HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

My mach 3 rv ac keeps tripping my 10000 watt generator

Customer Question
My Coleman mach 3 rv...
My Coleman mach 3 rv ac keeps tripping my 10000 watt generator breaker. How do i fix this?
Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 8 months ago
The generator is a 10000 watt DuoMax generator. This happens on the 220 plugin on the generator. The ac unit is a Coleman Mach 3 ac unit. I ran 12/2 AWG wiring from the AC, connecting blk/blk, green/copper, why/wht. Then in the breaker box I connect the black to a 15 amp breaker, the bare copper to the ground bar and the white to the neutral bar. The cabling from the breaker box inside to the connector box outside uses 10/3 gauge copper wire. Black to the first hot post in the breaker box, red to the second hot post in the. Reader box, green to the ground bar, and white to the neutral bar. There are other circuits connected in the breaker box, however even when I remove all other circuits from the interior breaker box the ac still causes the generator circuit breaker 50 amps to trip. I need help determine what is causing this problem. Can you please assist me?
Answered in 9 hours by:
8/4/2017
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,977
Experience: Furnace, A/C and heat pump specialist.
Verified

Sounds like the issue is most likely the unit not your wiring.

Does it trip immediately when you turn ac on?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
After cranking up the generator and switching the generator breaker to on, I think turn the AC to fan for about a minute then over to low or high cool. The AC will stay on for about 4 minutes then you can here the generator rev up then eventually the 50 AMP circuit breaker on the generator throws. If I flip the circuit breaker back, the ac will stay on for about 1 minute at most.
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

First step in troubleshooting is going to be to verify the amp draw on compressor when it trips.Do you have a clamp on meter?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Not at this time but I can get one. Where on the Coleman Mach 3 would I find the compressor. Will I need to take the cover off of the top unit or should I be able to get to it from the interior?
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

You will need to remove the cover.Locate the 3 wires going to compressor and clamp one single wire at a time.Without the meter you can check a couple of things visually. Make sure the capacitor does not look swollen and make sure all three wires are secure on the compressor

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I will get the meter this afternoon. What amperage should I be looking for? The AC unit should be drawing 14.9 AMPs are full load. Also I read up that it will draw 50.4 AMPs at rotor lock up. (I dont quite know what rotor lock up means)More importantly will the wires be color coordinated to assist me with knowing which in hot and which is ground?
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

The compressor wires we want to amp are none ground.One is Common One s Run and one is start. The locked rotor indicates that the compressor is locked up, but often a weak or dead capacitor will prevent starting and cause the locked rotor amperage

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

As a rule of thumb the amp draw should run 70 to 80 per cent of RLA but never exceed the 14.9

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Am I assuming correctly that the amp draw that I measure will help determining if the capacitor is weak or dead?
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

If amp draw is high, next step s to check capacitance on the capacitor.If amp draw is normal up until it trips, that would indicate a short ether in compressor or compressor wiring. So then we would remove each wire to compressor and check each of the three terminals to ground .If we have continuity between any terminal and a known ground like a cabinet bolt,compressor is bad.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Okay I will check all this afternoon and respond back.
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

WE will go from there

Ask Your Own HVAC Question
Customer reply replied 8 months ago
ok Thanks
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Look forward to hearing back

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Our thermostat do not work efficient after reset cool. Do we
Our thermostat do not work efficient after reset cool. Do we need reset circuit breaker? How? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
The compressor trips the circuit breaker in the house, not
the compressor trips the circuit breaker in the house, not immediately, about after 5 minutes. what are my options? can i replace only the compressor? It is a frigidare model FS3BC-042KA … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
Air Handler # NFCX3600C2 what causes the circuit breaker
Air Handler # NFCX3600C2 what causes the circuit breaker panel to fry? I replaced it once and the heat worked OK but when I tryed to run A C the board fryed again … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
I have a Trane Split System Heat Pump model #TWR030C100A2
I have a Trane Split System Heat Pump model #TWR030C100A2 that's stuck in defrost mode … read more
airheatman
airheatman
HVAC Technician
8,977 satisfied customers
Turned off circuit breaker while furnace running ... turned
turned off circuit breaker while furnace running ... turned on circuit breaker ... furnace did not come back on ... got message system malfunction outside sensor error on carrier infinity 96. read you… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND IT RESET FOR A TIME THEN DISPLAY CAME BACK UP … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Heil CA5536VKD2, circuit breaker trips when it
i have a Heil CA5536VKD2, circuit breaker trips when it turns on compressor runs for like a second then trips bad compressor? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I turned the circuit breaker off to my AC to replace a
I turned the circuit breaker off to my AC to replace a thermostat with a NEST thermostat. When finished, I turned the CB back on. No power. I put the old thermostat back on and still no power at therm… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Will a weak capacitor trip the circuit breaker. Today only
well I can tell you I took off a fan motor that had 3 wires and replaced it with one with 4 wires… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I woke up this morning to a tripped furnace circuit breaker,
I woke up this morning to a tripped furnace circuit breaker, I reset it and went up to the furnace and also noticed a burning smell and a humming noise.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My HVAC is not working. The AC circuit breaker trips as soon
my HVAC is not working. The AC circuit breaker trips as soon as the, I guess, the outside unit try to start … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,514 satisfied customers
The circuit breaker keeps shutting off when the Rheem
The circuit breaker keeps shutting off when the Rheem furnance/air conditioner tries to come on. What is our problem? We just had a new capacitor put in about two weeks ago. … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
What size amp circuit breakers needed for lennox heat pump
what size amp circuit breakers needed for lennox heat pump 14hpx-036-230-21 and Lennox air handler cby25uh-036-230-10? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,106 satisfied customers
On my Model 213C A/C, I have: Reset the circuit breaker,
On my Bryant Model 213C A/C, I have: Reset the circuit breaker, Replaced the fuses, Replaced thermostat batteries, Replaced the capacitor, Replaced the circuit board. Our A/C unit is less than five ye… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
The circuit breaker that I plugged my window unit into
The circuit breaker that I plugged my window unit into wasn't labeled so it got too much voltage when I plugged it in and it seems to have blown an internal fuse. I'm trying to figure out which compon… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Circuit breaker cutting off no ac or ac will not run,
circuit breaker cutting off no ac or ac will not run … read more
HvacmanSean
HvacmanSean
Owner
HVAC
232 satisfied customers
I turned off circuit breaker to cleanup a water problem in
Greetings, I turned off circuit breaker to cleanup a water problem in my house. As I went to turn on the heat it would start up but then turned back off. Please can you send me some pictures or a link… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My thermastat is blank I have reset my circuit breakers
My thermastat is blank I have reset my circuit breakers although they were not tripped , taken it off wall and replaced , still no reading … read more
airheatman
airheatman
HVAC Technician
8,977 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x