I am an HVAC contractor in Southern DE. I have a performance issue with a York system that another contractor installed and after going through a few things I believe they mismatched the outside and inside units. I have model and serial numbers. Can you help with that?

Contractor's Assistant: Are you an HVAC professional?

Yes

Contractor's Assistant: Do you plan on doing the work yourself?

I am not sure, that will be up to the homeowner to decide if they want me/ my company to fix or if they will contact the installing company.

Contractor's Assistant: Anything else we should know to help you best?

Well I have what I believe to be a 4 ton outside unit with a 5 ton inside unit. ECM motor set to medium high speed as per installation manual. 80 degree ambient temperature 61degree indoor wet bulb temperature, 7 degrees super heat and 3.2 degrees subcooling. 280PSI liquid line preassure and 127-134 PSI suction line pressure.

Submitted: 12 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 12 months ago
This is a York System, Inside air handler is Mod.AHE60D3XH21B Outside unit is Mod. YHJF48S41S5A. TXV system No super heat adjustment on TXV. R410 of course. Factory subcooling should be 8 degrees with current conditions,its not even close.
Customer reply replied 12 months ago
Double checked TXV bulb, it is secure and insulated, condenser coil clean and with those pressures I am pretty sure the charge is really close!
Answered in 42 minutes by:
7/24/2017
HVAC Technician: Phil, Mechanical Engineer replied 12 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,715
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, I just need the model numbers of the coils and condensing units, not the serial numbers

Regarding super heat, only number that really counts is when the system is down to operating temperatures ...not when the building is still hot.

I need to know the supply and return air temperatures, the indoor air temperature and the outdoor temperature then the head and suction pressures at the *exact same time

We can go from there

I am a retired mechanical engineer and HVAC/ electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally...All I ask is please select the ***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

Ask Your Own HVAC Question
Customer reply replied 12 months ago
I sent all that information! indoor wet bulb and outdoor dry bulb. I also sent suction and liquid pressures, as well as inside unit numbers and outside unit numbers, did you not get them?
HVAC Technician: Phil, Mechanical Engineer replied 12 months ago

.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 12 months ago

I need the indoor dry bulb temperature

at 72F indoor dry bulb the suction pressure should be 101 psig on R 410A

Ask Your Own HVAC Question
Customer reply replied 12 months ago
Okay, here it is! outdoor dry bulb temp,80 degrees, indoor wet bulb 60-61degrees. Liquid pressure 278-290 psi, suction pressure 127-134 psi super heat between 7 and 10 degrees (total) subcooling 3.2-5.5 degrees. TXV system York outside unit Model YHJF4841S5A inside unit number AHE60D3XH21B ECM blower mtr set to medium high speed return air temp. 72-73 degrees supply air temp between 59.9-62.3 dgrees. According to factory plate I should have 8 degrees of subcooling for current conditions not even close. charge is good. TXV bulb is tight and insulated.
Customer reply replied 12 months ago
Hey Phil you still with me or did you go to sleep?
HVAC Technician: Phil, Mechanical Engineer replied 12 months ago

Thanks, at 80F outside air the unit should be condensing at 341 psig, 25F hotter than outside air on a SEER14 system (click here please)

At 270 psig head pressure is not taken accurately, OR the system was vapor charged with R410a not liquid charged, Or the compressor discharge check valve (scroll compressor) is going bad.

its a bit of a mess.

However with a suction pressure of 130 psig~ and the room at 72F the suction pressure is way high (29 psig high), all that pointing to your suspicion that the evaporator coil is over sized, you could compensate for that by reducing the air flow by 15 to 20% no need to replace the coil at this point. I will look up the model numbers next

Factory charging information is useless if the equipment is mismatched... also useless if the air flow is not measured. However we can get around most of that.

