I have a Ruud 92% eff furnace that's been operating for 4 years, There's been no changes electrically to the furnace or house. Now I am getting a code 26, saying the neutral is reversed.
Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
11/27/2016
HVAC Technician: Gaztech, HVAC Technician replied 11 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 511
Experience: Owner at Gaztech
Verified

Welcome to Just Answer, my name is Luke

NOTE: I can only get credited for assisting you if you click the 5 star rating at the top of page if we are done

Are you ready?

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 11 months ago

Shut power off to furnace, open cover box where the 120V wire enters the furnace, check all connections, White to white, black to black, then proper ground wire connection. restore power and check if code still there.

If still there.. shut power off again and reverse wires in same box White to black ..

restore power and try.

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 11 months ago

Hope you got system going by now, can we close question?

NOTE: I can only get credited for assisting you if you click the 5 star rating at the top of page if you are satisfied with my answer

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Your answer was not helpful. It did not seem like you read the question. The furnace has worked for 3 years and there has been no electrical changes. It tried your suggestion and of course it did not work.
HVAC Technician: Phil, Mechanical Engineer replied 11 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, This is not an answer... it is step one of what could turn out to be a many step diagnostic process.

if the error code did not go away when you reversed white and black as the previous tech suggested, then it is probably a bogus error code, or some sort of shorted wire inside the furnace... since there have been no wiring changes in the house, all this points to a bogus error code due to the printed circuit board going bad.

That said it is possible that a 120v cord cap (plug) is wired incorrectly on a new appliance in the house, that can also result in reverse polarity.

Click here for a superb video on the topic

Next step is to do a heat stress test on the printed circuit board, use a hair drier to warm it slowly and gently to 120F, if there is any chance in behavior or the error code goes away etc, the board has a micro crack in one of its circuits that expanded when the board was warmed up.

We can go from there. I am off to bed shortly and will be back at 7 am

Regardless

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,824 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a electric furnace. The heating elements come on but
I have a coleman electric furnace. The heating elements come on but the fan does not run. The fan runs when you run it manually or with the A/C turned on. What sencer needs changed? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an Englander MDL 13-NCH 6" pipe. I have always been
I have an Englander MDL 13-NCH 6" pipe. I have always been confused about the connection on the top of the stove to the black pipe. It doesn't seem to fit tight inside it and I get some blow back smok… read more
Paul the Plumber
Paul the Plumber
Vocational, Technical or Trade Scho
21 satisfied customers
My Rodgers digital display thermostat does not display
My White Rodgers digital display thermostat does not display anything. The house is getting colder. The fan will turn on. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Thermostat will not shut off heat even though it is in the
thermostat will not shut off heat even though it is in the "off" position. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have a Trane TEM4 air handler. The blower motor runs
Have a Trane TEM4 air handler. The blower motor runs constantly. I have changed the control board, the transformer, and the contactor. The blower still runs continuously even when the thermostat is se… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
344 satisfied customers
Rheem RRNA-Bo36JK08E not blowing hot air. Fan and A/C works
Rheem RRNA-Bo36JK08E not blowing hot air. Fan and A/C works but no air on heat. Outside unit turns on but blows no air through inside vents … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm pretty sure my flame rollout switch is open but I can't
I'm pretty sure my flame rollout switch is open but I can't seem to find the reset button … read more
Gaztech
Gaztech
HVAC Technician
511 satisfied customers
HAVE A TRANE XL 80 REPLACED THE PART 50A51-495 WHICH IS NOW
HAVE A TRANE XL 80 REPLACED THE PART 50A51-495 WHICH IS NOW OBSOLETE WITH PART CNTO7566 THE PART IS NOT IDENTICAL TO THE ORIGINAL BUT IT IS INSTALLED AND THE FURNACE WORKS MY QUESTION IS WHY IS THE RE… read more
Gaztech
Gaztech
HVAC Technician
511 satisfied customers
I have a Rodgers Tstat model-63136 type-1F97-1277 my heating
I have a white Rodgers Tstat model-63136 type-1F97-1277 my heating setpoint is 68 degrees my space temp is at 80 degrees and the heating won't shut off. Dispay on stat says 79 degrees temp limit. Is m… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I'm a service technician that just installed the new
I'm a service technician that just installed the new th4110u2005 and whil programming the installer set up I opted for the partial lock out because it's going in a church and now I'm locked out with n… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We just installed goodman hot air propane furnace and glow
we just installed goodman hot air propane furnace and glow light is not blinking steady red but it wont fire … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a constant blinking light and will not start furnace
I have a constant green blinking light and will not start furnace evan if push button … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Goodman gpg153709041AA that will not go past the
I have a Goodman gpg153709041AA that will not go past the vacuum pressure switch. When the thermostat calls for heat the inducer start and draws vacuum. The pressure switch closes but that where the s… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have tried to turnt the boiler and when I turn on the
Hello, I have tried to turnt the boiler and when I turn on the boiler only the gas valve … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How do I unlock my Luxpro Thermostat?
How to unlock a Luxpro PSP511LC thermostat? The on-line manual says to use this key sequence: up, down, next, hold, rotary dial, and software reset. But it does not work. How do you key a rotary dial?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Phi, I have a HW Vision PRO IAQ. We had a power outage a few
Phi, I have a HW Vision PRO IAQ. We had a power outage a few days ago. The screen on the Pro IAQ is blank. I changed the battery and the screen light up and was functioning. This morning the screen is… read more
Webb-Guy
Webb-Guy
tech.
77 satisfied customers
Tappan furnace isn't staying on. Red light on panel blinks
Tappan furnace isn't staying on. Red light on panel blinks four times. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My American standard freedom 80 two stage furnace is very
My American standard freedom 80 two stage furnace is very sporadic. I have changed ignitor, flame sensor, and filter. 50 percent of the time it will not reach set temperature and short cycles giving a… read more
Gaztech
Gaztech
HVAC Technician
511 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x