I have a 5a fuse in a trane xr80 that keeps blowing, the…

I have a 5a...

I have a 5a fuse in a trane xr80 that keeps blowing, the board is a white-rogers

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Started about a month ago, I found the switch on the side of the furnace/blower had a bad ground, i properly grounded the wire and it worked for about 2 weeks, then the issue started again. I replaced the switch and board but still have the issue

Contractor's Assistant: Did you check the furnace's filters?

Filter is new

Contractor's Assistant: Do you plan on doing the work yourself?

Trying to, the last AC guy charged me $500 for exactly nothing the last time I had an issue

Contractor's Assistant: Anything else we should know to help you best?

Sure, the contactor was also replaced when the initial issue came up(friend in the business did that). also checked/tested the 2 wires that run from the board to the A/C(red and white i think), spliced in partial wiring to see if it was justn= cut somewhere but no luck

Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
8/16/2017
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,721
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Greetings, unplug one of the molex connectors to the board at a time, until the fuse ceases to blow, it will be that last circuit attached to the board that has the short in it.

If you unplug all of the connections to the board and the fuse still blows, then I will coach you on how to replace the board as long as you rate my input so far positively,

.

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please respect ne and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site.Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my simple answer so far positively.. and I will deliver that training and coaching to you All on the same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt,shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with troubleshooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer,if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,721
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 11 months ago
this board has a 12 pin and 4 pin connector slot, does it matter which one I pull first?
Customer reply replied 11 months ago
little more info, when the a/c is switched to off the blower works and the fuse does not blow, when I switch the a/c on is the only time it blows, should i still pull the connectors.

try it both ways, then take a close up, exceedingly well focused photo of the units wiring diagram glued to the inside of the blower access door and I will look those circuits over for you, and prescribe more tests

It sounds like the thermostat wire that runs to the outside unit is rubbing on a bare metal opening in the unit and has shorted out, that is very common. look that entire area over very closely.

We can go from here without a time limit in the morning

Ask Your Own HVAC Question
Customer reply replied 11 months ago
sounds good, I will send over the pix

use the 'add files' link next to your send button

Ask Your Own HVAC Question
Customer reply replied 11 months ago
thanks for the help, I isolated the issue in the low voltage (red/white) wires to the A/C, I ran a new wire and the unit is working fine.

Good work!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,721
9,721 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,721 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Trane XC80/XL19i system with a W/R 50v61-507
I have a Trane XC80/XL19i system with a W/R 50v61-507 control board on the furnace. initial sympton is a blown 5A low voltage (LV) fuse. If I remove the Honeywell TH8320V1008 thermostat from the wall,… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,948 satisfied customers
My heat pump won't start. the air handler in attic kicks on
my heat pump won't start. the air handler in attic kicks on and fan is blowing. have 240 volts to contactor on outside pump. 24vac to coil on contactor, both sides. I can depress contactor and fan run… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
4 months. I have 50A55-486 control board. I'm getting 120VAC
I have white rogers 50A55-486 control board. I'm getting 120VAC from 24VAC condensing unit contactor. Replaced ones 24 VAC contactor and replaced 2 control boards. They were burn out by 120VAC. Can you help? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,721 satisfied customers
I can't fine the c wire in my Trane XR80. Maybe it was cut
I can't fine the c wire in my Trane XR80. Maybe it was cut off somewhere within the furance because it was not being used. I need to connect it to the c terminal. What wire bundle could it be in? Phil… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a trane XR80 heater / AC unitl in my attic. Quite frequently
I have a trane XR80 heater / AC unitl in my attic. Quite frequently it wont kick on when it is suppose to cool and the house gets quite hot. I have to go into the attic and push on the wire on the low… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have changed over motors in my Outdoor Unit. What wires do
I have changed over motors in my Outdoor Unit. What wires do I connect to what? The old motor had only 3 wires- Yellow, BLack and Brown. THe new Dayton has Brown Purple and the Brown and Brown/White S… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Can a certified TRANE tech help me? 5V fuse keeps blowing
Can a certified TRANE tech help me? 5V fuse keeps blowing on Trane XR80 Setup: -Trane XR80 model DD1C120A9541A Furnace -Trane 2TXCC049AC3HCAA sitting on top of the XR80 (49,000 btu?) -Carrier 38TKB048… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Trane heatpump blew the 24v fuse. The fuse does not blow
My Trane heatpump blew the 24v fuse. The fuse does not blow if I disconnect the red 24v wire that goes to the outside unit, or if I go outside and unplug the control wiring connector from the outside … read more
Appliance Guru
Appliance Guru
18,166 satisfied customers
No Heat,Trane XE1100, No light on Defrost Board, replaced 24v
No Heat,Trane XE1100, No light on Defrost Board, replaced 24v transformer, Plugged Defrost board back in and smoked 24v transformer again. Replaced Defrost board and 24v transformer, still no heat and… read more
V12Tech
V12Tech
252 satisfied customers
Hello , I have a TRANE XR80 blower/furnace and a 2TTB3 Series
Hello , I have a TRANE XR80 blower/furnace and a 2TTB3 Series condenser. Just noticed this morning that condenser fan & Compressor are not comming on - but blower fan runs. I was thinking startup capa… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
hey my a/c isnt working. I found that the 5A fuse on the
hey my a/c isn't working. I found that the 5A fuse on the circuit board was blown. I replaced it and as soon as i closed the door switch it popped that one too. I can't find a short anywhere and the b… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Hi! Our Trane XR80 (TDD model) stopped working. Found the
Hi! Our Trane XR80 (TDD model) stopped working. Found the Igniter had "blown up" (there was a brown/yellow "blast pattern" on the sheet metal where it used to be - - the ceramic base for the igniter h… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
The fuse blows on the circuit board everytime on turn on the
The fuse blows on the circuit board everytime on turn on the ac on my carrier tech 2000. Please help. The circuit board is cepl130438-01. I have also tried a new honeywell thermostat and a white roger… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Trane BLU060K942BO will not heat, fan will come on and operate
Trane BLU060K942BO will not heat, fan will come on and operate but when call to heat is initiated nothing happens. I just replaced the Ignition control with a Trane (white-Rogers) CNT03776 as a kit wh… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
Our trane XR80 furnace red light was flashing continously calling
Our trane XR80 furnace red light was flashing continously calling for heat but nothing happened. Called our energy company who came out and determined we needed a new thermostat. We purchased a new ho… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an Intell Ignition D341396P01 in a Trane furnace. The
I have an Intell Ignition D341396P01 in a Trane furnace. The ignitor has burned out twice and the flame sensor has been replaced. The Trane unit was manufactured in March 2003. The unit is using propa… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Outdoor a/c unit not working Model 10 acc-024-230-02 , conductor
Outdoor a/c unit not working Model 10 acc-024-230-02 , conductor relay just clicks and there is 22 volts available. Indoor fan keeps running with thermostat connected , digital display fading disappea… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I attempted to switch my HVAC to Cooling today............It
I attempted to switch my HVAC to Cooling today............It blew the 2A fuse and the Thermosat went dark..........It did the same thing last year (Pressure went up and Blew the fusr).........I had a … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.