On my Bryant Model 213C A/C, I have:
Reset the circuit breaker,
Replaced the fuses,
Replaced thermostat batteries,
Replaced the capacitor,
Replaced the circuit board. Our A/C unit is less than five years old, manufactured in 2013. Every time I've added a part. The A/C will start working again. But then it stops by the next day, and it won't turn back on. Will a clogged drain line cause an A/C to stop working this way? The filter was wet when I changed it, by the way.
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
5/11/2017
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,703
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello,I am a retired mechanical engineer with 56 years in this business. I will go in depth with you, and up to a 6 hour time limit.

All I ask is please select the ***RATING LINK*** at the top of your page before leaving, that is the only way I am credited through the site.

Rating does not affect your charges nor ability to refund if not satisfied. If you can agree to that, lets continue by all means.

Yes, a clogged drain line will cause the system to quit cooling IF there is a small float switch fit into the the condensate drain line at the cooling coil inside the house click here for some pictures

Rate that answer positively if you want up to 6 hours of coaching.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Excellent. Thank you, Phil! And yes, I may want some coaching. I'll let you know soon. Thank you, again.
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago

If it turns out to be a drain line issue, please rate my answer....its the only way the company pays me for my time. lacking that I loose my shirt on these questions

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,703
9,703 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,703 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My Rheem Mod #RQNJ-a048JK-000 is only blowing cold air. The
My Rheem Mod #RQNJ-a048JK-000 is only blowing cold air. The heater was working 2 days ago. Is there anything I can do before I call a tech? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My a/c system just stopped. My Honeywell thermostat does not
My a/c system just stopped. My Honeywell thermostat does not show the current house temperature just "--". Tried changing from A/C to heat mode but system will not turn on. My Lenox furnace appears to… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
My upstairs a/c stopped working. The fan is not turning at
My upstairs a/c stopped working. The fan is not turning at all. I recycled the circuit breaker with no luck. I went out to the unit looking for the fuses but didn't see anything in the wall box. Just … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Lennox 10HPB30-3P that won't turn on. I have
I have replaced the capacitors and relays on the unit with no effect. … read more
Phil
Phil
Mechanical Engineer
9,703 satisfied customers
I purchased a Lennox Elite 3 ton split system. Model cbx27uh
I purchased a Lennox Elite 3 ton split system. Model cbx27uh 036 6/02. Motor x13. (8/25/12) I have had a series of problems: - The installer indicated the breaker needed to be changed to 45 amp. - Was… read more
Phil
Phil
Mechanical Engineer
9,703 satisfied customers
Here are my HVAC details: Bryant furnace Bryant thermostat Carrier
Here are my HVAC details: Bryant furnace Bryant thermostat Carrier Condensation and outoor unit Problems: 1. Heat comes on, but thermostat reboots after a minute or so, fan makes a buzzing sound. 2. T… read more
heatncoolrepair
heatncoolrepair
Former HVAC Service Technician
Vocational, Technical or Trade Scho
75 satisfied customers
Runs for an hour or so and then blows fuse. Could it be a
Runs for an hour or so and then blows fuse. Could it be a misset thermostatt or perhaps a malfunctioning theromstatt. Have had for five or so years, had the circuit rewired, the machine checked - stil… read more
Phil
Phil
Mechanical Engineer
9,703 satisfied customers
My Bryant display keeps going blank(off) and our technician
My Bryant display keeps going blank(off) and our technician has checked the system with nothing wrong? What is going on? It is getting annoying. The whole system goes off and then comes on randomly… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier condenser Model 38CKC036350. Yesterday it
I have a carrier condenser Model 38CKC036350. Yesterday it stopped working due a clogged air filter in the blower. I replaced the filter last night, checked the circuit breakers, and went to sleep. To… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Hi- just replaced batteries in my Honeywell thermostat th5110d1006
Hi- just replaced batteries in my Honeywell thermostat th5110d1006 model. Unfortunately, I pulled unit off of the wall not realizing you can remove battery compartment separately. I easily snapped the… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Hi there, I have a White-Rodgers 1F89-211 thermostat. The screen
Hi there, I have a White-Rodgers 1F89-211 thermostat. The screen has gone blank and it seems like the A/C is off. I've tried flipping the circuit breaker and resetting the thermostat but it hasn't wor… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Coleman EB20B furnace. Intermittantly it wont go
I have a Coleman EB20B furnace. Intermittantly it won't go on. If I reset the breakers on the unit, it will sometimes go on. It may work perfect for a day or so. I can hear the heat strips go on but t… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Got a Bryant AC unit. Recently had a power outage and afterwards
Got a Bryant AC unit. Recently had a power outage and afterwards unit didn't turn on. Display said "lo batt". Replaced batteries and re-programmed per instructions. Unit won't turn on even when temp s… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Good morning, We bought a house with a Bryant 7-day programmable
Good morning, We bought a house with a Bryant 7-day programmable thermidistat dedicated to the central AC unit. Everything was working perfectly until we had an electrician upgrade the service entranc… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I turned off the blower fan a couple of days ago on my Bryant.
I turned off the blower fan a couple of days ago on my Bryant. Now it won't come back on. I've checked the battery on the thermostat, the filter was a bit dirty and I changed the filter. I have checke… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a 5 year old Bryant A/C system. Larger unit downstairs
I have a 5 year old Bryant A/C system. Larger unit downstairs & smaller unit upstairs. My problem is my air filter below the air handler was extremely dirty. So instead of getting a new filter to repl… read more
Ryan V.
Ryan V.
UA Local 350 Journeyman
High School or GED
6 satisfied customers
hello! we had a power outage because of storms...since then
hello! we had a power outage because of storms...since then (last night) my bryant a/c unit makes a buzzing noise...the furnace blower is working, all circuits are working...help!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Help!My Trane XR 85 stopped working!New unit-less than a year.No
Help!My Trane XR 85 stopped working!New unit-less than a year.No lights or sound.All circuit breakers & switches on.What do I do.The reset also no responsive.… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x