I'm replacing a furnace blower motor and assumed it would be

plug and play. Old...
I'm replacing a furnace blower motor and assumed it would be plug and play. Old motor had 5 wires; white, brown, black, red and blue. The brown and white went to the cap, with another white wire coming from the furnace power box to the cap. The black went to the control panel, the blue was spliced to another wire from the power box and the red was taped. New motor is 1/3 hp, 1075, 3 speed, 115 volt Dayton motor and was the recommended replacement. It has more wires than the old one; white, brown, brown/white, black, red and blue. I wired it the same as the old one, except browns to either side of the cap and white to white. It hums and only starts when I finger flick it. Any ideas?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 13 minutes by:
4/25/2017
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 356
Experience: hvac technichian at performance plumbing and heating
Verified

hi I am dan I can help you with this. first is the white wire connected to the capacitor? if it is then remove it. also did you install the new capacitor or using the old one

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Old white wire attached to the old cap is now spliced to the white wire in new motor. New cap for the motor is installed.

ok does it work now

Ask Your Own HVAC Question
Customer reply replied 7 months ago
No, that was the original way I hooked it up. Still hums, but starts with a finger flick.

ok is the capacitor the correct size for the new motor?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Motor is a Dayton model 4M098 and the cap is the one paired to it; 5/370. I also tried a 7.5/440 and nothing.

ok try reversing the rotation and see if it works

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Not sure that will work. When I start it with my finger, it starts up no the correct rotation no problem.

that will not fix the problem it is just to test if it is a problem with the motor or the jumper plug. also make sure the plug is connected all the way

Ask Your Own HVAC Question
Customer reply replied 7 months ago
It threw a pretty nice spark and tripped the breaker. Switched it back and it is still trying to run.

ok what is the model number of the furnace

Ask Your Own HVAC Question

ok and the furnace is 115 volts correct?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Correct.

ok next put the jumper back the way it was, set the thermostat to fan on and disconnect the blue wire from the motor and test the opperation

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Nice spark and tripped breaker.

ok any further troubleshooting will require using a multimeter to trace out where the problemis

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Let me dig through my boxes. If I find it, I'll shoot another note.

ok let me know

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Not sure if you are still on, but I have a multimeter in hand

ok next can you take some clearer pictures of the wires and where they are connected and leave the blue wire disconnected so just the black white and capacitor are connected

Ask Your Own HVAC Question

ok next disconnect the black and white and connect the white to one meter lead and the other meter lead to the relay terminal and make sure you are getting 115 volts and then measure from the relay terminal to ground and make sure you are getting 115 volts

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Terminal and white = 0v, terminal and the old blue connection = 26v. Checked the multimeter in a socket and got 120v.

ok just to confirm the thermostat was still set to fan on and from the black wire terminal to the white wire from the furnace you had 0 volts? did you test from the black wire terminal to ground?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Correct. Relay to ground was 124v

ok there is a problem with that white neutral wire it is broken or disconnected somewhere. check that wire next

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Screwed that up. I have a new fangled thermostat that takes a while to kick in. 124v terminal to white.

ok now while the motor is disconnected ohm the motor between the black and white wire

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Not sure how to read resistance readings, with power on 0.0. Power off is 0.L.

power has to be off for continuity testing. disconnect the black and white wires for the motor. set the meter to ohms or continuity, attach one lead to the black wire from the motor and the other to the white wire from the motor

Ask Your Own HVAC Question
Customer reply replied 7 months ago
3.9 for resistance, 4.6 ohms continuity.

ok now reconnect the black wire to the terminal and the white wire to the white wire. leave the blue disconnected. the motor should run

Ask Your Own HVAC Question
Customer reply replied 7 months ago
It wanted to start up, but I had to spin it to get going.

ok then since you already tried 2 capacitors and it didn't work and then by reversing the rotation and it tripped the breaker then I would say the motor is bad. even though it is a brand new motor it must have something wrong inside it. everything is wired correctly and assuming the capacitor is good there is no reason why it shouldn't work.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Got it. I'll try a new one. Thanks for the help. How do you get credit for this?

