RUUD mod UPML-048JAZ. Outdoor unit works if it is in the mood. Replaced transformer no chg. 2 years ago tech told us to not use heat pump, use emergency heat. Said he put the selector that sounded like a air driven slide on heat pump) to AC and said don't shift it back to reg heat pump op. Worked flawlessly but now doing exactly original prob. Slow to get temp dawn now, but when it wasn't confused would freeze you out to set temp. What did he shift? Where is it. We had power outages and after that I suspect magic fingers selected heat pump.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filters new. Thermo selects and causes unit to run, and air handler is fine. We can tap on the unit outside and encourages it to come on and work. It did this long ago. Like it thinks it's between heat and cold selection, tech said keep the heat to emergency and it isolated resultd were awesome

Contractor's Assistant: Do you plan on doing the work yourself?

If possible, that fellow isn't here anymore and his fix was in a couple of min and worked awesome

Contractor's Assistant: Anything else we should know to help you best?

I have extensive electrical background computer major companies and do AC to Cathodic Protect pipelines etc.

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 12 minutes by:
8/2/2017
HVAC Technician: Phil, Mechanical Engineer replied 11 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,694
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Greetings, this will be much more than a simple answer... it will take you and I several hours to sort out exactly what is wrong. and possibly fix it,

You will need a multimeter

I can opt out and we can see if someone else here wants to get involved, if you want me to go those extra miles for you just follow the instructions below

.

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please select the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course.....rate my simple answer so far positively..and I will deliver that training and coaching to you All onthe same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt,shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door andI will mark it up with troubleshooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer,if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

Ask Your Own HVAC Question
Customer reply replied 11 months ago
There isn't a diagram in air handler case that we see. Perhaps one on the outside unit but don't recall one. To be completely honest I remember my tech explain there was a (slide) ? Valve that determined heat or cold. He told me it hangs up semi in the middle, so cools but not well. And heat was not good. After he moved it physically to cool, no further problems.
Customer reply replied 11 months ago
The clue was when the out unit was trying to heat pump it sounded like a air driven valve with air bleeding off. Crazy but it was. After we selected cool side in outside unit it was spot on great. Cold enough if desired to hang meat.
HVAC Technician: Phil, Mechanical Engineer replied 11 months ago

Hello, that slide valve is called a 'heat pump reversing valve' sometimes a '4 way valve'

Click here

If it is actually sticking, it needs to be replaced, however it is possible that it is not getting the proper 24vac to its control coil, that is a less expensive fix

Valve is worth about $250 retail, and 6 hours labor to replace it... total cost between $800 to $1,200 with refrigerant and a new drier

.

please select the***RATING LINK***at thetop of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied. We can go from there without a time limit if you wish.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,694
9,694 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,694 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Trane system and I am experiencing a problem again
I have a Trane system and I am experiencing a problem again that I experienced about a month ago. Then the outside temp was in the teens. it is 38F today. My heating has stopped (electric not gas). My… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How can I lockout the heat pump and run only the aux heat
How can I lockout the heat pump and run only the aux heat (heat strips) from the thermostat?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have central air heat pump trane unit. Have central air
have central air trane unit heat pump. in either the heat mode --compressor running or in the emergency heat mode , the heat circuit breaker trips after about 5 minutes. in the cool mode there is no problem . . a technician checked the system this past .summer when i had this problem sporadicallyin the cool mode . he did not find a problem. suggested that that circuit breaker was bad. The circuit breaker was changed . --it did NOT solve the problem . I removed the cover from the thermostat. --found the 3 batteries badly corroded . cleaned the terminals --replaced the batteries . system worked fine in cool mode . now it appears the problem has shifted to the heat mode - Can it be that the Trane touch thermostat is defective and is causing the heat breaker to trip ????..or there is another possible problem ??? ..I.hate to call the tech folks and spent more dollars if not needed … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
HAve a question about wiring a fan control for a hot water
HAve a question about wiring a fan control for a hot water coil to a Diakin DV PEC series air handler… read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
71 satisfied customers
Aux heat will not come on unless thermostat is switched to
Aux heat will not come on unless thermostat is switched to emergency heat … read more
Phil
Phil
Mechanical Engineer
9,694 satisfied customers
I am having a bit of an epic adventure with my Trane
Hello! I am having a bit of an epic adventure with my Trane heat pump and air handler. Here's the backstory. In early April, we had our ductwork cleaned for the first time in the history of the house.… read more
Phil
Phil
Mechanical Engineer
9,694 satisfied customers
Had hvac tech come friday bc ac stays at 75 all day long and
Had hvac tech come friday bc ac stays at 75 all day long and won't reach 70 or 71. He checked outside heat pump and said everything was fine. Told me to check temp difference between output and return… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an Armstrong heat pump SHT10G24A that the outside unit
I have an Armstrong heat pump SHT10G24A that the outside unit will not shut off - even when zero outside. It has been running round the clock for weeks as long as the temperature is below 30 degrees. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane XL1000 fully electric 2 stage heat tab system.
I have a Trane XL1000 fully electric 2 stage heat tab system. I had an old analog termostat and had a ac person replace it with a White-Rogers one this summer. The AC worked fine and when it got cold … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hello, I have a Goodman Heat Pump that is 2 yrs old. The Heat
Hello, I have a Goodman Heat Pump that is 2 yrs old. The Heat worked fine this winter, but when tried AC, the outside unit would not turn on. I called the person that installed it and he came by and s… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Hi! We had a serviceman look at our Bryant heating/cooling
Hi! We had a serviceman look at our Bryant heating/cooling unit because water was leaking. He said he found a float in the condensate pump sticking, shook up the container (whatever it's called) and s… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
got a call from a tennant who said the outside heat pump unit
got a call from a tennant who said the outside heat pump unit was a "solid block of ice" --the unit was just installed new a month ago. the tennant reports that the heat inside is on at 68 degrees but… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a 13 years old York 4 ton Heat pump model EDFH which
I have a 13 years old York 4 ton Heat pump model EDFH which ices when the temperature gets below 32F. The problem with this pump started when the card became defective about three months ago when the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
We have an Bryant Evolution Heat Pump. The Outside Temperature
We have an Bryant Evolution Heat Pump. The Outside Temperature reading is 148 deg. There is presently snow around system which we just cleared but now it reads outside temo-Sensory error. What does th… read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
I have a Rheem Heatpump / Air Handeler Models RPLB-048JAZ/RBHC-21J11NFG.
I have a Rheem Heatpump / Air Handeler Models RPLB-048JAZ/RBHC-21J11NFG. The thermostat is a ICM SC2210. The problem is that the thermostat works on AC but never shuts off on heat. There was work rece… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
hi- i have a rheem model RCHJ 48A2GG24 serial M0703 central
hi- i have a rheem model RCHJ 48A2GG24 serial M0703 central heat air system, problem is that when set to heat and auto on the thermostat the air blows stronge thru the vents, but it is not hot, actual… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Mark Henley, You were so helpful perhaps you can help me further.
Mark Henley, You were so helpful perhaps you can help me further. You told me that I need a smart recovery therm. for my heat pump to keep from having the emergency heat coil go on when it is bringing… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Hello, Have a Gibson JT5BD-030k that was installed about
Hello, Have a Gibson JT5BD-030k that was installed about a year and a half ago. It works fine in AC but in heating mode it doesn't work properly. It doesn't build up a lot of heat when in heating mode… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x