Evaporator water flow too low alarm keeps happening.

Evaporator water flow too...

Evaporator water flow too low alarm keeps happening. Recently cleaned coils now this. The pumps are running fine. The pressures are good on the approach. The water strainer is clean. What is this a cause of?

Contractor's Assistant: How long has this been going on? And how severe is the problem?

The system shuts down after 3-5 minutes. For about 7 days now

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

There was a power outage a week ago, then the fan vfd vfd's went into fault. I did a hard reset then fans started working. Then evap water flow too low alarm

Show More
Show Less
Ask Your Own HVAC Question
Answered in 32 minutes by:
8/7/2017
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,019
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi Ham, I'm Brian, the same tech that helped last year. Is this on the same Trane CGAM chiller you're having the problem? And, could you explain in more detail what you mean by "The pressures are good on the approach." Please?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
The manufactures specs is 5-10 degrees. I have 8.
Customer reply replied 10 months ago
Evaporator approach.
Customer reply replied 10 months ago
thanks for last year. You solved that issue...

You're welcome, glad I could help.

Since your approach is good chances are the refrigerant level is proper so that's good. I haven't pulled the manual because I wasn't sure what chiller you had but most modern chillers use a flow switch for proof of flow and the chiller's LWT and RWT temperature sensors for a FLOW TOO LOW alarm. I think I would first check both sensors for accuracy to rule in/out a faulty temperature sensor.

I'm also thinking about the VFD issue and whether it's just a coincidence or not. I can't really think of anything related unless the drive lost a parameter or setpoint and isn't running at the proper speed. Just thinking out loud here but if your chilled water pump and piping got jarred during the power issues, could a pocket of air have moved into the chilled water barrel? That could cause some low temperature or high delta T issues between the sensors. Maybe a good idea to check the chilled water barrel for air.

Offhand, I can't really think of anything else. I'll put some thought into it though and if I come up with something else, I'll post a new response.

Thanks,

Brian

Ask Your Own HVAC Question

Thanks, ***** ***** chiller. Ok, I'll fetch the manual and see if I can see anything more...

Ask Your Own HVAC Question

So, I guess I would need to know a little more about the conditions. Have you been there when you caught it going into this alarm? Since you say the approach is ok, I'm having a hard time wrapping my head around this. It appears the chiller is looking at the leaving water temperature against the saturated suction temperature for that diagnostic but that's the approach so I'm a bit confused since you say the approach is normal. What are the suction pressure and entering and leaving temperatures? What is the Delta T across the evap? What percent loaded was it? What was the outdoor temperature? Having these numbers may help me understand things better and point you in a better direction.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Fixed it. Bad temp entering water sensor.. thanks
Customer reply replied 10 months ago
It was 10 degrees out of range and rising.

That's great news! I hope I was some help. I'm really glad you got it up and running. They can be a bear to fix sometimes.

Thanks much for using Just Answer. Please remember to rate your service with me before leaving!

Best regards,

Brian

Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,019
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified
Brian HVAC Guy and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,019
1,019 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am trying to locate the evaporator coil on my ac unit and
I am trying to locate the evaporator coil on my ac unit and I'm reading I should not open the box around the unit unless the breaker for the ac is off, but there isn't a breaker labeled ac on the brea… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The head pressure slowly raises as the suction pressure
The head pressure slowly raises as the suction pressure stays steady in the cooling mode … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a 113 condenser and the suction pressure is only 15
I have a bryant 113 condenser and the suction pressure is only 15 psi and the liquid line is 198 #. is there a problem with the txv? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
On my Trane evaporator/air handler/furnace unit, the fan
On my Trane evaporator/air handler/furnace unit, the fan will not come on, though thethermostat/control panel in the thehouse … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I am replacing a evaporator on a refrigerator and I have a
I am replacing a evaporator on a refrigerator and I have a FB12 flame barrier. It has two sides and aluminum and fiberglass. There's a little sticker on the aluminum side saying do not use the side to… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My upstairs HVAC has the evaporator located in the attic.
My upstairs HVAC has the evaporator located in the attic. There are two drain lines running inside the wall to ground, one on the evaporator and one on the drip pan under the evaporator, the drip pan … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
68 satisfied customers
What would make evaporator fan motor stop and the unit to
what would make evaporator fan motor stop and the unit to freeze up … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Evaporator coil has a leak. Its a Lennox coil part number
question is Lennox coils have had issues with Leaks coil is about 6 years old i was wondering if another brand coil… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I need the BTU rating for a Heatcraft Evaporator Model
I need the BTU rating for a Heatcraft Evaporator Model ADT56AWGJ … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Today, evaporator coil froze over and i heard the outside
Today, evaporator coil froze over and i heard the outside condensor area making a louder noise. i shut the ac off when noticing this and the coil melted and the fan blows air now. i looked at the evap… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,876 satisfied customers
How much does an evaporator coil cost for Ruud Model
how much does an evaporator coil cost for Ruud Model UBHA-17J11SFGA cost? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I replaced a jazz bored today along with evaporator fan
I replaced a jazz bored today along with evaporator fan motor and I can only get the motor running if I use the ground wire to one terminal on the motor and one of the wires that has 120 V I replaced … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I need an evaporator motor for a mini split unit. Sn
I need an evaporator motor for a mini split unit. Sn 50120031-7056 What is the best way to get this? … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
I have a Gladiator Freezerator and the evaporator fan won
I have a Gladiator Freezerator and the evaporator fan won sorry won't turn off could it be the control board … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x