I have a Nordyne Furnace Model GL1RA 090C-16B that the fan…

Customer Question
I have a Nordyne...

I have a Nordyne Furnace Model GL1RA 090C-16B that the fan keeps running when in AC mode

Contractor's Assistant: Did you check the furnace's filters?

Replaced

Contractor's Assistant: Do you plan on doing the work yourself?

And replace computer board

Contractor's Assistant: Anything else we should know to help you best?

Replaced thermostat and control board

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 11 months ago
Red Light flashes only when in cooling mode. When the Thermostat clicks off it will stop for a second and click right back on. The compressor for the AC turns off. Fan on furnace just keeps running. Removed all wires from thermostat and fan keeps running.
Customer reply replied 11 months ago
The red light means limit circuit open or external load on w any ideas what this is?
Answered in 2 hours by:
7/30/2017
HVAC Technician: Phil, Mechanical Engineer replied 11 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Greetings, if the high temperature limit switch inside the furnace trips, the main blower will keep running in order cool the furnace off... I think that is happening here

.

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please select the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course.....rate my simple answer so far positively..and Iwill deliver that training and coaching to you All on the same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt,shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with troubleshooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo tome.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer,if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
This question addressed my issue where my furnace fan will
this question addressed my issue where my furnace fan will come on but the burner is not lighting. There is a steady red light. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Nordyne Furnace Model GL1RA 090C-16B. The Status
Hello, I have a Nordyne Furnace Model GL1RA 090C-16B. The Status light is flashing twice(Inducer blower running). I bypassed the Pressure Switch after the inducer started to check it. When I did this,… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
nordyne furnace model fg6rl 100c 16b and runs in cycles red
nordyne furnace model fg6rl 100c 16b and runs in cycles red light flashes one time after C limit circuit open or external load on W. Hoses look good and I blew through the one that goes to sump.Servic… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a KG6RA 072C 16B, the blower runs but the gas burners
I have a KG6RA 072C 16B, the blower runs but the gas burners don't ignite. Also the A/C works, compressor shuts off but the blower does not shut off when the temp reaches the thermostat setting. The c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
have a nordyne gl1ra090c-16b vent fan comes on, burner comes,
have a nordyne gl1ra090c-16b vent fan comes on, burner comes, when blower come s on burner turns off ????… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Nordyne Model GL1RA 090C-16B gas heater which is only
I have a Nordyne Model GL1RA 090C-16B gas heater which is only blowing cold air. When I trip the fuse breaker and turn back on, the blower and exhaust turn on together immediately without any wait tim… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
For model KG6RC 080C-16B furnace circulating motor turns on
For model KG6RC 080C-16B furnace circulating motor turns on immediately after power on. Red light on solid. Thermostat disconnected. Connecting R-W does not initiate ignition sequence. Circulating fan… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Frigidaire model L1RA 090C-12B Furnace that will only
I have a Frigidaire model L1RA 090C-12B Furnace that will only blow cold air. The fault light code says it is a limited circuit or external load on W... I have checked the routine items (replaced air … read more
tadowhere
tadowhere
Maintenance Supervisor
Vocational, Technical or Trade Scho
90 satisfied customers
I HAVE A NORDYNE FURNACE MODEL NUMBER KG6RC 080-16B AND WHEN
I HAVE A NORDYNE FURNACE MODEL NUMBER KG6RC 080-16B AND WHEN IT STARTS UP THE FLAME WILL COME ON AND AS SOON AS THE MAIN FAN COMES ON THE FLAME SHUTS OFF. WHEN THE FAN QUITS THE FLAME COMES BACK ON AN… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a nordyne gl1ra 072c-12a and seem to have gone out.
i have a nordyne gl1ra 072c-12a and seem to have gone out. Its blowing cool air even though i set the heater switch to off on the thermostate. I also see a red blinking light on the switch board where… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Nordyne Furnace Model GL1RA 090C-16B with a serial
I have a Nordyne Furnace Model GL1RA 090C-16B with a serial # XXXXX GLA020805917. I have a problem with the furnace as it is blowing only cold air. I have cleaned the heat sensor, and replaced the air… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My furnace keeps going into blow mode. My code says it is an
My red light is blinking and my furnace just uses the fan, the heat coil doesn't even try to light it, the furnace goes straight to fan. My code says it is an ' limit circuit open or external load on … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a gibson GL1RA 072C-12A updraft furnace and with ac
I have a gibson GL1RA 072C-12A updraft furnace and with ac on and the fan switch on the thermostat on auto, the air handler fan does not cut off. The compressor cycles by the thermostat. Is the fan sw… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a frigidaire gas furnace. A couple things are not working
I have a frigidaire gas furnace. A couple things are not working properly all of a sudden. The blower fan will not turn off without me turning the furnace completely off at the switch, changing the th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a nordyne gas furnace model no. GL1RA 072C-12A. the
i have a nordyne gas furnace model no. GL1RA 072C-12A. the light code is 1 flash meaning limit curcuit open or external load on "W" i was told in the past by a hired pro to remove the limit sensor and… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
We have a Nordyne C5BA-T60C-C unit. the fan is blowing cold
We have a Nordyne C5BA-T60C-C unit. the fan is blowing cold air and the ignitor and gas will not come on to heat the air. I tried turning off the gas valve as it says to do on the inside panel and the… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am having a problem with a Westinghouse FG6RA-096c-16B 1.Thermostat
I am having a problem with a Westinghouse FG6RA-096c-16B: 1.Thermostat activates 2.Inducer starts 3.igniter lights 4.Gas valve opens 5.Flame 6.Blower Motor Starts 7. Gas Valve shuts off in 3-4 minutes… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Frigidaire furnace (FG6RA 096C 16B) when calling for heat,
Frigidaire furnace (FG6RA 096C 16B) when calling for heat, evrything starts off okay. Inducer starts, Igniter lights, burners ignite, short delay and then blower starts. Then after 2 minutes igniters … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.