Have a carrier rtu. Runs fine for 5 minutes then shuts down…

Have a carrier rtu...

Have a carrier rtu. Runs fine for 5 minutes then shuts down cooling. Heat pump with no strip heat. Thermostat is calling for cool. Indoor fan is running.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filters fine, tstat is calling forcool. Has honeyweii 7220 economizer c ontrol

Contractor's Assistant: Do you plan on doing the work yourself?

Ye s

Contractor's Assistant: Anything else we should know to help you best?

All lps hps sensors jumpered , no chang e. Defrst board loses 24 volts on pin 10.

Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 hours by:
7/21/2017
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,200
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello. the defrost board has gone bad. If you rate that answer positively I will spend an unlimited amount of time coaching to a complete diagnosis and repair (could also be a bad sensor attached to the defrost board)

Ask Your Own HVAC Question
Customer reply replied 7 months ago
New defrost board, new Honeywell 7220. New vfd fan control.
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 435
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings
Verified

hi i am dan i can help you with this. have you tried bypassing the economizer controls?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
How do I bypass the Honeywell 7220

you can either go into the settings under test run and you can set it to connect Y in to Y out. it will stay like that for 10 minutes or you can just disconnect the Y in and Y out and twist them together

Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 435
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings
Verified
Daniel Plourde and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 7 months ago
Y in and out are staying up. On the defrost board P2 pin 5 blue is up. P3 pin 10 drops.
Phone call session started

found the wiring diagram. what you want to look for is a freeze thermostat that will be attached to the indoor coil that is what is tripping the unit off. it may be the switch is faulty or the coil is actually freezing could be the coil is dirty or some other restriction. you said the fire stat tripped, there may also be fire dampers in the duct that have closed and need to be reset. let me know if you have any more questions

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Jumpered out freeze sensors, no difference

ok then i would recommend calling carrier factory tech support 1-***-***-****

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Carrier factory support is sigler down here in southern California

that is a supplier for parts but you can call the tech support line and talk to them and they can walk you through exactly what to check

Ask Your Own HVAC Question
Customer reply replied 7 months ago
They sent me to sigler

ok did you try calling them?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
not very helpful

ok have you checked that it is not the compressor overheating when it shuts off?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
not overheating

ok does the second circuit work or do the same thing?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
How do I pay you for your help.
Monday tech support is going to visit site. I hope it is something really dumb that I have overlooked.

there is nothing else you need to do. good luck with the unit

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Thank you.

.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Daniel Plourde Your Own Question
Daniel Plourde
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 435
435 Satisfied Customers
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings

Daniel Plourde is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,200 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Carrier Steam Humidifier - HUMXXSTM3134. The red
I have a Carrier Steam Humidifier - HUMXXSTM3134. The red light was blinking, so technician replaced canister. Red like is STILL blinking. red light … read more
Bill
Bill
Service Mgr
24 satisfied customers
I have a Carrier unit with heater that will not turn on. My
Hi I have a Carrier unit with heater that will not turn on. My house is only 5 years old and the company which installed the unit seems to no longer be in business. How can I get the warranty honored … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My furnace (Carrier) is not coming on. There is power going
My furnace (Carrier) is not coming on. There is power going to the furnace but yet it won't come on. The panel attached to the furnace (Honeywell) indicates a red light for both heat and zone 3. I hav… read more
Bill
Bill
Service Mgr
24 satisfied customers
Carrier furnace. Igniter comes on, but no flame. There was
Carrier furnace. Igniter comes on, but no flame. There was an electrical issue earlier today on the electric company's side of the meter. It has been repaired. Furnace was OK prior to that. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace rated at 1865 cfm was recently installed in
carrier furnace rated at 1865 cfm was recently installed in Jan 2018. Total cfm for all vents is 1056 cfm. heat distrbution for 16 vents ranges from 69 to 95 cfm. what could be the problem? Please adv… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier model 58mec100 and the heater will not
I have a carrier model 58mec100 and the heater will not cycle back on and the light will blink 1 then 6 green on the control board. I can switch the power off for a minute then it tries again and come… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier furnace model 58CTA090-12114 that was
I have a Carrier furnace model 58CTA090-12114 that was installed in 2005,I am currently having an issue with it when it is called upon for heat, it will start the burner sequence with the ignitor glow… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The ignitor to my Carrier furnace will not trigger so no
Hi Pearl. The ignitor to my Carrier furnace will not trigger so no heat can enter the house. I've manually reset the limit switch and cleaned the flame sensor and was looking for suggestions on what t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a carrier infinity model 58CVA090 that seems to be
hi! i have a carrier infinity model 58CVA090 that seems to be only blowing cold air, wondering if pilot light out since i just changed filters and my thermostat reset how can i tell if my pilot light … read more
Daniel Plourde
Daniel Plourde
HVAC Technician
435 satisfied customers
I have a thermostat that says it is Carrier on the front and
I have a thermostat that says it is Carrier on the front and has Class 2 30V Max, LR1620 marked on the back. I want to move to a Wi-fi thermostat? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm trying to find a blower motor for a carrier 58wav045.
I'm trying to find a blower motor for a carrier 58wav045 … read more
MattR757
MattR757
HVAC Contractor / Owner
Associate Degree
14 satisfied customers
Non working furnace issue - Carrier Weathermaker 8000. The
Non working furnace issue - Carrier Weathermaker 8000. The ignition module was changed a couple of years ago. There's a clicking sound but not burning. Ideas? Cost?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Our carrier infinity says "system malfunction". The fan is
our carrier infinity says "system malfunction". The fan is working but it is not cool. I went to the attic and changed the filter but code is still there. What does this mean? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have a Carrier Weather Maker 8000 ts and the light on the
Have a Carrier Weather Maker 8000 ts and the light on the front panel is blinking … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Carrier Infinity System Thermostat Model #
We have a Carrier Infinity System Thermostat Model # SYSTXCCUIZ01-A and the plastic "heat" and "zone" buttons are broken. We are looking for a new unit with this model number to replace our current un… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Im changing my thermostat from a carrier to honeywell
Im changing my thermostat from a carrier to honeywell rth6580wf. The orange wire, not sure where to connect it on the honeywell … read more
Phil
Phil
Mechanical Engineer
9,200 satisfied customers
Airheatman, Trying to source a control board for a Carrier
Hi airheatman, Trying to source a control board for a Carrier forced air furnace that a technician said was no longer available. The number is ***** obscured, looks like 3057?5 702 working with a 3012… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have Carrier fan coil unit model FV4CNB003. Have Carrier Fan
Have Carrier Fan Coil unit # FV4CNB003. Seemed to run and change speed during operation. Is this normal? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x