I woke up this morning to a tripped furnace circuit breaker, I reset it and went up to the furnace and also noticed a burning smell and a humming noise.
Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 12 minutes by:
8/30/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,999
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy. When blinking and humming...is the fan turning? Is the thermostat set for a particular function?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
The fan is not turning. And the system is set to ac
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago
Thats what I thought. The module on the rear of the motor has burned out. Can you see the model number on back end of blower motor?
Ask Your Own HVAC Question
Customer reply replied 7 months ago
No. It is a tight fit between the motor and the right wall of the unit.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

Ok what has happened:

You have a variable speed motor. The motor has an end bell on the rear with a circuit board inside. This circuit board as some thermistors that have burned out. The only fix is to replace the module. It involves 2 bolts and a little wiring.

If you have a contractor do this it will run around $400-$500.

Billy

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Looking at the schematic I can see that there are two sets of wires going to the blower is there any way to isolate either one of these to stop the humming and verify that either one is the cause of the fault
Customer reply replied 7 months ago
What's the price of that unit.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

There are 2 sources of power...24v on the harness with many wires...and 120v on the harness with fewer.

You have both voltages to the motor....but it is stuck in the board.

If you have a meter I can get you a service manual. I see this daily and 99.9% is the end bell module. Without the number I asked for on motor I cannot be specific on price.

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

here is the layout

click here

The low voltage plug is on module that removes. Unplug the low voltage harness and humming will stop.

You can replace the entire motor and module but it is aprox$800-900 dollars for both

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I have a meter. And yes, one has 16 wires ...(16 wire ECM harness and one with 5 wires. A black wire of the 5 is supplied from a transformer. The other of the five are white, green, and a pink jumped wire.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

The 5 wire is constant 120v

The 16 wire is 24 volt signals determining run speed, volume, ramping etc.

see a good manual HERE

I am certain once you go through the steps you will find a bad module.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I'll go up and try this and use a mirror to find the model number.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

it may be easier to remove...take out 2 long bolts from rear and the module pulls straight off

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

I need to place this question according to status...do you need more information or are you all set?

Billy

Ask Your Own HVAC Question
Customer reply replied 7 months ago
New info. I removed the harness with 16 wires ... The humming continued. Just as an added step I reconnected that harness then removed the black lead from the five supplying high voltage to the motor... The humming continued. Then I removed the white one of the five...the humming continued... Then I removed both black and white leads in an attempt to remove all power from the motor... The humming continued. Now to the strange part, I reconnected everything and went to the wall control to turn on the unit, and viola, the blower advanced to speed the the unit blew cool air... I'm glad that it is on but I know that something both caused the elictrical burning smell, and tripped the furnace breaker. Also hopefully another symptom, I went to the neighbors unit and it hums but not as loud, is this a symptom of a pending failure. Did I reset something. What would you recommend as my next steps a voltage check, resistance check... Anything?
Customer reply replied 7 months ago
I need more time.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 7 months ago

The 2 may not be related...the hum you hear could be the 24v transformer which is live 24 hrs a day. The transformer is a small 2" square cube.

The burning smell and no blower is indicative of the motor module. Let me know how things turn out.

Ask Your Own HVAC Question
Was this answer helpful?
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,999
22,999 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Our thermostat do not work efficient after reset cool. Do we
Our thermostat do not work efficient after reset cool. Do we need reset circuit breaker? How? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
The compressor trips the circuit breaker in the house, not
the compressor trips the circuit breaker in the house, not immediately, about after 5 minutes. what are my options? can i replace only the compressor? It is a frigidare model FS3BC-042KA … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
Air Handler # NFCX3600C2 what causes the circuit breaker
Air Handler # NFCX3600C2 what causes the circuit breaker panel to fry? I replaced it once and the heat worked OK but when I tryed to run A C the board fryed again … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
I have a Trane Split System Heat Pump model #TWR030C100A2
I have a Trane Split System Heat Pump model #TWR030C100A2 that's stuck in defrost mode … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Turned off circuit breaker while furnace running ... turned
turned off circuit breaker while furnace running ... turned on circuit breaker ... furnace did not come back on ... got message system malfunction outside sensor error on carrier infinity 96. read you… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND IT RESET FOR A TIME THEN DISPLAY CAME BACK UP … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Heil CA5536VKD2, circuit breaker trips when it
i have a Heil CA5536VKD2, circuit breaker trips when it turns on compressor runs for like a second then trips bad compressor? … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,999 satisfied customers
I turned the circuit breaker off to my AC to replace a
I turned the circuit breaker off to my AC to replace a thermostat with a NEST thermostat. When finished, I turned the CB back on. No power. I put the old thermostat back on and still no power at therm… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Will a weak capacitor trip the circuit breaker. Today only
well I can tell you I took off a fan motor that had 3 wires and replaced it with one with 4 wires… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I woke up this morning to a tripped furnace circuit breaker,
I woke up this morning to a tripped furnace circuit breaker, I reset it and went up to the furnace and also noticed a burning smell and a humming noise.… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,999 satisfied customers
My HVAC is not working. The AC circuit breaker trips as soon
my HVAC is not working. The AC circuit breaker trips as soon as the, I guess, the outside unit try to start … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,514 satisfied customers
The circuit breaker keeps shutting off when the Rheem
The circuit breaker keeps shutting off when the Rheem furnance/air conditioner tries to come on. What is our problem? We just had a new capacitor put in about two weeks ago. … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
What size amp circuit breakers needed for lennox heat pump
what size amp circuit breakers needed for lennox heat pump 14hpx-036-230-21 and Lennox air handler cby25uh-036-230-10? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,106 satisfied customers
On my Model 213C A/C, I have: Reset the circuit breaker,
On my Bryant Model 213C A/C, I have: Reset the circuit breaker, Replaced the fuses, Replaced thermostat batteries, Replaced the capacitor, Replaced the circuit board. Our A/C unit is less than five ye… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
The circuit breaker that I plugged my window unit into
The circuit breaker that I plugged my window unit into wasn't labeled so it got too much voltage when I plugged it in and it seems to have blown an internal fuse. I'm trying to figure out which compon… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Circuit breaker cutting off no ac or ac will not run,
circuit breaker cutting off no ac or ac will not run … read more
HvacmanSean
HvacmanSean
Owner
HVAC
232 satisfied customers
I turned off circuit breaker to cleanup a water problem in
Greetings, I turned off circuit breaker to cleanup a water problem in my house. As I went to turn on the heat it would start up but then turned back off. Please can you send me some pictures or a link… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,999 satisfied customers
My thermastat is blank I have reset my circuit breakers
My thermastat is blank I have reset my circuit breakers although they were not tripped , taken it off wall and replaced , still no reading … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x