I have a Lennox HVAC dual zone with a damper control board with 4 relays on it and 5 connections labeled stat1,stat2,damp1,damp2 and furnace. The original symptom was that when the upstairs thermostat was on, the AC compressor outside would not kick on. If I turned it off, and turned on the downstairs tstat, the compressor would run. A tech came out and said the board was bad, wired both dampers to damp2 and said only use the upstairs tstat. That seemed ok for awhile (although no zone control) but now the compressor still doesn't run some times. It seems to kick on and off at will. Is that an indication of that damper relay board being bad.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
8/2/2017
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,891
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, this situation you have here is complex and will likely take hours and some skill on your end to diagnose. There is not a simple answer other than 'its a controls problem and also possibly a dirty condenser coil or bad outside unit fan motor'

I am not the only expert here, you can choose to rate my work or opt out and see if anyone else here will go that distance with you.

.

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please select the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my simple answer so far positively.. and I will deliver that training and coaching to you All on the same dime soto speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt,shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with troubleshooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer,if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,891
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 months ago
I would like to pursue this further. At least some basic steps to try and determine the cause. I'm unable to attach the file though. Is there another way to send it?

Thanks.

I will coach you through this in detail.. not just a few hints etc

Are loading the picture of the zone control panel into your computer, then going to this dialog box and clicking on the 'add files' link?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Thanks for the quick response. When I click add files nothing happens. Tried IE and Chrome.

Try using the paper ciip icon at the right end of the tool bar at the top of this dialog box

and tell me you are tying this from a smart phone, or computer and if its an apple brand

Ask Your Own HVAC Question

I got the diagram, give me a few minutes to mark it up with trouble shooting instructions,

I also need a photo of zone control panel with its door open showing all of the wire connections

Ask Your Own HVAC Question

Test #1 Next time the system fails to come on in cooling mode, when it generally does come on in in cooling mode, jumper R to T at the thermostat terminal strip on the printed circuit board inside the furnace,

Click here please

IF the AC suddenly comes on, we know for sure that the problem is with the zone control panel or one of the attached thermostats,

IF the AC does not come on, measure the voltage between R and C if you have 24vac there and the AC does not come on, with the jumper between R and Y in place then we know the problem is with the printed circuit board, or the outside unit.

(never jumper R to C that will blow the 3 amp fuse on the printed circuit board)

Ask Your Own HVAC Question

Ooops Jumper R to Y not R to T (there is no T)

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Great, it's not coming on so I'll try it now. Jumper R to Y on the board with all the relays (2nd photo) that goes to the furnace unit, correct?

Yes try the R to Y jumper there but also to be 100% sure, jumper as shown on the wiring diagram inside the furnace (Yellow jumper wire shown)

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok, that kicked on the outside unit and it did stay on once I removed my jumper although I don't know that it will stay on.
Customer reply replied 4 months ago
Anything I can do to make sure it comes back on once it reaches temp and kicks back on? Also, what board would be a good replacement for that old one? I can't find those online anywhere.

We can stay on that path for a while to see how it works out and if the jumper once again starts the AC

That is about the oldest zone control set up I have ever seen, replacing the entire zone controller will be a good idea, including the thermostats

click here please

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Lol....the house is only 17 years old but it is the original HVAC. So leave the jumper on permanently until I can replace the board?

The jumper is for testing only, do not leave it in place, but you can use it to manually run the AC to cool the house down, then remove it

Click here for how to wire the new Honeywell HZ311 zone control panel,

Ask Your Own HVAC Question

17 years when it comes to electronic controls is about like a 17 year old computer.. workable to some degree but obsolete when it fails

Ask Your Own HVAC Question

Those are 4 wire damper motors... I have to see if they will work with the HZ311

Can you get me the brand and model number of the damper motors.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
TrolAtemp Model MST 24v 6 w 93-057H-001
Anyway to bypass that damper where the unit will kick on until I get another board? It quit on me again.
Customer reply replied 4 months ago
I have to run and get another fuse. I must have touched the blue wire. Thanks so much for your help and hanging with me this time of night. I really appreciate it. I'll check the response when I get back.

