I have a Trane X90, model # TUC080C942 B2
I previously went through trouble shooting and replacing a limit. (see pic). (I would think you can see the discussion in my previous questions.) The guy at the HVAC supply store said he hasn't seen many of those fail. I installed it and it worked fine. Maybe not quite as warm as before.2 weeks in, I notice cold air blowing again in the morning. I'm pretty sure it started the cycle warm. First thing I tried was to bypass the limit I just replaced. Everything came on like a charm. I tested the limit, after taking it out, with a multimeter. no flow.As I was taking off the piece of wire that I bypassed with, it touched part of the furnace body and sparked a little.When I got the new limit, I installed it and tried to turn it on. Nothing.I went and bought real, insulated test leads this time. I tried the R and W bypass and it worked fine.What am I dealing with?
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
11/19/2016
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,894
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

so at this point it only runs with r and w bypassed?

And I did not see pic of the part replaced...is it a limit or a rollout?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
34;it" being the jpg photo)
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

Ok,

May have some bad news..that is a porcelin roll out switch. It detects when heat rolls the wrong way backwards from the heat exchanger.

This is a "one and done" switch. If it trips more than once the odds are great that you have a bad or plugged heat exchanger (both are bad).

As far as running with r and w shorted together, this means the thermostat was compromised when it shorted to ground and you need a new thermostat......BUT.....I would have the exchanger checked before investing anymore money in the unit.

The roll out is the one switch we never want to see trip because it means main heat exchanger problem..

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Is there a way I can check to see if its plugged?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

If it is plugged it is in the secondary heat exchanger...you can attempt to apply as much suction to the drain direct from furnace...using a shop vacuum.

Also you can tell by studying flames as they come on.....if you see them dance when the main blower kicks on or turn tips yellow it means a crack in exchanger. Even if plugged it is a heck of a job...I have had to remove the entire exchanger and flush and then reinstall...full days job..

Ask Your Own HVAC Question
Customer reply replied 1 year ago
How dangerous is it to run it with the rw bypassed, Briefly and watched.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

no danger at all to run with r and w bypassed...it just will not shut down.

The danger is if you bypass the rollout switch.....then we get into potential fire and carbon monoxide issues.

R and W is simply taking the thermostat out of the loop....Just please do not bypass the roll out or main limit.

Billy

Ask Your Own HVAC Question
Customer reply replied 1 year ago
No, I understand the need for the roll out switch. Thanks for the concern.
I just wanted to make sure regarding the thermostat.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

I apologize as it is much easier for me to give advice that saves money..But this is entering in to the dividing line of major repair or replacement.

I certainly wish you the best and feel free to stop back if further info is needed.

Just rate service to move off the active list.

Billy

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Would that have anything to do with the air temp not being quite so hot?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

yes...it is directly tied to the main heat transfer component. Basically this is the equivalent of a bad motor in a car...

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Did you review my previous discussion? I wish I would have had this info then. I would have called a tech at that point.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

I just went back and reviewed and you are correct.

As soon as the roll out was identified as being the culprit, everything should have ceased at that point.

I apologize, but then again I am old and have been working on these unit s along time...

Anything after finding an open rollout was likely putting off the inevitable...

Ask Your Own HVAC Question
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,894
22,894 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Centurion 2 not working with the flashing indicator
I have a Centurion 2 not working with the green flashing indicator 4 time. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Collector flue box gets extremely hot to touch. It's a
Collector flue box gets extremely hot to touch JA: Just to clarify, what type of fireplace is this? Customer: It's a furnace JA: Do you plan on doing the work yourself? Customer: Yes JA: Anything else… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,894 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
In 2003, we had a new high-end Carrier Infinity Weathermaker
In 2003, we had a new high-end Carrier Infinity Weathermaker furnace installed - Model 58MVP-100-20 (run on propane). 8 years later, in 2011 - while still under warranty (parts and labor) the main hea… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Funky smell coming from heat exchanger outside...... repair
funky smell coming from heat exchanger outside...... repair guy said the gas not m ixing with the air properly..true? said probably just clogged … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,894 satisfied customers
Heat exchanger is a month old and heat stopped working.
Heat exchanger is a month old and heat stopped working. Three lights are blinking saying it is a limit or rollout switch … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a property with a Keeprite heat exchanger installed.
I have a property with a Keeprite heat exchanger installed. I believe the filter is clogged but I don't know where it's located. The model is PGF018K040E … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
How can I clean the inside of the heat exchanger on my
how can I clean the inside of the heat exchanger on my furnace? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My carrier heating heat exchanger is plugged. I understand
My carrier heating heat exchanger is plugged. I understand it is civered under a recall action. if bI purchase a new systeem 59mn7a080-20 what price drduction do I receive? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How much time should be allowed to change a heat exchanger
How much time should be allowed to change a heat exchanger for a 48tjf016 series 580ba and 2 men?… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have Yorx High efficiency tubular heat exchanger, im not
Hi, my name is***** have Yorx High efficiency tubular heat exchanger, im not sure wich model though GY9S , GM9S, or GF9S. There is water leaking from the white PVC pipes, can I just cut them out and r… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I was looking into a trane tud060 heat exchanger and noticed
I was looking into a trane tud060 heat exchanger and noticed a buildup of white powder at one of the factory seams and need to know what is causing this. I attached a pic. Thanks… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,894 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x