't work. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a White Rodgers !F-95-1291 Touch screen thermostat
I have a White Rodgers !F-95-1291 Touch screen thermostat with remote outdoor sensor. The out door reading is off by 10 degr F, too low. What's the prob? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an f8024 white rodgers, i am renting right now but
I have an f8024 white rodgers, i am renting right now but the unit worked last summer, i just replaced the batteries, but when i press the temp down button, nothing happens. … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
60 satisfied customers
I have a white/rodgers 8A05A -101 relay that I want to use
I have a white/rodgers 8A05A -101 relay that I want to use for a hot water circulating pump. The thermostat wiring is straight forward but the wiring for the 120 v is not. I have the following wires. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
How do you program a White Rodgers 1F80-361, I can't find my
How do you program a White Rodgers 1F80-361, I can't find my manual and the temperature is stuck at 69.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi, I think I have a problem with the control board on my
Hi, I think I have a problem with the control board on my York Diamond 80 gas furnace. Keep getting 3 blinks (pressure switch stuck open or closed...don't remember which). Replaced pressure switch and… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
White-Rogers thermostat is blinking the flame icon. Help
My White-Rogers thermostat is blinking the flame icon. Went away for the weekend, turned it down to 55. Came home Sunday night turned it back up to 66. Monday - gone most day, came home at night notic… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hello, I have a White Rodgers thermostat and I got a message
Hello, I have a White Rodgers thermostat and I got a message on the display that the read "Low Battery". So I changed out the 2 double AA batteries and all seemed okay; however now I have an snowflake… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
have a bad thermocouple connected to a white rodgers type 3056-2
have a bad thermocouple connected to a white rodgers type 3056-2 aoutomatic pilot switch ,oliver macleod gas fireplace model dv73wfn not made any more either is the thermocouple, any suggestions… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Trane XE 80 Gas furnace. Problem: Burners will not
I have a Trane XE 80 Gas furnace. Problem: Burners will not ignite. The pressure switch was replaced first, bad diagnosis from me, didn't need it. Then I swapped out the control board (White Rodgers 5… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x