I am an HVAC contractor in Southern DE. I have a performance

Customer Question
issue with a York system...
I am an HVAC contractor in Southern DE. I have a performance issue with a York system that another contractor installed and after going through a few things I believe they mismatched the outside and inside units. I have model and serial numbers. Can you help with that?
JA: Are you an HVAC professional?
Customer: Yes
JA: Do you plan on doing the work yourself?
Customer: I am not sure, that will be up to the homeowner to decide if they want me/ my company to fix or if they will contact the installing company.
JA: Anything else we should know to help you best?
Customer: Well I have what I believe to be a 4 ton outside unit with a 5 ton inside unit. ECM motor set to medium high speed as per installation manual. 80 degree ambient temperature 61degree indoor wet bulb temperature, 7 degrees super heat and 3.2 degrees subcooling. 280PSI liquid line preassure and 127-134 PSI suction line pressure.
Submitted: 5 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 5 months ago
This is a York System, Inside air handler is Mod.AHE60D3XH21B Outside unit is Mod. YHJF48S41S5A. TXV system No super heat adjustment on TXV. R410 of course. Factory subcooling should be 8 degrees with current conditions,its not even close.
Customer reply replied 5 months ago
Double checked TXV bulb, it is secure and insulated, condenser coil clean and with those pressures I am pretty sure the charge is really close!
Answered in 42 minutes by:
7/24/2017
HVAC Technician: Phil, Mechanical Engineer replied 5 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,155
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, I just need the model numbers of the coils and condensing units, not the serial numbers

Regarding super heat, only number that really counts is when the system is down to operating temperatures ...not when the building is still hot.

I need to know the supply and return air temperatures, the indoor air temperature and the outdoor temperature then the head and suction pressures at the *exact same time

We can go from there

I am a retired mechanical engineer and HVAC/ electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally...All I ask is please select the ***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I sent all that information! indoor wet bulb and outdoor dry bulb. I also sent suction and liquid pressures, as well as inside unit numbers and outside unit numbers, did you not get them?
HVAC Technician: Phil, Mechanical Engineer replied 5 months ago

.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 5 months ago

I need the indoor dry bulb temperature

at 72F indoor dry bulb the suction pressure should be 101 psig on R 410A

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Okay, here it is! outdoor dry bulb temp,80 degrees, indoor wet bulb 60-61degrees. Liquid pressure 278-290 psi, suction pressure 127-134 psi super heat between 7 and 10 degrees (total) subcooling 3.2-5.5 degrees. TXV system York outside unit Model YHJF4841S5A inside unit number AHE60D3XH21B ECM blower mtr set to medium high speed return air temp. 72-73 degrees supply air temp between 59.9-62.3 dgrees. According to factory plate I should have 8 degrees of subcooling for current conditions not even close. charge is good. TXV bulb is tight and insulated.
Customer reply replied 5 months ago
Hey Phil you still with me or did you go to sleep?
HVAC Technician: Phil, Mechanical Engineer replied 5 months ago

Thanks, at 80F outside air the unit should be condensing at 341 psig, 25F hotter than outside air on a SEER14 system (click here please)

At 270 psig head pressure is not taken accurately, OR the system was vapor charged with R410a not liquid charged, Or the compressor discharge check valve (scroll compressor) is going bad.

its a bit of a mess.

However with a suction pressure of 130 psig~ and the room at 72F the suction pressure is way high (29 psig high), all that pointing to your suspicion that the evaporator coil is over sized, you could compensate for that by reducing the air flow by 15 to 20% no need to replace the coil at this point. I will look up the model numbers next

Factory charging information is useless if the equipment is mismatched... also useless if the air flow is not measured. However we can get around most of that.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I completely agree concerning the factory charge information. I have looked up the system on Yorks site and they confirm that the inside coil and TXV are 5 ton units and the outside unit is a 4 ton unit. I do not think this was vapor charged. I believe they opened the service valves and walked away from it, unless York did it. The unit is only 3 years old. I question why you think the suction pressure is way too high? thats 42-44 degrees of evaporating temperature, pretty normal really. Liquid pressure is completely accurate, I can assure you of that!
HVAC Technician: Phil, Mechanical Engineer replied 5 months ago

See the R410a pressure temperature chart I attached earlier, at 80F outside and assuming a SEER 14 unit, it would be condensing at 25F hotter than the outside air (105F condensing is 340 psig head pressure)

271 psig head condensing would be 89F condensing temperature that would happen on when it was 67F outside... 271 psig is way low. something is wrong there, The york model number YHJF4841S5A did not come up for me, if this was a two speed system, the low head pressure would make sense.

