We have a heating/cooling system model 340MAV06100 Series D…

We have a Bryant...

We have a Bryant heating/cooling system model 340MAV06100 Series D and the blower is not working. The heat pump turns on, but not the blower. It was working this morning but shut off. We checked the breakers and all is ok. Any ideas on what to check for troubleshooting. Thank you.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Thermostat was lowered and did come on. What do we check for the filter?

Contractor's Assistant: Do you plan on doing the work yourself?

Yes, but only basic work.

Contractor's Assistant: Anything else we should know to help you best?

No thanks. Just checking if there was something simple that could be checked or reset to get it working.

Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
8/22/2017
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
Experience: Furnace, A/C and heat pump specialist.
Verified

We would need a meter to troubleshoot. If you have a meter let me know .If not you can get an inexpensive one at Walmart for about 15 bucks if you would like to troubleshoot and I would be happy to guide you.

http://www.walmart.com/ip/Innova-3300-Equus-3300-Hands-free-Digital-Multimeter/14644665

Ask Your Own HVAC Question
Customer reply replied 11 months ago
I have a meter.
Customer reply replied 11 months ago
I have a meter

First step in troubleshooting will be to call for COOL at tstat. Then remove blower panel on furnace. Hold or tape door switch in and check between the COOL terminal and the Neutral on control board where blower wires connect to see if board is sending 120vac to motor. See below

Ask Your Own HVAC Question
Customer reply replied 11 months ago
there's power

OK does your meter read microfarads (uF)? If so we will check capacitor next.If power out of board has to be a bad capacitor or motor

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Does not read in uf

If you get a meter reads capacitance turn off power unplug brown wires from cam and see if within 6% of rating.

Does cap look puffy at all?

Ask Your Own HVAC Question

Since cap is less than 10 bucks you could start by replacing it.If that doesn't solve you will need to replace motor

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Getting beyond our capabilities. We'll call a technician. Thanks for your help.

If you have further questions, please let me know.

Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.

To rate answer, please select one of the stars on the page.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
9,213 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Disconnected and reconnected honeywell basic thermostat (new
Disconnected and reconnected honeywell basic thermostat (new - 3 mo.) to do some drywall repair. On reconnect, "Cool" just flashes, LCD reads "In Recovery" and no air blows. Removed batteries, turned … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Trying to find out why my carrier heat pump stopped cooling
trying to find out why my carrier heat pump stopped cooling and is giving a system malfucntion code … read more
Michael Ferryman
Michael Ferryman
110 satisfied customers
Air conditioning system, Rheem condenser unit running, heat
Air conditioning system, Rheem condenser unit running, Bryant heat pump running, no air being blown out vents. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am installing a nest thermostat in lieu of an my
Hi I am installing a nest thermostat in lieu of an my communicating Bryant stat. I currently have ABCD labeled wires. Reading this thread, I understand I can move them in the furnace to RWYG. My quest… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have 2000 90i series HVAC. Fan running but lost heat on very
Have 2000 Bryant 90i series HVAC. Fan running but lost heat on very cold day in Boston. Getting LED light error message three green three red. Tried turning on and off by switch does not start up flam… read more
Tim Ohms
Tim Ohms
HVAC Journeyman
31 satisfied customers
My HVAC system stopped working yesterday. Here are the
Hi! My HVAC system stopped working yesterday. Here are the components: White Rodgers Thermostat 1F81-51 White Rodgers Control Module 50A51-495 Trane XL 80 The screen on the thermostat went blank. I to… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I heat system off; I have a evolution control. Haven't
I heat system off; I have Bryant a evolution control … read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
Heat pump on cooling cycle states "System malfunction - call
Heat pump on cooling cycle states "System malfunction - call technician". It's the weekend and it's hot. Can I fix or override? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Bryant plus 90 only blowing cold air. Thermostat set to auto
Bryant plus 90 only blowing cold air. Thermostat set to auto and pilot light is lit. Checked filter which husband apparently hasn't changed for some time from the looks of it. Got a bit cool last nigh… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox elite series xp14 heat pump connected to
Hello. I have a Lennox elite series xp14 heat pump connected to work in conjunction with an oil furnace. The oil furnace was serviced yesterday and now the heat pump is not working. That is, the therm… read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
My Bryant Zone Perfect Plus thermostat won't pump heat
I recently bought a house with a Bryant zone perfect plus thermostat. This is the first time I needed to use it and it won't pump heat. There are 2 zones. Both are programmed identically. The Therm is… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My Bryant Evolution T stat went blank too... I got a lot of
My Bryant Evolution T stat went blank too... I got a lot of info from the previous answers, but I was at the part of taking the face off the blower to see what the light was doing.. In the last post i… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Im having a massive amount of trouble wiring my thermostat
I'm having a massive amount of trouble wiring my thermostat (I'm sure you get this one all the time!). I have a Bryant heat pump with axillary heat. The previous thermostat (a mercury switch model) ha… read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
A/C stopped working. E1 error on thermostat. Earlier it sounded
A/C stopped working. E1 error on thermostat. Earlier it sounded like the switch was clicking off and on repeatedly. Turned it off at breaker - no change. Turned switch off - thermostat reset with same… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a Bryant 355MAV heating and cooling system. My troubleshooting
I have a Bryant 355MAV heating and cooling system. My troubleshooting LED lights that blink 2 yellow and 4 green tell me (according to the panel) that my secondary voltage fuse is open (24V) wiring (a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Have a Carrier AC system for 10 years and never got problem
Have a Carrier AC system for 10 years and never got problem before. Turned on AC this morning to warm up my house (it was cold this morning) for about an hour before smelled some burning oil smell fro… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Bryant central gas furnace that is virtually brand
We have a Bryant central gas furnace that is virtually brand new but has never worked right since we moved into our house. It will come on for a while but then shut itself down and then it will not re… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a Honeywell Chronotherm III hooked to a Trane XE1000
I have a Honeywell Chronotherm III hooked to a Trane XE1000 heat pump. We had the problem where the the heat pump kept cooling even though the temperature was lower than the thermostat setting. I turn… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x