HVAC

Have HVAC Questions? Ask an HVAC Expert for Answers

Ask an Expert,
Get an Answer ASAP!

HVAC
This answer was rated:

Nordyne furnace pressure switch open with inducer on is the

code and I have changed...
nordyne furnace pressure switch open with inducer on is the code and I have changed out the switch and still the same code
JA: Did you check the furnace's filters?
Customer: no but they were changed recently
JA: Do you plan on doing the work yourself?
Customer: yes
JA: Anything else we should know to help you best?
Customer: fan motors starts but there is no iginition or glow plug lighing up that I can see
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
11/6/2016
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,017
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Thre are several thing that can keep the switch from closing, they are: a blocked or partially blocked exhaust vent, a weak draft fan, a clogged port where the other end of the tubing connected to the switch is attached to the furnace. You don't give me a model number so I don't know if this is a condensing furnace but if it is a clogged exhaust condensate drain can also keep the switch from closing

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Rick
the unit is a Nordyne and the Model Number is ***** 6RC 100C-16B I have cleared the intake and exhaust vents as it is a 90% furnace. I have switch out the pressure switch with a replacement from Nordyne and nothing changed. I am a licensed general contractor but don't really know too much about HVAC I guess I know enough to be dangerous. All that happens is that the fan motor starts like it going to turn on the blower but just never does and I get the flashing signals on the mother board don't really know what else to do

Did you check the condensate drain? If it's clear then then you need to check where the vac tubing on the switch connects to the furnace. You can poke a paper clip into the ports (not into the switch). Beyond that you'd need a maometer to check the draft pressure to determne if the fan is doing it's job or not.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I cleared the drain already and tried to did the paperclip thing to no avail is there a lockout mechanism on this board and is there a way to reset it?

You reset by powering the unit down waiting a couple minutes then power it back up.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
How can bleed the gas lines to make sure gas is coming in properly I really dont' think its getting gas to the unit. I usually turn my gas off over the summer cause we have electric heat but this year I didn't and when I turned on the unit for the first time it came on for like 5 minutes and then this problem started. Is there a valve or something on the unit to make sure gas is actually flowing to the unit? And if its not getting gas to the unit could that cause the error code I am getting. Just trying to think of all options before I spend 200 on a meter

If gas supply was an issue you'd get a different error (failed ignition). Your unit hasn't made it far enough into the sequence to ignite. You might want to call in a pro instead of dropping all that money on a manometer.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Well I'm at the point where I have to defeat this issue LOL so I get the meter and it tells me not enough pressure is somewhere what is the next step? I actually want to learn how these things work so that is why I want to figure this out

If you're sure the vent/intake is clear then a poor draft reading would indicate something is in the fan itself or you need a new fan.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
The fan does kick and it doesn't sound any different than it use to and I'm sure I cut the intake line and cleared it because it did have a wasp net on the pipe going to the outside. I can't get into the box that holds that line to see if there is something else in there as the panel won't come off. The box is at the top of the unit and has a clear glass circle in it but I really can't see in even with a light. I removed the black 2 inch hose from the fan as it was clean with no debris. So I know I'm close and I dont' think a new fan is going to solve the problem. But what Do I know that's why I'm talking with you

Just to test try disconneting the exhaust and intake pipes from the furnace and restart it. If the unit advances beyond the pressure switch error (igniter initializes) then you need to dig deeper into the exhaust/intake pipong. You can try a shop vac to suck out the piping.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Will do later on tonight when I get home from work and get back with you

Ok, disconnect them 1 at a time then both if needed. Start with the intake

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Intake is already disconnected and I know that line is clear I was going to remove the hose again from the fan and shove the shop vac up there and see if there is any blockage

Ok

Ask Your Own HVAC Question
Customer reply replied 1 year ago
RIck I will be getting back to this tonight been busy with work and its been in the 70's the past few days here but I want to get this fixed asap

I'm online until about 7 pm EST. I'll respond as soon as I can

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Ok Rick so I have isolated the problem I do believe, when I was doing my initial check of the vents and everything I found a yellow jacket nest in the intake vent, and when I took off the vent tub to the intact I found a honey comb in there so its safe to say they have covered up or nested in something important in the top box of the furnace Ive taken off all the screws on the front but the cover does not want to budge there are two more screws at the bottom but i wanted to confirm with you that this part of the unit is accessible attached is a picture of the box with the glass on it at the top of the unit. Ok well it won't let me attach a picture anyway I do believe this will solve the problem if I can get that nesting cleared Ive already tried to vacuum it out and got a little but I those things are pretty strong so can I access this area of the unit?

