I just finished the installation of a Goodman SXC1800481 AC

system. However, I cannot make...
I just finished the installation of a Goodman SXC1800481 AC system. However, I cannot make sense of the thermostat wiring diagrams. The schematic on the compressor unit shows connections to R, C, Y1 and Y2. However, my PRO T705 thermostat only has R, C, Y, W & G. What is the proper connection for these terminals so that I can start running the compressor unit?
JA: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?
Customer: It is a brand now AC system. The only code shown is "H8" meaning High Voltage???? I assume that it is a thermostat wiring issue.
JA: Do you plan on doing the work yourself?
Customer: yes
JA: Anything else we should know to help you best?
Customer: The manual on the thermostat indicates that the "Compressor Relay" should be connected to Y and C. The "C" connection is made between the thermostat and the compressor unit. Should either the Y1 or the Y2 connection be made to C???
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
1/8/2017
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,232
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Russ here . Need to get a different thermostat that will handle 2 stage unit. Honeywell focus pro 5000 will work. For now to run cooling just connect yellow wire to unit and place a jumper between Y1 and Y2. This will work till you get a new thermostat. Russ

Ask Your Own HVAC Question

Anymore questions. Russ

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Nope. You nailed it !

Graet. If nominee questions please rate my answer. Installing one of those SXC 18 tomorrow. Thanks. Russ

Ask Your Own HVAC Question

Glad its working. Great job. If no more questions please rate my answer. Russ

Ask Your Own HVAC Question

Do you still need help. Russ

gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,232
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified
gotoman for ac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask gotoman for ac Your Own Question
gotoman for ac
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,232
5,232 Satisfied Customers
Experience: 51 years of experience install design and repair of all makes and models of AC

gotoman for ac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Goodman two stage gas furnace, 3 years old, currently is
goodman two stage gas furnace, 3 years old, currently is code in system status code says LO , its firing up but not staying on? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Which symbol on the Friedrich heating/cooling unit is for
Which symbol on the Friedrich heating/cooling unit is for heat? Thank you! … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Honeywell chromotherm iii thermostat. I am getting
I have a Honeywell chromotherm iii thermostat. I am getting an intermittent AC error message. At times the heating system functions perfectly the the error message appears and it's done. Then after a … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I just instaled a new Payne furnace and a/c condensor. The
I just instaled a new Payne furnace and a/c condensor. … read more
David Bowden
David Bowden
Owner
325 satisfied customers
Im hooking up a Goodman SSZ140481 system to a Honeywell
Im hooking up a Goodman SSZ140481 system to a Honeywell RTH6580WF thermostat. The wiring is funky. Previously the wiring was connected to an Aprilaire 8446 non-programmable thermostat. The wiring was … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a central a/c model brcq0241be and my dog was digging
I have a coleman central a/c model brcq0241be and my dog was digging and tore out the thermostat wiring out of the control box I need to know how to wire it back up. I have three wires coming from in … read more
HvacmanSean
HvacmanSean
Owner
HVAC
219 satisfied customers
Need low voltage wir,in diagram ton electric Raheem air
Need low voltage wir,in diagram for 5 ton electric Raheem air handler with 20kw strlps … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My name is ***** *****. I'm trying to wire my nest
Customer: My name is ***** *****. I'm trying to wire my nest thermostat to my existing White-Rodgers Zoned Heating system … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Taco SR502-4 2-zone switching relay on an oil fired
Good afternoon! I have a Taco SR502-4 2-zone switching relay on an oil fired hot water heating system. I'm trying to connect a Honeywell Smart WiFi thermostat. I have three conductors at the switching… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Lennox 65f9801 with heat pump to honeywell rth7600d1030
lennox 65f9801 with heat pump to honeywell rth7600d1030 thermostat wiring diagram conversion… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
outside heat pump will not turn on, electric heat works OK,
outside heat pump will not turn on, electric heat works OK, no air conditioning or normal heat… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Need help for the local furnace people are not able to get
Need help for the local furnace people are not able to get it right. I am trying to wire a Filter 3m-50 thermostat to a Trane system up. Now they have the Black and White wire shorted together on the … read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
399 satisfied customers
I need a Hunter thermostat wiring diagram. I am trying to install it
I'm trying to install a Hunter thermostat, Model 44155C. I have 5 wires coming out of the wall and do not know how they hook up.… read more
jrloar
jrloar
Master HVAC Tech.
Associate Degree
15 satisfied customers
I purchased a Honeywell Model TH8110U thermostat to replace
I purchased a Honeywell Model TH8110U thermostat to replace the one currently in use. The thermostat controls a single stage heating and cooling air to water heat pump that is 30 years old. Installati… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Hi. Ive got a two-stage burner carrier natural gas furnace.
Hi. I've got a two-stage burner carrier natural gas furnace. It originally was wired with just three wires (red to r, white to w/w1, and green to g). I'm in the market for a new thermostat and am tryi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Im installing a WR stat IF95-1291 with Hum control on a system
I'm installing a WR stat IF95-1291 with Hum control on a system with a True Steam HM509A, the wiring diagram for the HM509A shows 2 Hum terminal to wire to the humidstat. If I connect the HM termial o… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I need a good thermostat wiring diagram that will mate a Rheem
I need a good thermostat wiring diagram that will mate a Rheem RPKA-036JAZ heat pump unit with a Rheem RBCA-1J15sFAA inside unit with heat strips to a RObert Shaw model 9515 Tstat. I would like a simp… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I am working on a american standard heat pump/a/c unit with
I am working on a american standard heat pump/a/c unit with a propane furnace, when it starts the heat pump comes on even though its very cold outside 5f and then the propane starts also, I am an hvac… read more
Roger (Mr. Fixit)
Roger (Mr. Fixit)
Service and Sales Manager
Bachelor's Degree
16 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x