I installed a brand new a/c system in a modular home in the…

Customer Question
I installed a brand...

I installed a brand new a/c system in a modular home in the keys. A 4 ton rheem with flexible duct through out the home. But my problem is the coils keep freezing after an hour or 2 of running. There return opening on the closet door is a 20x20 not sure if it's enough of a return but I have tried it with the closest door wide open and the coils still freeze

Contractor's Assistant: What's the make and model? And have you checked the settings recently?

Yes the pressures are perfect

Contractor's Assistant: Do you plan on doing the work yourself?

Yes I'm am a tech

Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 day by:
4/3/2017
HVAC Technician: Ricky Main,
 replied 1 year ago
Ricky Main
Category: HVAC
Satisfied Customers: 8
Experience: dasdasd
Verified

I would make sure the fan is on high speed. Is this a package unit and are you using any of the factory duct in the home or is it all new flex?

Ask Your Own HVAC Question
HVAC Technician: Ricky Main,
 replied 1 year ago

Also what is model number of unit you are using?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Don't have the model with me. It's all new flex roughly 33 ft of 6" and 20 ft of 4". With 2 outlets 6"and 4 outlets 4". Split system with the fan on high. Also I should add it's running on 407c
HVAC Technician: Ricky Main,
 replied 1 year ago

You have 1200 cfm's that must go thru the inside unit. Each 6" is only good for 60cfm and the 4" is good for 25cfm. That means you are only moving 220 CFM's. You need to either increase the size or add more taps.

Thanks

Ask Your Own HVAC Question
Customer reply replied 1 year ago
There's only room to add a couple more taps. But what if I reduce the fan speed would that help
HVAC Technician: Ricky Main,
 replied 1 year ago

No, that would move less air and make it freeze up faster. If you increased them all to 8" it would move 150CFM per tap. So 8-8" taps would give 1200 CFM.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
But the flex duct that is there is 6" and already covered by Sheetrock
HVAC Technician: Ricky Main,
 replied 1 year ago

Need to find a way to get rid of some air or put a smaller unit in. Need 400 CFM per ton so 2 ton would only need 800 CFM.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Do you think if I'm able to adapt the duct work by opening up the Sheetrock were the outlets are take put in 8" T's with the 6" flex duct and put (3) 8" outlets like that and try to add a few 4" would that help
HVAC Technician: Ricky Main,
 replied 1 year ago

No because the 6" going to the T is only capable of carrying 60 CFM

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My question is about a duct plan for 1140 sq ft apartment
My question is about a duct plan for 1140 sq ft apartment (second floor of a heated/cooled first floor with new double pane windows). I am installing a 2.5 ton AC to cool 6 rooms. My supply ell throug… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
13 year old funace Luxaire with a small (short) A coil.
13 year old funace Luxaire with a small (short) A coil. Compressor gave up the ghost after 24 years need to replace. A coil with compressor. Furnace maybe too tall. Is there a short A coil pairing for… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
working on an older nordyne electric furnace. mod # *****
working on an older nordyne electric furnace. mod # ***** installed a new 4 ton evap. coil with a new 4 ton condensing unit. this trailor system has 2 trunk lines, one right under the furnace and a 12… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hvac tech says valve in compressor unit is leaking on rheem
hvac tech says valve in compressor unit is leaking on rheem 3 year old air cond. although part is under warranty says it will cost 800.00 to fix… read more
A-1 Tech
A-1 Tech
Service Manager
Vocational, Technical or Trade Scho
361 satisfied customers
My A/C is less than two years old and works great. The problem
My A/C is less than two years old and works great. The problem is that at the Air Flow Intake (where the filter is) there is a strong smell of stagnant water and it is getting worse. It is a 4 1/2 ton… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Weve got pets that we have to keep separated, so one is always
We've got pets that we have to keep separated, so one is always in one of two bedrooms with the door closed. Recently, a modification was done to the ductwork for the Rheem furnace in the house by mai… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hi I have a nordyne e3 series downflow a/c and heat pump air
Hi I have a nordyne e3 series downflow a/c and heat pump air hendler. Model #E3EB-015H. The coils keep leaking water from the inside of the coil down onto the blower. Oh it is new has done this from d… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
K. Got a duct issue this time. In reference to "double wides"
K. Got a duct issue this time. In reference to "double wides" or modular homes, these days they are not built with metal walls and 1X2 boards. In fact, they are probably better insulated than a stick … read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
When it gets real hot my a/c wont cool no lower than about
When it gets real hot my a/c won't cool no lower than about 83 degrees. Is this normal? I just had a new coil put in.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Working on a modular home split system. This particular system
Working on a modular home split system. This particular system appears to be intentionally installed this way. The outdoor unit is a normal R-22 system. The indoor air handler only has half a cabinet … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Working on a modular home split system. This particular system
Working on a modular home split system. This particular system appears to be intentionally installed this way. The outdoor unit is a normal R-22 system. The indoor air handler only has half a cabinet … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a home office with a walk-in closet. The room is wired
I have a home office with a walk-in closet. The room is wired for computers and home theatre equip to reside in the closet. Currently, there is no return in the office (or closet), so the room heats u… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi, We just bought a home with a Coleman Furnace, model LM8S115C20DH11A
Hi, We just bought a home with a Coleman Furnace, model LM8S115C20DH11A installed. I don't know what type or where an air filter would go for this model. It is a downflow furnace.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Have a rheem RBHK-25J18SUY and would like a diagram or pic
Have a rheem RBHK-25J18SUY and would like a diagram or pic of how i should do the supply truck after the required 3 foot plenum directly connected to the top of the blower. Installing in a closet with… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
had a 5 ton ruud installed with a seer raqting of 11.2 and
had a 5 ton ruud installed with a seer raqting of 11.2 and it ran fine for 12 years. i replaced it with another 5 ton ruud with a seer rating of 13. at the same time i replaced the evaporator with a n… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Have a 2005 Nordyne GL1RA090C-16B gas furnace. Its in a hall
Have a 2005 Nordyne GL1RA090C-16B gas furnace. It's in a hall closet on main floor (center of house) behind normal 6panel door. When furnace on, the back of the door gets very warm. And, I see only fr… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I am building a new home. It has a 4 ton a/c package unit
I am building a new home. It has a 4 ton a/c package unit vs. a split unit. They are proposing to put the return grill location outside a closet wall behind a door. If the door stays open...no sense o… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
What causes a loss of cooling capacity to a central air conditioning
What causes a loss of cooling capacity to a central air conditioning unit? Mine won't go below 74 degrees. We have changed the compressor fan motor and capacitors as well as the thermostat. Help, we l… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x