If you're referring to the box the exhaust fan or intake is attached to then yes it can be removed but the gasket behind it and the gasket on the fan housing must be tight when you put it back together to avoid exhaust leaks.
I'd appreciate a favorable rating.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I got it off looks pretty clean in there and still tripping the same code so now what? Nanometer?

If you're sure the exhaust and intake are clear along their entire length then next step would be to replace the pressure switch (assuming you're sure its tubing is open/OK). We would put a manometer on the exhaust but they are pretty pricey so if you don't have one a new pressure switch would be a lot cheaper.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
ok I did buy a new switch but took it off and put the other one back on because I thought that was not the problem I will put on the new one and blow all lines clear and see what happens

ok

Ask Your Own HVAC Question
Customer reply replied 1 year ago
GOT HEAT cleared a T and the line to the burners and that did the trick
Thanks RIck I will leave a positive feedback

You're welcome

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,017
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,017
23,017 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Aire flo Gas furnace and it is stating that furnace
I have a Aire flo Gas furnace and it is stating that furnace pressure switch open with inducer on. check the hoses,connections, made sure the vents not obstructed. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Furnace turns off after running for a minute. Or won't turn
Furnace turns off after running for a minute. Or won't turn on at all. Power outage a couple days ago seems to have started the problem. Sometimes getting a 4-flash error code … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Nordyne,furnace, pressure switch open fault is
I have a Nordyne,furnace , pressure switch open fault is indicated. The model of furnace is KG7TC120D45D it is about 6 yrs old., had Hvac Tech come out just about 2 weeks ago. Furnace was firing up. W… read more
Rick
Rick
HVAC Supervisor
23,017 satisfied customers
I have two furnaces each 20 years old both are not working
I have two miller furnaces each 20 years old both are not working all of a sudden … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My rheem furnace will not light. We ran out of propane
My rheem furnace will not light. We ran out of propane because of a faulty gauge and ever since the heater will not work.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Second opinion] My furnace rubs but there's no heat, Yes iv
Second opinion] My furnace rubs but there's no heat … read more
HvacmanSean
HvacmanSean
Owner
HVAC
226 satisfied customers
I have an older Trane Gas furnace. Tech service has not been
I have an older Trane Gas furnace. Tech service has not been able to find out why my furnace will not fire all the time. It will work sometimes , other times not. They have replaced most things they t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Our heater will not heat up it is indicating pressure switch
Our heater will not heat up it is indicating pressure switch did not close or reop … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an Armstrong V tech 80 furnaces. Runs OK but
Hi Richard, I have an Armstrong V tech 80 furnaces. Runs OK but sometimes gives 3 flash pressure switch error and then requires several tries at the thermostat until it finally gets going again. It wi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Echelon 8.s is doing a something similar to the customer
My Coleman Echelon 8.s is doing a something similar to the customer here. We replaced the flame sensor and the pressure switch(as the red light flashing slow 3 times indicated was the problem) and sti… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Phil. I'm replacing my furnace pressure switch on my heater
Good Evening Phil. I'm replacing my furnace pressure switch on my Bryant heater FS6675-1320 Pressure Switch HK06WC076....with a universal one.....I know how to wire it, and which side to connect the v… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm back. LOL!! Ok it took me a minute but I finally
Hey there I'm back. LOL!! Ok it took me a minute but I finally replaced the Inducer motor just moments ago. I am still getting code 31. I repeated the test you had me to do and it still only runs for … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace is out. It is running but blowing cool air. It
Hi! My furnace is out. It is running but blowing cool air. It has a message on the thermostat that says FURN LO PRESS OPEN … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a Lennox g24m3-75a-4. One of your techs helped me
I have a Lennox g24m3-75a-4. One of your techs helped me diagnose a bad thermostat a month ago. Changed it out. It's worked fine on heat and air since until yesterday. When set to heat the thermostat … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a American Std. freedom 80 furnace that was having trouble
I have a American Std. freedom 80 furnace that was having trouble staying on line, it was cycling on and off, we tracked that issue to a dirty flame sensor so we cleaned that with some steel wool and … read more
Expert
Expert
i have a carrier 58sta/stx furnace. Its flashing code 23 and
i have a carrier 58sta/stx furnace. Its flashing code 23 and will not light. Pressure switch is good. Bad board or cracked exchanger?… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Gas furnace pressure switch and tubing. My pressure switch
Gas furnace pressure switch and tubing. My pressure switch keeps shutting the furnace off. I remove the rubber tube from the circulating fan, blow it out and put it back which solves the problem tempo… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have Goodman model GMPN080-4 the condesation drain trap and
I have Goodman model GMPN080-4 the condesation drain trap and the furnace pressure switch keep filling with water even though the water to the dehumidifier is turned off and the drain trap fills in ab… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x