My thermostat is blank today. AC was not blowing cold air

Customer Question
just blowing air and the...
My thermostat is blank today. AC was not blowing cold air just blowing air and the outside unit was just buzzing as if it could not kick on.
JA: Did you double-check the thermostat's settings? And what about the filters?
Customer: the hermostat settings were correct. Now the thermostat is blank. Filters are fine
JA: Do you plan on doing the work yourself?
Customer: Only if it's an easy fix.
JA: Anything else we should know to help you best?
Customer: That's about it. It's a trane xr12 unit outside
Submitted: 5 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
6/11/2017
HVAC Technician: Regan Land, HVAC Technician replied 5 months ago
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 707
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified

Hello and welcome to JustAnswer - My name is ***** ***** I'll be happy to assist you. Is the indoor unit easily accessible?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
it is.
HVAC Technician: Regan Land, HVAC Technician replied 5 months ago

Okay good - is it in a closet, basement, attic? And is the unit in a vertical position or laying on its side?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Is the start capacitor hard to replace? And how do I know which part to get? It's a trane XR 12. Model number 2TTR2030A1000AA
Customer reply replied 5 months ago
It's in the basement And is vertical
HVAC Technician: Regan Land, HVAC Technician replied 5 months ago

Start capacitors are easy to replace, but wouldn't cause the thermostat to go blank. Let's start by taking a look around the indoor unit for signs of water. There may be a small pan that has a float switch that may have water in it, or the floatswitch may be on the drain line. Let me know if you find anything. Do you have a multi-meter and feel comfortable using it?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I have the thermostat working again but the outside AC unit will not turn on. I just have air blowing in the house without AC. I figured out the thermostat went blank when I opened the door on furnace unit to check filter. Sorry I didn't tell you that.
HVAC Technician: Regan Land, HVAC Technician replied 5 months ago

That's okay! I'm glad that issue is solved. In that case, the start kit may be the issue, but there are several other possible causes. Does the outdoor unit stop buzzing when the thermostat is turned off?

Ask Your Own HVAC Question
HVAC Technician: Regan Land, HVAC Technician replied 5 months ago

Okay, have you opened the panel on the outdoor unit to see the electrical components? I'm hoping you just have something stuck in the contactor causing it to not be able to make a good contact. Can you take a pic of the electrical section and post it here? Do you happen to have a multimeter handy?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I will open the panel now and take a picture. No I don't have a multimeter handy.
HVAC Technician: Regan Land, HVAC Technician replied 5 months ago

Okay, no worries - Do me a favor and shut the high voltage power off to the outdoor unit. There should be a breaker or disconnect on the wall by the outdoor unit to do this. See if the buzzing stops when you torn the high voltage off.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
i shut that off and no buzzing.
Customer reply replied 5 months ago
Occasionally the unit "clicks" even with the power shut off.
Customer reply replied 5 months ago
I actually just have the 30A fuses pulled to shut off high voltage. That works correct?
HVAC Technician: Regan Land, HVAC Technician replied 5 months ago

Okay, I now think the buzzing is coming from the fan motor. That silver cylinder with the wires coming off the top is a dual run capacitor. The top of it (where the wires connect) should be flat - yours is slightly rounded indicating a bad capacitor. That one is a 45+5 x 440. You can find them all over the internet, or you can go to a local HVAC shop tomorrow to purchase one. Just make sure the power is off and that you put the wires back on the new one just like they come off the old one (terminals will be marked C, H, and F). Also, stay away from China made caps - the oil they use in them is not good. Stick with ones made in the USA.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Perfect. Thank you very much.
HVAC Technician: Regan Land, HVAC Technician replied 5 months ago

No problem! If you are satisfied can you do me a favor and rate my services? Thank you for using JA!

