Related HVAC Questions
5 ton split, R410a, new evap, new outdoor unit, new line
Bryant 5 ton split, R410a, new evap, new outdoor unit, new line set. system evacuated and charged to factory specs. suction pressure at 95 psi, discharge pressure at 300 psi. sub cooling measures 21 d… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
10,082 satisfied customers
If the reversing valve has a internal short like you said is
if the reversing valve has a internal short like you said is that why my suction psi is ;low… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
10,082 satisfied customers
Rheem model number RCFA– HM3617AC 2 1/2 ton split unit R22
Rheem model number RCFA– HM3617AC 2 1/2 ton split unit R22 Why is my discharge pressure low at 93 PSI, Ambient temp 85, suction pressure normal at 68 psi. Good airflow, no air restriction unit clean… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
hi , I replaced a old lennox heat pump with a grandaire heat
hi , I replaced a old lennox heat pump with a grandaire heat pump. I followed the subcooling method of charging it up and I have very low suction pressure (35 #) and a liquid pressure of 250#. Outside… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,366 satisfied customers
I have a 2.5 ton central Air conditioner and my suction pressure
I have a 2.5 ton central Air conditioner and my suction pressure is about 76 and discharge pressure about 190. The air conditioner runs very long to cool down the room temp and I noticed the suction l… read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
7,962 satisfied customers
the compressor is in, the unit is charged, the temp pressure
the compressor is in, the unit is charged, the temp pressure chart says for an 85 degree day the pressure should be 155. the unit isn't cooling as well as it used to. the split is only 10 degrees at t… read more
A-1 Tech
A-1 Tech
Service Manager
Vocational, Technical or Trade Scho
526 satisfied customers
i have a heat pump that in heating mode and is not heating..blower
i have a heat pump that in heating mode and is not heating..blower motors are on.. but cools fine in cooling mode.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,366 satisfied customers
Carrier 2.5 ton package unit straight cool 410A, scroll compressor.
Carrier 2.5 ton package unit straight cool 410A, scroll compressor. We have high suction pressure, normal head pressure, won't get down to cool temperature. We had high superheat and we checked the TX… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
I have a 2.5 ton split system heat pump. Both condenser and
I have a 2.5 ton split system heat pump. Both condenser and air handler is 2.5 tons, 1150 sq ft. Pressures are 138 suction, 370 head. According to the manual, superheat and subcooling should be 7-9 +/… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,366 satisfied customers
just got back into hvac cant remember superheat on how to
just got back into hvac can't remember superheat on how to fiquire by rule of thumb can you help… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,514 satisfied customers
Was working on a 3 1/2 ton heat pump, when I got there the
Was working on a 3 1/2 ton heat pump, when I got there the coil was froze up. No sign of airflow restriction, coils were clean and also cleaned them even more. SO I assumed low on charge, added a litt… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,366 satisfied customers
Im looking for a FREON CHARGING CHART for a TRANE HEAT PUMP
I'm looking for a FREON CHARGING CHART for a TRANE HEAT PUMP MODEL# XXXXX The SUCTION LINE is HOT,the pressure reading at the SERVICE PORT at the REVERSING VALVE was 20 PSI and DISCHAGE PRESSURE was 8… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
In 85 plus degree weather and all things operating within normal
In 85 plus degree weather and all things operating within normal ranges-what should the temperature be at the copper discharge valve coming off of the compressor, on an infinity heatpump?… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,514 satisfied customers
I have a Rheem RAKA 048 condenser / RCBA 48 coil section system.
I have a Rheem RAKA 048 condenser / RCBA 48 coil section system. System is 16 yrs old, had icing problems. Tech diagnosed system had "issues" with metering device, contamination in system, and possibl… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,514 satisfied customers
The indoor coil of my Bryant 113ANA036 air conditioner is freezing.
Have a Bryant 113ANA036 air conditioner that was installed a year ago and went to look at it, and the indoor coil is freezing up.It is a Puron system, has good air flow, clean coil,the pressures is 32… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,514 satisfied customers
i just installed a new 2 1/2 ton heat pump 410 a with a txv
i just installed a new 2 1/2 ton heat pump 410 a with a txv airhandler. I have 30 feet of line set and my pressures are 120 suction and a 240 discharge. at 45 deg. outside ambient temp are these presu… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
what is the normal operating pressure for the suction and the
what is the normal operating pressure for the suction and the high side, split system conventaul unit w/ R-22?… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
problem unit iced. let it thaw out. gauges read 265/50. outside
problem unit iced. let it thaw out. gauges read 265/50. outside temp 104. inside 80. good air flow. added freon 22. discharge now 275 suction 50. diconnected txv bulb and exposed to out side air. no m… read more
Tom Goellner
Tom Goellner
owner
Vocational, Technical or Trade Scho
1,632 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

10,082 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.