Have a carrier rtu. Runs fine for 5 minutes then shuts down…

Have a carrier rtu...

Have a carrier rtu. Runs fine for 5 minutes then shuts down cooling. Heat pump with no strip heat. Thermostat is calling for cool. Indoor fan is running.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filters fine, tstat is calling forcool. Has honeyweii 7220 economizer c ontrol

Contractor's Assistant: Do you plan on doing the work yourself?

Ye s

Contractor's Assistant: Anything else we should know to help you best?

All lps hps sensors jumpered , no chang e. Defrst board loses 24 volts on pin 10.

Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 hours by:
7/21/2017
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,470
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello. the defrost board has gone bad. If you rate that answer positively I will spend an unlimited amount of time coaching to a complete diagnosis and repair (could also be a bad sensor attached to the defrost board)

Ask Your Own HVAC Question
Customer reply replied 11 months ago
New defrost board, new Honeywell 7220. New vfd fan control.
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 455
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings
Verified

hi i am dan i can help you with this. have you tried bypassing the economizer controls?

Ask Your Own HVAC Question
Customer reply replied 11 months ago
How do I bypass the Honeywell 7220

you can either go into the settings under test run and you can set it to connect Y in to Y out. it will stay like that for 10 minutes or you can just disconnect the Y in and Y out and twist them together

Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 455
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings
Verified
Daniel Plourde and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 11 months ago
Y in and out are staying up. On the defrost board P2 pin 5 blue is up. P3 pin 10 drops.
Phone call session started

found the wiring diagram. what you want to look for is a freeze thermostat that will be attached to the indoor coil that is what is tripping the unit off. it may be the switch is faulty or the coil is actually freezing could be the coil is dirty or some other restriction. you said the fire stat tripped, there may also be fire dampers in the duct that have closed and need to be reset. let me know if you have any more questions

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Jumpered out freeze sensors, no difference

ok then i would recommend calling carrier factory tech support 1-***-***-****

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Carrier factory support is sigler down here in southern California

that is a supplier for parts but you can call the tech support line and talk to them and they can walk you through exactly what to check

Ask Your Own HVAC Question
Customer reply replied 11 months ago
They sent me to sigler

ok did you try calling them?

Ask Your Own HVAC Question
Customer reply replied 11 months ago
not very helpful

ok have you checked that it is not the compressor overheating when it shuts off?

Ask Your Own HVAC Question
Customer reply replied 11 months ago
not overheating

ok does the second circuit work or do the same thing?

Ask Your Own HVAC Question
Customer reply replied 11 months ago
How do I pay you for your help.
Monday tech support is going to visit site. I hope it is something really dumb that I have overlooked.

there is nothing else you need to do. good luck with the unit

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Thank you.

.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Daniel Plourde Your Own Question
Daniel Plourde
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 455
455 Satisfied Customers
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings

Daniel Plourde is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,470 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Carrier Weathermaker 8000 is not working. Help.
My Carrier Weathermaker 8000 will not start the furnace. The fan blows but it stops and never fires. It has error 13. 1 blink, then 3 blinks. House is cold and I need to fix ASAp. Any help?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Carrier Thermostat thats flashing HP and not responding
I have a Carrier Thermostat that's flashing HP and not responding when I push any of the buttons...what should I do?… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
How to replace Carrier thermostat to a Honeywell thermostat
I just purchased a Honeywell RTHL2410C thermostat to replace an expensive Carrier thermostat that no longer works. The Carrier thermostat only had a red wire (V+) and black wire (Vg) attached to the w… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Needing a replacement compressor for a carrier 38YRA024310,
Needing a replacement compressor for a carrier 38YRA024310 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier model 25hnb636a310 unit is not coming on. Where
my carrier model 25hnb636a310 unit is not coming on … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm looking at an infinity series carrier system with the 4
I'm looking at an infinity series carrier system with the 4 wire connection terminals "a,b,c, and d" could you tell me what the letters correspond to? The thermostat says indoor communication error an… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
Thermostat has no power for a Carrier HVAC unit. The LCD
Thermostat has no power for a Carrier HVAC unit. The LCD display of the Thermostat is blank. Checked power to HVAC, which is okay. Any suggestions to fix the problem? … read more
Phil
Phil
Mechanical Engineer
9,470 satisfied customers
Carrier vs Rheem brand? Which one better? For carrier we got
Carrier vs Rheem brand? Which one better? For carrier we got 10 year warranty, 3 years labor and 5 year maintenance plan For rheem we got 10 year warranty, 2 year labor and 2 year maintennacr plan Any… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Carrier 25HPA430A0030010 heat pump, installed and
I have a Carrier 25HPA430A0030010 heat pump, installed and running fine for 7 years. Last night, the compressor stopped running. Status light on control board is Code 82 - Thermal lockout after 4 succ… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
What Carrier thermostat will replace a Carrier Thermidistat
What Carrier thermostat will replace a Carrier Thermidistat installed in 2000? I want an exact functional replacement. … read more
Phil
Phil
Mechanical Engineer
9,470 satisfied customers
Have a carrier infinity 25hnb624c0031203o that is giving me
have a carrier infinity 25hnb624c0031203o that is giving me an error 179 - How do I fix this? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
WHAT IS THE BELT SIZE FOR CARRIER MODEL: 40RUAAO8A2A6AOAOAO,
GOOD DAY, WHAT IS THE BELT SIZE FOR CARRIER MODEL: 40RUAAO8A2A6AOAOAO … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
How does the cover get removed on a Carrier Carrier
How does the cover get removed on a Carrier Carrier TSTATBBP2S01B thermostat so I can replace it with an Ecobee? … read more
hvacdave84
hvacdave84
53 satisfied customers
My Carrier Split A/C wont turn on and only a continuous green
My Carrier Split A/C wont turn on and only a continuous green flashing light is showing on the front panel of the unit. This is all happened after a power outage… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
how do I reset my limit rollout switch on my Carrier Heate
how do I reset my limit rollout switch on my Carrier Heater?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
The yellow purge light is flashing on my honeywell zoning system.
The yellow purge light is flashing on my honeywell zoning system. Can I reset it by pushing the boot button ?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My Bryant furnace keeps shutting off. What could be wrong?
My Bryant (Carrier) Plus 90 furnace, model 398AAW036080D shuts off after running for a bit. I can reset and it will come back on, but always shuts back off, so I assume it is sensing a problem during … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Carrier furnace keeps shutting down and shows code 34
I have a Carrier 58PAV090 furnace that is about 7 years old. It wouldn't turn on (although it has worked this season), so I pulled the two panels and then put them back on. It tries to start up, but t… read more
Jason Martin
Jason Martin
Maintenance Supervisor
Vocational, Technical or Trade Scho
88 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x