If the contractor mis matched the coil and condensing unit there is a good chance that he vapor charged with R410a not liquid charged, that will throw all the numbers off. We can keep that in the back of our head for now.

The suction line with the room at 72F DB, should be sweating all the way back to the condensing unit, but NOT onto the compressor itself, that is a more reliable guide than super heat measurement when the system is running at temperature for best dehumidification, (the factory numbers are for highest efficiency so they can advertise it but not best dehumidification and most especially with the indoor coil 20% over sized.

Tell me the brand and model number of the TXV please...

We can go from there

We will have to work with this for a while

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 5 months ago

I will be out for an hour, slow the air flow down 20% lets see if we can get the suction pressure to 101 psig with the room at 72F dry bulb and 15F delta T across the coil.

We can sort out this head pressure anomally as we go along.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I did check the condensing delta and it is only 13 degrees, TXV is a Sporlan I believe, SI-ITVM4J1 with a ZGA bulb charge. I did have suction line sweating back to the outside unit, I did not check to see if it was all the way to the compressor but I suspect it was pretty close. I have left the home and I am back at the shop so I can't reduce the air flow. I also have to be careful to not do anything that may give the installing contractor any reason to NOT honor the system warranty. I was merely asked to check the system and report on my findings. I am not sure slowing the airflow is the answer to a mismatched system long term. This is a fairly large house with the inside unit located in an attic above the second floor. I do believe that there is already a reduction in air flow due to the fact that there is one 16X25 filter in a return grill. Way too small for 1750 CFM or close to that. I appreciate your help, my recommendation to the home owners will be to contact the installing contractor to have him match both units and add additional returns
HVAC Technician: Phil, Mechanical Engineer replied 5 months ago

That recommendation you want to give is safe enough for you and should work for the system, if you were going to tweek it though, you can generally get to the internal expansion valve adjustment through the flare nut on the outlet end, turn it in 1 full turn, that will starve the coil so that it will work better with a 4 ton condensing unit.

There will be no liability in that mechanically, same with slowing the air down 20%,

If that 270 psig head pressure is accurate, either its a two stage compressor operating on low stage, OR something else is incorrect, Head pressure at 80F outside requires a *coil temperature 25F hotter so thats 105F and 341 psig head, (the air off the coil however will only be 15F hotter)

Someone may have put some R22 into that system... watch out.

please select the 'finish and ratey our expert' link near the top of your page to close the question, I will appreciate it.

Your positive rating is the only way the company pays me for my work, lacking that I work at a loss. Thanks!

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,155
9,155 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,155 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My crown boiler boiler model no. AWR070ENST2PSU runs for a
My crown boiler boiler model no. AWR070ENST2PSU runs for a short time, shuts down, then takes a long time on start running again. We change the control. the pump, and the gas valve, Don't appears to h… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My rhino e75CN/e110cn high efficiency condensing gas boiler
my rhino e75CN/e110cn high efficiency condensing gas boiler will not heat the house above 64 degrees. have set the thermostats to 78 and still will not het the house above 64. the LED display on the u… read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I need an evaporator motor for a mini split unit. Sn
I need an evaporator motor for a mini split unit. Sn 50120031-7056 What is the best way to get this? … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
383 satisfied customers
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Gladiator Freezerator and the evaporator fan won
I have a Gladiator Freezerator and the evaporator fan won sorry won't turn off could it be the control board … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hvac I am using a Goodman gsx 16 seer 2.5 ton the evaporator
Hvac I am using a Goodman gsx 16 seer 2.5 ton the evaporator has 3/4 suction and the condenser has a 7/8 I'm going about 20 foot which size do I use for the copper tube… read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
41 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Peerless steam boiler that had a condensate pump
I have a Peerless steam boiler that had a condensate pump that ran when the tank filled. We have changed to a condensate demand pump with a 24 volt controller relay. How do i connect into the Mc D 47 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
This is a boiler. The past 10 days. The Munchkin 80M boiler
the past 10 days. The Munchkin 80M boiler is a gas-fired boiler that was designed for residential homes. This boiler is rated at 92% efficiency and an Input Btu's of 27,000 to 80,000 Btu's. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
9,155 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x