Ask Your Own HVAC Question
Customer reply replied 12 months ago
I completely agree concerning the factory charge information. I have looked up the system on Yorks site and they confirm that the inside coil and TXV are 5 ton units and the outside unit is a 4 ton unit. I do not think this was vapor charged. I believe they opened the service valves and walked away from it, unless York did it. The unit is only 3 years old. I question why you think the suction pressure is way too high? thats 42-44 degrees of evaporating temperature, pretty normal really. Liquid pressure is completely accurate, I can assure you of that!
HVAC Technician: Phil, Mechanical Engineer replied 12 months ago

See the R410a pressure temperature chart I attached earlier, at 80F outside and assuming a SEER 14 unit, it would be condensing at 25F hotter than the outside air (105F condensing is 340 psig head pressure)

271 psig head condensing would be 89F condensing temperature that would happen on when it was 67F outside... 271 psig is way low. something is wrong there, The york model number YHJF4841S5A did not come up for me, if this was a two speed system, the low head pressure would make sense.

If the contractor mis matched the coil and condensing unit there is a good chance that he vapor charged with R410a not liquid charged, that will throw all the numbers off. We can keep that in the back of our head for now.

The suction line with the room at 72F DB, should be sweating all the way back to the condensing unit, but NOT onto the compressor itself, that is a more reliable guide than super heat measurement when the system is running at temperature for best dehumidification, (the factory numbers are for highest efficiency so they can advertise it but not best dehumidification and most especially with the indoor coil 20% over sized.

Tell me the brand and model number of the TXV please...

We can go from there

We will have to work with this for a while

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 12 months ago

I will be out for an hour, slow the air flow down 20% lets see if we can get the suction pressure to 101 psig with the room at 72F dry bulb and 15F delta T across the coil.

We can sort out this head pressure anomally as we go along.

Ask Your Own HVAC Question
Customer reply replied 12 months ago
I did check the condensing delta and it is only 13 degrees, TXV is a Sporlan I believe, SI-ITVM4J1 with a ZGA bulb charge. I did have suction line sweating back to the outside unit, I did not check to see if it was all the way to the compressor but I suspect it was pretty close. I have left the home and I am back at the shop so I can't reduce the air flow. I also have to be careful to not do anything that may give the installing contractor any reason to NOT honor the system warranty. I was merely asked to check the system and report on my findings. I am not sure slowing the airflow is the answer to a mismatched system long term. This is a fairly large house with the inside unit located in an attic above the second floor. I do believe that there is already a reduction in air flow due to the fact that there is one 16X25 filter in a return grill. Way too small for 1750 CFM or close to that. I appreciate your help, my recommendation to the home owners will be to contact the installing contractor to have him match both units and add additional returns
HVAC Technician: Phil, Mechanical Engineer replied 12 months ago

That recommendation you want to give is safe enough for you and should work for the system, if you were going to tweek it though, you can generally get to the internal expansion valve adjustment through the flare nut on the outlet end, turn it in 1 full turn, that will starve the coil so that it will work better with a 4 ton condensing unit.

There will be no liability in that mechanically, same with slowing the air down 20%,

If that 270 psig head pressure is accurate, either its a two stage compressor operating on low stage, OR something else is incorrect, Head pressure at 80F outside requires a *coil temperature 25F hotter so thats 105F and 341 psig head, (the air off the coil however will only be 15F hotter)

Someone may have put some R22 into that system... watch out.

please select the 'finish and ratey our expert' link near the top of your page to close the question, I will appreciate it.

