I have a Daikin Inverter and the heating Mode is not

Customer Question
available on the remote. Not...
I have a Daikin Inverter and the heating Mode is not available on the remote. Not sure when this happened but when I want to turn on the heating the symbol for heating doesn't eve come up on the remote...
Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
5/10/2017
HVAC Technician: MattR757, HVAC Technician replied 6 months ago
MattR757
MattR757, HVAC Technician
Category: HVAC
Satisfied Customers: 59
Experience: 18+ Years experience in residential and commercial HVAC service and repair
Verified

Do you have more than one indoor unit? You may have a mode conflict between the indoor units. - With multi-unit heat pumps the mode locks out so you can't have one unit in heating while another unit is in cooling.

Turn all of the indoor units to fan mode and then, after about 1 min when the outdoor unit recognizes that nothing is in cooling mode, the heat mode should be available.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
No no.I only have one unit.Simple installation. The only thing which is different now is that the heating mode is simply not available on the remote.
HVAC Technician: MattR757, HVAC Technician replied 6 months ago

It's possible that the outdoor unit board is locked into cooling mode, or possibly a setting has been changed in the programming. You could try powering off the outdoor unit for about 1 minute to reset the outdoor control boards and see if you're modes unlock and become available.

I will research the issue and see if I can find any other possible solutions. In the meantime another expert may have some suggestions

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I did try powering the outdoor unit down for 10 min and no change.
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, first make sure you have good batteries in the remote, if that fails remove the batteries from the remote and fit them in backwards for 60 seconds, then reinsert them in the correct position. Let me know how that goes.

(I will be out for about 2 hours, then I will get back to you)

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Hi Phil. It didn't work. Not sure what we can try next? everything is ok except that the heating sign doesn't come on on the remote when I am going through the modes....
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks, ***** ***** case a Daikin dealer would try a different remote, if that failed he would he would look for a blinking LED error code on the outdoor unit printed circuit board, if there were none he would replace the printed circuit board.

Diagnosis is not easy on these, if you can tell me the full model number of both the inside and outside units I can pull the factory manual on your system. click here.

We can go from there

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I couldn't find my model number in the link you sent. Inside Unit model number is ***** ,Outdoor unit model number is *****
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

click here for the Daikin error codes, if no error code is showing up, then the printed circuit board is most likely bad... that said, it takes Daikins factory test equipment to prove it.

If you need help finding a well rated Daikin technician in your area, tell me which direction you are from the center of the nearest larger town or city and I will search one up for you

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I am happy to change the PCB myself.Do you know where I can buy one for that part # ?
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Tell me please what large city you are nearest to. I will find you local parts source

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Hi Phil. I am in Brisbane ,Queensland Australia. Post code 4118
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

http://www.hhaircon.com.au/

This outfit is rated 4 out of 5 stars on 14 votes and is a Daikin dealer.

They should have the instruments needed to check the board out, either ask them to come out and do the diagnosis to insure that it is indeed a bad board, or take the board in to them for testing.

Let me know how it goes

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,824 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Goodman two stage gas furnace, 3 years old, currently is
goodman two stage gas furnace, 3 years old, currently is code in system status code says LO , its firing up but not staying on? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Which symbol on the Friedrich heating/cooling unit is for
Which symbol on the Friedrich heating/cooling unit is for heat? Thank you! … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a trane XL90 and it's not working properly. The
Hi there. I have a trane XL90 and it's not working properly. The igniter glows bright but once the gas valve opens (can hear it and smell it eventually) the glow stops and nothing happens. I have the … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have 30 year old gas furnace (no air conditioner). the
Hi, i have 30 year old bryant gas furnace (no air conditioner). the problem is that the fan doesn't stop. searched internet and learned that mostly the problem is with the fan limit switch. however, i… read more
Webb-Guy
Webb-Guy
tech.
72 satisfied customers
My thermostat is cycling on and off vert frequently, about
my thermostat is cycling on and off vert frequently, about 20 to 30 seconds each … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My lennox heater is not heating. The thermostat is set. I
The thermostat is set. I did not check the filter, but it is only 10 months old and the fan is running, when I just trun on the fan … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace 58mcb080-20 gas valve will not open... i
carrier furnace 58mcb080-20 gas valve will not open... i confirmed 24 volts going to valve... replaced the valve and same problem... i jumped 24 volts from the transformer and it opens no problem... n… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I tried to install new Honeywell WiFi thermostat
Hi. I tried to install new Honeywell WiFi thermostat th9320wf5003. And it doesn't show display. In … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Weil-Mclain boiler that keeps going int lock out
Hello we have a Weil-Mclain boiler that keeps going int lock out mode. It runs for about 20 seconds and then shut off with a solid red light. We now have an amber and red solid light. Can you help? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Lady hru? I'm troubleshooting an American Standard Freedom
Good evening lady hru? I'm troubleshooting an American Standard Freedom 80 furnace that's indicated to me the thermal protection device is open. What do I need to do to fix the issue? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My remote doesn't communicate with my unit. Its not the
My remote doesn't communicate with my unit. Its not the remote and I tried to re sync them several times. No luck. The unit will not turn on … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
952 satisfied customers
I have a Honeywell propane furnace and the pilot is out.
I have a Honeywell propane furnace and the pilot is out. Iwhen the propane guy came today he said it was an automatic electrical light one but it's not on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a question about an electric tankless or on demand
hello, I have a question about an electric tankless or on demand water heater … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My furnace won't start. Furnace is in attic. I disconnected
Yes, I disconnected thermostat and read no voltage on any leads … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Im trying to add a c wire to a EB15e. I just bought this
I just bought this place and im trying to install a smart tem … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
343 satisfied customers
I have a 19.9 Rheem 120 volt water heater it does not have a
I have a 19.9 Rheem 120 volt water heater it does not have a drain valve . how do I drain it ? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Quiteside minisplit shows E1 code when I switch it to heat.
quiteside minisplit shows E1 code when I switch it to heat … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
343 satisfied customers
Trying to install Honeywell lyric t5 wi fi thermostat to
Trying to install Honeywell lyric t5 wi fi thermostat to control heat pump with 7 wires … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
343 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x