Ask Your Own HVAC Question
Customer reply replied 5 months ago
If this doesn't start up
The unit tomorrow can I contact you again through this thread?
Customer reply replied 5 months ago
I will be happy to rate your services! It's been great service.
HVAC Technician: Regan Land, HVAC Technician replied 5 months ago

If for some reason this thread closes then you can start another and request me - I'll make sure you won't be charged for the additional question.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Thank you!!
HVAC Technician: Regan Land, HVAC Technician replied 5 months ago

No problem! Let me know if you need anything.

Ask Your Own HVAC Question
Ask Regan Land Your Own Question
Regan Land
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 707
707 Satisfied Customers
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist

Regan Land is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a Nordyne gas furnace- unit mod#M1MB 077A AW - fails on
Have a Nordyne gas furnace- unit mod#M1MB 077A AW - fails on flame failure. Igniter glows,main flame comes on,goes into failure. When reset it will run for days and again have same problem. Could ther… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Imperial 80 plus gas furnace. New (2 yo) draft inducer fan
imperial 80 plus gas furnace. New (2 yo) draft inducer fan intermittently runs non stop, even with thermostat off. pressure switch? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Ruud furnace unit shut off while I was unscrewing the
My Ruud furnace unit shut off while I was unscrewing the cover for the blower. I did not shut the system off before I started unscrewing the cover. I did hit the shut off switch after the unit shut do… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have furnance is not turning on but making low humming
Hi..I have furnance is not turning on but making low humming noise..just researching it … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I waited too to change my filter, and now I'm getting a 3-1
I waited too long to change my filter, and now I'm getting a 3-1 status code on my Carrier furnace unit. How do I clear the code? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How do I determine my new Goodmn furnace unit blowing
how do I determine my new Goodmn furnace unit blowing capacity so I can match with the correct filter … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Just today for about 5 hours I am not sure where the outside
just today for about 5 hours I am not sure where the outside sensor is and how to reset it … read more
Regan Land
Regan Land
HVAC Technician
707 satisfied customers
I'm getting an e103 error on my Nest Thermostat been
Hi. i'm getting an e103 error on my Nest Thermostat been installed for 2 years. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Air conditioner outdoor unit makes noise! Noticed clacking
Air conditioner outdoor unit makes noise! Noticed clacking the pipe in the furnace unit which take the water out from ac coil side! We fixed the pipe and took all the water out! I turned on ac, am I e… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Can a high Static pressure on the return damage any part of
Can a high Static pressure on the return damage any part of a Carrier Enterprise Split System Unit when the outside unit has a two speed fan and the furnace unit inside in only a one speed? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Thank you for your time. i am trying determine where the
Hello and thank you for your time. i am trying determine where the placement of a Lennox Merit 14ACX-036-230 evaporative coils would be located within our home? The unit we thought would contain the c… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a model CL060-1b. I would like to know the diameter
I have a model CL060-1b. I would like to know the diameter required for the line set. Can you point me to a manual that has those specifications? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My friend installed my new rth6350/rth6450 thermostat and
Hi. My friend installed my new rth6350/rth6450 thermostat and it's not cooling down. I do not have a heat pump. Is the metal jumper to be completely removed if I only have the red wire. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier furnace unit and I want to know what size
I have a Carrier furnace unit and I want to know what size filter to use in it. I have been using the wrong size. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My newly installed goodman furnace had 4-blink error code.
My newly installed goodman furnace had 4-blink error code. The flame goes off every 5 minutes, and cool down for 5 minutes before the error code reset itself. We checked the exhaust pipe, return vent … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a question about my York diamond 80 furnace not
Hi there I have a question about my York diamond 80 furnace not working with my ac unit after installing a Honeywell lyric smart thermostat … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
We have a furnace in our mobile home. It started running
We have a Coleman furnace in our mobile home. It started running very got in the furnace unit itself. The pantry is next to the furnace closet and it got so warm in the pantry that it melted the choco… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox 10ACC unit with a G40 furnace unit. It is
Hello, I have a Lennox 10ACC unit with a G40 furnace unit. It is controlled with a Sure Light control board 10M9301. At times, the unit will suddenly stop working. When I look at the diagnostic lights… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x