I recently replaced my furnace control board. The furnace is

Customer Question
a Lennox G40-OUH and the...
I recently replaced my furnace control board. The furnace is a Lennox G40-OUH and the control board was a White Rodgers 50-A65-121-07. The only replacement was a White Rodgers 50A65-843 Universal Board that replaces all old 50A65 ignition control boards. The replacement went fairly well except that now the furnace is not communicating with the thermostat. There are no trouble flashing indicators on the furnace and it works great when power is on but no temperature control to shut it down. Please help !
Thanks much!
Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
5/4/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,766
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

Can you tell me what wires you have on what terminal (on the board) where the thermostat wires attach?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Sure, I could just send you a picture if that would be easier?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

thats fine...if you have ac also I will need to see those 2 wires as well at circuit board

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

you can attach any photos in this chat

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

thank you.

so when power is on...what runs?

blower

furnace/heat

ac?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
the blower and furnace/heat
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

if you remove the white wire from W...what does the unit do then when power on?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I have not tried that
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

can you try now and let me know?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
ok give me a couple minutes
Customer reply replied 6 months ago
Looks like nothing, it did not come on.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

thank you...sounds like thermostat shorted when board went, hook back up...then remove w at thermostat...if it does not run then you have a bad thermostat

Ask Your Own HVAC Question
Customer reply replied 6 months ago
ok, would it have shorted another thermostat because I went and bought a new thermostat thinking that exact thing and it didnt work either.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

I would know more once w is unhooked...

The thermostat connects R to W for heat...so somewhere there is a short..or bad stat...removing w from thermostat will tell us which

Ask Your Own HVAC Question
Customer reply replied 6 months ago
ok will do
Customer reply replied 6 months ago
do i keep w disconnected at the board?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

reconnect at board....then disconnect at thermostat

Ask Your Own HVAC Question
Customer reply replied 6 months ago
ok thanks
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

any luck?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
sorry I can't find the new thermostat anywhere, I have the old one but I don't know if it is fried it was the one that we were using when I replaced the control board. Don't know if it matters but I have been using the heat for several days without a thermostat hooked up by just flipping the power switch to the furnace, is that a no no?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

all I need is to have the white wire at thermostat not hooked to anything...or just remove the thermostat and tell me if the furnace still runs

Ask Your Own HVAC Question
Customer reply replied 6 months ago
it does not, I had the wires attached to the thermostat plate without the thermostat on and it would turn on when I gave it power. now i just removed the white wire from the plate at the thermostat and it does not turn on.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

then the white wire is clear and is only sending 24v to w on board due to a short at, in thermostat or wired wrong terminal.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
by terminal do you mean at the board? can you tell by the pictures if it is wired correctly, it is in the exact same position and color as the last one. and what do I do next?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 6 months ago

your wiring at the board is fine.

the issue is there was/is a short at thermostat....or the thermostat is set for heat..

removed w wire and furnace stopped....this means somewhere at the thermostat the red wire is touching to where it energizes the white wire....after seeing the yellow wire and green wires at the circuit board it appears they got hot during a short circuit at sometime.

Short story = the reason the furnace keeps running is not because of the circuit board.....it is at the thermostat, thermostat wired wrong, thermostat wire pinched behind wall plate etc.....the cause is at the thermostat area

Ask Your Own HVAC Question
Customer reply replied 6 months ago
ok because i hooked up the new thermostat if there is a short in the wiring could it have fried the new one as well?
or should it be ok? Also do I just go by the standard color code with the four wires as in the instructions of the thermostat?
Customer reply replied 6 months ago
are you still there?
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,766
22,766 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
How can I tell I my York furnace control board is the cause
How can I tell I my York furnace control board is the cause of the furnace not completing the heat cycle. It shuts down and give me the pressure sensor/switch code but two tech's have been out and ver… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,766 satisfied customers
Need help to reset White Rodgers thermostat. Temp not increasing
I have a White-Rodgers thermostat and for some maddening reason it has defaulted to running a program and says "hold" at 67. So even though I arrowed up the temperature (I want it at 72) but it will n… read more
Expert
Expert
This is the same guy with the Goodman furnace control board
Hi, this is the same guy with the Goodman furnace control board / transformer. My plumber said what caused the board to fail was a short in the blower motor from water from AC unit backing up into blo… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,766 satisfied customers
The down arrow on my white Rodgers thermostat will not lower
The down arrow on my white Rodgers thermostat will not lower the temperature. Model 1F80-261… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a White-Rodgers thermostat with the flap that opens
Hi, I have a White-Rodgers thermostat with the flap that opens to the menu. All of a sudden the temp of the room that the display shows on the left is not showing the temperature in Fahrenheit, but it… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My white rodgers 1f78 non-prgm thermostat won't work. The
My white rodgers 1f78 non-prgm thermostat won't work. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a White Rodgers !F-95-1291 Touch screen thermostat
I have a White Rodgers !F-95-1291 Touch screen thermostat with remote outdoor sensor. The out door reading is off by 10 degr F, too low. What's the prob? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an f8024 white rodgers, i am renting right now but
I have an f8024 white rodgers, i am renting right now but the unit worked last summer, i just replaced the batteries, but when i press the temp down button, nothing happens. … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
27 satisfied customers
I have a white/rodgers 8A05A -101 relay that I want to use
I have a white/rodgers 8A05A -101 relay that I want to use for a hot water circulating pump. The thermostat wiring is straight forward but the wiring for the 120 v is not. I have the following wires. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a Goodman GMNTE120-5 It has a furnace/control board
I have a Goodman GMNTE120-5 It has a furnace/control board with this part number B1809925two of the wires have come off two connectors, and the wires are the same color - trying to determine if it mat… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,766 satisfied customers
I recently replaced my furnace control board. The furnace is
I recently replaced my furnace control board. The furnace is a Lennox G40-OUH and the control board was a White Rodgers 50-A65-121-07. The only replacement was a White Rodgers 50A65-843 Universal Boar… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,766 satisfied customers
I have an amana furnace control board with an led flashing 3
I have an amana furnace control board with an led flashing 3 times … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
White Rodgers Thermostat 1f78-1151 is hooked up but not
I have a white Rodgers Thermostat 1f78-1151, I've hooked it up and it isn't working. I don't know if I wired it wrong. When I just connect the wires together the baseboards come on.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an old White/Rodgers thermostat that I'm upgrading to
I have an old White/Rodgers thermostat that I'm upgrading to a wifi Honeywell. All wires are labeled, but there is one labeled W that has no corresponding slot in the new thermostat. Is this W equal C… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,766 satisfied customers
We have a 15-20 yr old white-Rodgers thermostat wired to an
We have a 15-20 yr old white-Rodgers thermostat wired to an attic furnace; a pain to get to. We have to keep getting up in there to reset it. This time it's not coming on? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I need help with my -Rodgers furnace control board 50e47-060
I need help with my White-Rodgers furnace control board 50e47-060 on a Trane furnace. It has a blinking red light. On the unit it says " steady red light- replace control, blinking red light-referred … read more
type2technician
type2technician
253 satisfied customers
My white-Rodgers thermostat keeps failing. Sometimes it works.
The white-Rodgers thermostat keeps failing. Sometimes it works sometimes it doesn't. A company came to check and when they were here, it was working then it failed again. They check the HVAC in the at… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Changed batteries on White Rodgers Thermostat. It stopped working
I have a White Rodgers thermostat control model #1F78. Today the thermostat said batteries were low so I changed them. Now nothing works. I tried other batteries and nothing. I put the old ones back i… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x