My oil burner shakes the whole furnace when firing. All new.

My oil burner shakes...

My oil burner shakes the whole furnace when firing

Contractor's Assistant: Did you check the furnace's filters?

All new

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

It caught fire in the fall, I changed pump and shaft, also nozzle and electrodes . Its in my shop and only use a couple times a week.

Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
3/3/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,835
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

You're describing delayed ignition. Most common cause of this is improperly gapped electrodes. I need the brand of the burner to advise you on electrode gap setting. There are other possibilites some of which you can't address without very expensive test equipment but the electrodes are a good place to start.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Becket

1/8" apart, 5/16" above centerline, 1/16" ahead of the face of the nozzle.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
just to say, I have held plumbing lic,
Customer reply replied 1 year ago
could the air tube and nozzle play a part in the hard start

You could have a brand new nozzle that's bad (bad spray pattern) but I'd adjust the electrodes first, then replace the nozzle next. Nozzle assemby position in relation to the burner head and the type of head are also variables but are typically addressed when the burner is set up initially. These settings are to involved to spell out here. I'd have to refer you to the burner manual.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
ok, original was ,75/ 80 B. B being solid spray right, I bought 2 didn't matter, I will try electrodes. I have pump pressure at 100. small furnace. any last thoughts

That's about all you can do without test equipment except for testing the ignition transformer. You can check the transformer with a heavy (plastic handle) screwdriver, shut off the oil valve on the pump and put the blade of the screwdriver on one terminal of the transformer and hold the tip 1/2" away from the other terminal and hit the reset button. If the arc doesn't jump the gap then the transformer is weak and should be replaced.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
ok, thank you

You're welcome

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,835
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now

I'd appreciate a favorable rating

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,835
24,835 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an oil burner question, One week, Yes, Please connect
Please connect me with someone who deals with oil burner questions… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My beckett oil furnace flash blinking red light. I changed.
hi, my beckett oil furnace flash blinking red light … read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
GA-Sha I have a Rheem Classic oil fired furnace heating my workshop.
I have a Rheem Classic oil fired furnace heating my workshop. The furnace is mounted on top of the shop. I built the shop inside of a 36 X 48 steel building. It is 9 feet above the bottom of the tank.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
have Williamson furnace 1965 turns on. runs for about a minute
have Williamson furnace 1965 turns on. runs for about a minute then shuts off. never fires. no flame.… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
My Beckett oil burner fires up then quits after 3-4 minutes.
My Beckett oil burner fires up then quits after 3-4 minutes. I have replaced the CAD cell, the filter and the noozle and cleaned the ignitor rods. I don't think I bumped the rods and got them out of a… read more
GreenHeating
GreenHeating
Owner / Installer
Boiler / Steam Engineering
59 satisfied customers
I have a Laennox Elite Series 023Q3/4 105/120-6a oil furnace
I have a Laennox Elite Series 023Q3/4 105/120-6a oil furnace in its fourth season. The unit was serviced in late Dec after it had failed to start one morning. new nozzle ,filter ,return air filter and… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hi & thanks in advance for your assistance! The Wayne MSR
Hi & thanks in advance for your assistance! The Wayne MSR oil burner in my 1985 vintage Whirlpool forced air furnace is having an intermittent problem that I'm trying to fix before leaving for a short… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
Our hot air oil burner every 3+/- days blows cold air. The
Our hot air oil burner every 3+/- days blows cold air. The fan is blowing but the furnace is not producing heat. I f I hit the reset button (Honeywell R8184 M 1002 Intermittent Ignition Oil primary) i… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
oil fired fired furnace. ( steam). changed nozzle and oil tank
oil fired fired furnace. ( steam). changed nozzle and oil tank filter as usual. now will ignite fine with some smoke which disappears. then after running five minutes or so smoke reappears. never had … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Concord model r2 ever time yoou change the temperture on thermostat. yo
I have a Concord model R2 evertime you change the temperture on thermostat. you have restart and it will work a couple then quit. New Nozzel, New Filters, Adjusted igniters and to me when it starts it… read more
GreenHeating
GreenHeating
Owner / Installer
Boiler / Steam Engineering
59 satisfied customers
My oil boiler is not firing up and the lockout light is on
Hi, My oil boiler won't fire up. Lock out light is on. Have checked for fuel, changed nozzle, all to no avail. The burner goes through the motions of starting but just lock's out. Any ideas would be m… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
trouble shooting beckett burner on Lennox oil fired furnace.
trouble shooting beckett burner on Lennox oil fired furnace. found reset button tripped, unit tried to fire but locked out immediately. checked out control, determined I needed to replace the control … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
In servicing an oil furnace using a AFG Beckett burner, I am
In servicing an oil furnace using a AFG Beckett burner, I am experiencing a problem with fuel run on after or during ignition. At first I suspected improper setting of the nozzle/electrode assembly, f… read more
Robert
Robert
Associate Degree
161 satisfied customers
i have replaced pump electrodes filter nozzle transformer power
i have replaced pump electrodes filter nozzle transformer power supply box or what ever its called were the reset button is. still will not fire up?and the electric eye. now what. oh yeah it's a becke… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My fuel oil furnace fan comes on but the burner does not.
My fuel oil furnace fan comes on but the burner does not. I push the reset button and the burner fires and works for a minute or so and then the burner shuts off and the fan stays on. I do this again … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
About a month ago i started having problems with my honeywell
About a month ago i started having problems with my honeywell oil burner furnace it was getting fire then shortly after turning off red botton pop up. i asked a question here on just answers.... a day… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
i have a miller oil fired furnace with a wayne burner and i
i have a miller oil fired furnace with a wayne burner and i noticed that fuel drips out of the nozzle and works its way down the motor on the floor ,I changed the fuel pump switched fuel from #2 to #1… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have an oil fired furnace, with a Carlin Elite model Ez-1
I have an oil fired furnace, with a Carlin Elite model Ez-1 burner. It has been tripping the primary about once a day for two weeks now. I replace the nozzle a few times,my tech came did a complete cl… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x