Click here for the wiring diagram needed to make the existing dampers work with the Honeywell HZ311 zone control panel diagram is lower left on page 2 only 3 wires needed

Ask Your Own HVAC Question

Click here for the wiring diagram needed to make the existing dampers work with the Honeywell HZ311 zone control panel diagram is lower left on page 2 only 3 wires needed

Ask Your Own HVAC Question

Stay in touch as needed

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Thanks again. So no way to bypass until I get a new board? Can the thermostat wire directly to the board in the furnace?

Good idea, yes you could wire one of the thermostats directly to the furnace terminal strip... in that case however you would have to manually open both dampers, there should be a manual open lever on them,

Let me know if you can find the levers or not

Ask Your Own HVAC Question

I need a photo of the damper and its linkage,... we would disconnect the linkage and use duct tape to hold it in the damper open position

Ask Your Own HVAC Question
Customer reply replied 4 months ago
My phone died but it just has a little arm that rotates around. I can just clamp it in its current position. So connect the stat wires color->color on the furnace terminal strip? I'll give it a try since it seems to be cutting out a lot more now.

If it is cutting out with R and Y jumpered then the problem is most likely with the printed circuit board inside the furnace

That said, I would replace the old zone controller on principle

You also need to be sure the the condenser coil on the outside unit is clean

click here, you can buy the ac coil cleaning kit at Home depot, thats the best, ***** ***** some other larger hardware store

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,891
8,891 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,891 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Alpine boiler making interment rumbling noise in exhaust
alpine boiler making interment rumbling noise in exhaust during post purge … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL #702H02997 THAT THE COMPRESSOR WAS RECENTLY REPLACED BUT i STILL HAVE A ISSUE WITH IT IT CRANKS BUT IT STOPS AFTER 45 SECONDS NEED HELPWITH THIS IS… read more
R G
R G
44 satisfied customers
I have a heat pump condense unit and it has made this loud
I have a heat pump condense unit and it has made this loud tat tat tat tat tat tat noise (when in heat mode) when it turns on or off. It goes from the condenser unit all the way to hearing in the blow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Rick, The thermostat terminals on the ZVC404 Zone Valve
Hi Rick,The thermostat terminals on the ZVC404 Zone Valve Control are marked as 24 VAC. Does this mean that when the terminals on the thermostat are closed, the circuit is completed and energized with… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My condenser trap on my Potterton Combi Promax is full i
Hi Pearl my condenser trap on my Potterton Combi Promax is full i have just discovered this is the reason why i had a pool of water on my worktop , how can i deal with this please … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
Have a Nordyne gas furnace- unit mod#M1MB 077A AW - fails on
Have a Nordyne gas furnace- unit mod#M1MB 077A AW - fails on flame failure. Igniter glows,main flame comes on,goes into failure. When reset it will run for days and again have same problem. Could ther… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,228 satisfied customers
My Ruud furnace unit shut off while I was unscrewing the
My Ruud furnace unit shut off while I was unscrewing the cover for the blower. I did not shut the system off before I started unscrewing the cover. I did hit the shut off switch after the unit shut do… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Peerless steam boiler that had a condensate pump
I have a Peerless steam boiler that had a condensate pump that ran when the tank filled. We have changed to a condensate demand pump with a 24 volt controller relay. How do i connect into the Mc D 47 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
This is a boiler. The past 10 days. The Munchkin 80M boiler
the past 10 days. The Munchkin 80M boiler is a gas-fired boiler that was designed for residential homes. This boiler is rated at 92% efficiency and an Input Btu's of 27,000 to 80,000 Btu's. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Brought a boiler from nome heating. Bought a boiler from
bought a boiler from mike west nome heating for eght thousand dollars need to insurance for my boiler … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
8,891 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
How do I determine my new Goodmn furnace unit blowing
how do I determine my new Goodmn furnace unit blowing capacity so I can match with the correct filter … read more
Phil
Phil
Mechanical Engineer
8,891 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
8,891 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x