I have a custom ac installation i need help with. I have a…

I have a custom ac...
I have a custom ac installation i need help with. I have a 1500 sq ft shop with a waste oil heater and no ac. It has a very strong 4200 cfm fan. A friend gave me a 3 ton ac condenser and coil (coil is without a box, i think you call it air handler?). I would like to know if there is a way for us to attach the coil to the waste oil heater fan, what type of box we would need for that etc. We would have a licensed contractor attach everything, and charge it up, we just want to see how feasible it is, and maybe move the equipment to where it belongs first as that we can do ourselves. I can provide a picture of what it looks like now.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
6/22/2017
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,074
Experience: Furnace, A/C and heat pump specialist.
Verified

Can you slow the fan speed down on the furnace? THe 4200cfms would move way to much air across coil to pickup heat.We need to get tr down to about 1200cfms.

Ask Your Own HVAC Question
Customer reply replied 12 months ago
We are picking up ac not heat though? I don't understand.

1. To make air conditioning, we pick up heat from the building through the evaporator and remove the heat to outdoors.(You can not make cold, you can only remove heat resulting in cold)

2.Unfortunately the unit heater is not a good air source for the coil you have.You would be better off to locate you a used air handler on Craigslist or somewhere to use along with the outdoor unit.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,074
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 12 months ago
thank you!
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,074
9,074 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The pan beneath the AC condenser has rusted and if the AC is
The pan beneath the AC condenser has rusted and if the AC is running, leaks into the ceiling beneath. This part of the AC is in the attic. Is the pan replaceable and how costly is this repair. … read more
airheatman
airheatman
HVAC Technician
9,074 satisfied customers
I have a Rheem model 13PJA60 condenser that I am trying to
I have a Rheem model 13PJA60 condenser that I am trying to determine the recommended orifice size for the evaporator expansion valve.This is a R22 unit that was shipped dry. Just want to confirm the o… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
On my Trane evaporator/air handler/furnace unit, the fan
On my Trane evaporator/air handler/furnace unit, the fan will not come on, though thethermostat/control panel in the thehouse … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Our condensate drain in not working properly. It has been
Our condensate drain in not working properly. It has been cleaned out and is clear. There is a cleanout before the p-trap. It seems that when the cap is removed, the system drains properly. Any sugges… read more
airheatman
airheatman
HVAC Technician
9,074 satisfied customers
Miller/nordyne condenser fan running constantly. Just
miller/nordyne condenser fan running constantly JA: I'll do all I can to help. How long have you been dealing with this? Customer: just started last nite JA: Do you plan on doing the work yourself? Cu… read more
airheatman
airheatman
HVAC Technician
9,074 satisfied customers
My blower fan does not run. The condenser and condenser fan
My blower fan does not run. The condenser and condenser fan run fine but the air handler fan does not. The squirrel cage turns freely and makes weak attempts to turn but does not run so it seems there… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am replacing a evaporator on a refrigerator and I have a
I am replacing a evaporator on a refrigerator and I have a FB12 flame barrier. It has two sides and aluminum and fiberglass. There's a little sticker on the aluminum side saying do not use the side to… read more
airheatman
airheatman
HVAC Technician
9,074 satisfied customers
What is size of clear tubing for condensation for Friedrich
What is size of clear tubing for condensation for Friedrich room air conditioner PH14B … read more
airheatman
airheatman
HVAC Technician
9,074 satisfied customers
My upstairs HVAC has the evaporator located in the attic.
My upstairs HVAC has the evaporator located in the attic. There are two drain lines running inside the wall to ground, one on the evaporator and one on the drip pan under the evaporator, the drip pan … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
66 satisfied customers
What would make evaporator fan motor stop and the unit to
what would make evaporator fan motor stop and the unit to freeze up … read more
airheatman
airheatman
HVAC Technician
9,074 satisfied customers
i was told that my condensing unit was no good by a company
i was told that my condensing unit was no good by a company that want yo sell me a new one i asked how come i was told my compressor was not working but when i put my gages on i get a reading lowside … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Inside uint blowing but outside condenser not coming on.
inside uint blowing but outside condenser not coming on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Evaporator coil has a leak. Its a Lennox coil part number
question is Lennox coils have had issues with Leaks coil is about 6 years old i was wondering if another brand coil… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I need the BTU rating for a Heatcraft Evaporator Model
I need the BTU rating for a Heatcraft Evaporator Model ADT56AWGJ … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a modine unit heater, model pa105ab, 80,000 btu. the
i have a modine unit heater, model pa105ab, 80,000 btu. the burner lights fine, but the fan won't turn on. started randomly, but won't turn on at all … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Today, evaporator coil froze over and i heard the outside
Today, evaporator coil froze over and i heard the outside condensor area making a louder noise. i shut the ac off when noticing this and the coil melted and the fan blows air now. i looked at the evap… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
I replaced a jazz bored today along with evaporator fan
I replaced a jazz bored today along with evaporator fan motor and I can only get the motor running if I use the ground wire to one terminal on the motor and one of the wires that has 120 V I replaced … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
airheatman
airheatman
HVAC Technician
9,074 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x