ok good luck with it. let me know if you have any more questions about this. the only way I receive credit is by you rating my service by selecting one of the 5 stars on your page. thank you for using this service

Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 356
Experience: hvac technichian at performance plumbing and heating
Verified
Daniel Plourde and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Daniel Plourde Your Own Question
Daniel Plourde
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 356
356 Satisfied Customers
Experience: hvac technichian at performance plumbing and heating

Daniel Plourde is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,877 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Luxaire9v serires furnace Blower won't go into second stage.
Luxaire9v serires furnace Blower won't go into second stage. I replaced pressure switch and still no working. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace blower fan comes on without heat set point
Carrier furnace blower fan comes on without heat set point being triggered … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace blower stopped suddenly. I live in about 2,000sq
My furnace blower stopped suddenly. I live in about 2,000sq feet single family home. I called an HVAC technician. They arrived and installed a new motor. However, after they left I run the furnace and… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have an older luxaire commerical furnace blower motor runs
have an older luxaire commerical furnace blower motor runs all the time … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,877 satisfied customers
My furnace blower wiil not start. Hopefully. Furnace tries
my furnace blower wiil not start JA: Did you check the furnace's filters? Customer: no JA: Do you plan on doing the work yourself? Customer: hopefully JA: Anything else we should know to help you best… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My evcon furnace blower fan cycles every day at 8:20 with no
My coleman evcon furnace blower fan cycles every day at 8:20 with no demand and no exhaust fan operation. It just co es on runs for 2 minutes then shuts down, and there was no previous heat dema d … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Nordyne furnace blower starts immediately when I turn on
My Nordyne furnace blower starts immediately when I turn on the switch. The LED light on the control board flashes 5 times. There is no flame. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My '92 Carrier model 58ssc furnace blower motor has finally
Hi! My '92 Carrier model 58ssc furnace blower motor has finally quit. I wonder what I can replace it with … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a question about a furnace blower that is not
We have a question about a Bryant furnace blower that is not working. The model number is ***** We have noticed a blinking light error that has two short and four long blinks. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a loud noise coming from furnace blower motor. Do i
I have a loud noise coming from furnace blower motor. Do i need to oil up the motor? Its a lennox g40uh (x) … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I'm replacing a furnace blower motor and assumed it would be
I'm replacing a furnace blower motor and assumed it would be plug and play. Old motor had 5 wires; white, brown, black, red and blue. The brown and white went to the cap, with another white wire comin… read more
Daniel Plourde
Daniel Plourde
HVAC Technician
356 satisfied customers
My furnace blower won't shut off. Have confirmed it's not
My furnace blower won't shut off. Have confirmed it's not the thermostat (by disconnecting same). Could the fan relay cause this? … read more
derekh1966
derekh1966
0 satisfied customers
Our lenox furnace blower doesn't come on when on auto
Our lenox furnace blower doesn't come on when on auto setting. Still comes on when set to on. Ideas of what maybe going on? … read more
Tim Ohms
Tim Ohms
HVAC Journeyman
31 satisfied customers
My furnace blower will turn on but the AC condenser wont. I
My furnace blower will turn on but the AC condenser wont … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,877 satisfied customers
Furnace blower cycle on and off even when thermostat is in
furnace blower cycle on and off even when thermostat is in the off position. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Sometimes my mobile home intertherm propane furnace blower
Sometimes my mobile home intertherm propane furnace blower does not run and the unit gets really hot. Then after a while (maybe cools down) then the blower runs and things seem normal. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The furnace blower fan will not shut off even when the wires
Hi, the furnace blower fan will not shut off even when the wires are disconnected. (I am typing this for my Brother) he is working on the furnace. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Frigidaire Furnace - Blower starts running when heat is
Frigidaire Furnace - Blower starts running when heat is called, but there is no flame - Green LED flashing when heat called - Green and Red solid when no heat called… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x