My unit ices. up. Tech checked the Freon and said it was

Customer Question
right according to specs. The...
My unit ices. up. Tech checked the Freon and said it was right according to specs. The condenser coils were cleaned. The air filter was changed. The evaporator he said was clean. The evap. fan was cleaned and the fan motor was replaced. The thermostat was changed. Still the unit ices up the suction line. What could be the problem?
JA: Did you double-check the thermostat's settings? And what about the filters?
Customer: The thermostat was set at 75. The filter was replaced with a new one. The same kind being used for years.
JA: Do you plan on doing the work yourself?
Customer: At this point I don't know what to check next and evidently the tech I called didn't either. I can do everything except the Freon because I don't have a license any more. I retired.
JA: Anything else we should know to help you best?
Customer: The tech said the evap. coil was clean but I didn't see it. Is there any thing else that would cause this problem or should I pull the evap. and check it myself?
Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 36 minutes by:
7/17/2017
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, about the only thing that will cause the coil to ice the suction line is not enough warm air flow across the cooling coil....return air should be in the 72 to 75F range, not cooler.

if there is a bypass duct installed between the supply and return and it is open.. that will cause the return air temprerature to drop below 60F and that will ice the coil and the suction line.

.

Sometimes the duct liner used in some configurations comes loose and blocks the air flow in the system.

.

If it is a new system, and the evaporator is more than 20% smaller than the condensing unit, the coil will run colder and sometimes frost the suction line.

.

Tell me what the head and suction pressure reads were and the exact indoor and outdoor temperatures at the time, with that information I can assess the situation more closely for you.

.

I am a retired mechanical engineer and HVAC/ electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please select the ***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied..

.

If you need to be coached through a full diagnosis/repair, and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course.. ...

.

rate my simple answer so far positively..and I will deliver that training and coaching to you All on the same dime so to speak..

.

If you can agree to that, rate now, lets continue by all means.

.

.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I will check for a bypass and blockage but don't remember seeing either. The Tech that checked the evaporator coil said it was clean but I am not so sure now. I will check it myself. The tech didn't tell me the pressures so I will have to check them myself tomorrow. Thanks
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago

Thanks, ***** ***** see you tomorrow

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,824 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My condenser trap on my Potterton Combi Promax is full i
Hi Pearl my condenser trap on my Potterton Combi Promax is full i have just discovered this is the reason why i had a pool of water on my worktop , how can i deal with this please … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
Webb-Guy
Webb-Guy
tech.
77 satisfied customers
On our heat pump the evaporator blower runs constant even
On our heat pump the evaporator blower runs constant even when set to auto. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Peerless steam boiler that had a condensate pump
I have a Peerless steam boiler that had a condensate pump that ran when the tank filled. We have changed to a condensate demand pump with a 24 volt controller relay. How do i connect into the Mc D 47 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
This is a boiler. The past 10 days. The Munchkin 80M boiler
the past 10 days. The Munchkin 80M boiler is a gas-fired boiler that was designed for residential homes. This boiler is rated at 92% efficiency and an Input Btu's of 27,000 to 80,000 Btu's. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am told I have a leaking evaporating pan in a Lennox Model
I am told I have a leaking evaporating pan in a Lennox Model #C16-46-1FF. Iwould like to find a replacement pan. Is this possible, or can I tape crack? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit,
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit, Model MS-A12WA). That recently started leaking a pretty significant amount of water. The water must be building up inside the unit and then at s… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has run without problem for the last two years. Lately, it has begun to shut down and then restart on its own after about an hour or more. The l… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Evaporator water flow too low alarm keeps happening.
Evaporator water flow too low alarm keeps happening. Recently cleaned coils now this. The pumps are running fine. The pressures are good on the approach. The water strainer is clean. What is this a ca… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I have a gibson C5BA-T42C- evaporator coil. Had a new
I have a gibson C5BA-T42C- B evaporator coil. Had a new condenser put in. they didn't change the coil. Said it would be ok. They used r410a freon. Case on this coil say r22. Is this coil going to work… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x