Your positive rating is the only way the company pays me for my work, lacking that I work at a loss. Thanks!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,715
9,715 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,715 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Hvac I have a five ton r-22 condensing unit five ton coil
Hvac I have a five ton r-22 condensing unit five ton coil and txv my question is I have three and half ton 134 condensing unit used about five years old I removed in sound working order can I flush an… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
3 years ago a contractor install a 2 ton 16 seer condenser
3 years ago a contractor install a 2 ton 16 seer condenser and air handler for the second floor of my home In the summers hottest days in new york it is not able to cool sufficiently. only about an 8 … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
What is the normal operational pressures on a rheem
what is the normal operational pressures on a rheem 13ajm30a01 2.5 ton compressor high and low side @70 degree out side temp and subcooling for this system, it is txv system. label is almost unreadabl… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I am charging my heat pump it is an r410a and its about 90
I am charging my heat pump it is an r410a and its about 90 degrees outside i have gotten the low side up from about 100psi to 130 and the high side from around 300psi to 340-50 is this about right wha… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i have only one degree F superheat on this 7.5 ton unit. i
i have only one degree F superheat on this 7.5 ton unit. i have tested the txv. i put the sensing bulb in a cup of ice water, the superheat went up! and when i put it in my palm, the super heat decrea… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
Hello, Ive been out of the HVAC industry for many years and
Hello, I've been out of the HVAC industry for many years and prefer to service my own HVAC systems (I have two - one upstairs and one down). I'd like an expert to answer three key questions. But first… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a ycjd 060 York ac unit with a air handler, why would
I have a ycjd 060 York ac unit with a air handler, why would the unit be cycling like crazy when I know the unit is full. would it have to do with having no type of motor modulator on the system? we l… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
hi , I replaced a old lennox heat pump with a grandaire heat
hi , I replaced a old lennox heat pump with a grandaire heat pump. I followed the subcooling method of charging it up and I have very low suction pressure (35 #) and a liquid pressure of 250#. Outside… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Why does my 14 SEER 3.5 ton Goodman Heat Pump compressor sound
Why does my 14 SEER 3.5 ton Goodman Heat Pump compressor sound like it is being slugged with liquid refrigerant at startup in the Heat mode? It is a R-410A unit. It sounds great in Cool mode. Have che… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
York 5 ton outside unit, ADP 5 ton evaporator coil Installed
York 5 ton outside unit, ADP 5 ton evaporator coil: Installed with TXV System runs but unable to cool to desired temp, Called A/C tech. Here are the readings as best as I can make out from his writing… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have a 3 ton Trane XL13i mod. # 4TTX3036A 1000AA with a
I have a 3 ton Trane XL13i mod. # 4TTX3036A 1000AA with a variable speed air handler mod. # XXXXX Does this have a TXV and do you use the superheat or subcooling method for charging? What are reasonab… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a 2.5 ton split system heat pump. Both condenser and
I have a 2.5 ton split system heat pump. Both condenser and air handler is 2.5 tons, 1150 sq ft. Pressures are 138 suction, 370 head. According to the manual, superheat and subcooling should be 7-9 +/… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have a 3 ton Amana 16 seer unit with a matching coil and
I have a 3 ton Amana 16 seer unit with a matching coil and txv; unit was installed last year by a local company and seems to perform great. Being an engineer, I like to measure things; a temperature m… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have a Rheem RAKA 048 condenser / RCBA 48 coil section system.
I have a Rheem RAKA 048 condenser / RCBA 48 coil section system. System is 16 yrs old, had icing problems. Tech diagnosed system had "issues" with metering device, contamination in system, and possibl… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a goodman gsh130181ab and needs freeon need 2 know head
I have a goodman gsh130181ab and needs freeon need 2 know head and suction pressure on a 90 degree day don't have a super heat bulb available?thanks… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Dear sir. i just finished installing my first R 410 ref. goodman
Dear sir. i just finished installing my first R 410 ref. goodman pkg unit. typically what pressures will i see when this unit is running @ 95 degrees in this hot, humid alabama summer? Also when troub… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
The indoor coil of my Bryant 113ANA036 air conditioner is freezing.
Have a Bryant 113ANA036 air conditioner that was installed a year ago and went to look at it, and the indoor coil is freezing up.It is a Puron system, has good air flow, clean coil,the pressures is 32… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Customer complaint system is not cooling. Split Heat Pump
Customer complaint: system is not cooling. Split Heat Pump system: AHU - Comfortmaker ‘97 Condenser – Trane '03, 3 ton, R22 Pressures (psig): High side: 240 Low side: 82 Just now cleaned Condenser uni… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x