I have a Trane XL90 model TUC100B960A0 Furnace. I was told

Customer Question
by "HVAC Guru" (justanswer.com HVAC...
I have a Trane XL90 model TUC100B960A0 Furnace. I was told by "HVAC Guru" (justanswer.com HVAC Technician) in May that my board needed to be replaced due to non-start condition. I have purchased a White Rogers Model 50E47-843 to replace my White Rogers Model 50E47-060. I am having problems identifying the correct wire conversion from the old to new board.
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
9/25/2016
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,888
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is ***** ***** I will do my best to assist you. I am looking over your question now and will respond shortly.

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

what particular wires do you have an issue with?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
On my old Board 50E47-060 I had the following blade connections;MV
MV
TR
TH
FP
GND
L
ING
Customer reply replied 1 year ago
On my new board 50E47-843 I have the following blade connections;MV2
TR
GND
TH
MV1
L2
HS2
FP
L1
HSI
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

Thank you...now just to assist as go along.

Did you have this in with the new control?

See Here

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

MV - mv 1
MV- mv2
TR -tr
TH- th
FP- fp
GND - grnd
L - L1

ING - hsi

are there others?

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

does that help at all?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
please. I need help knowing which wires go where.I currently have the following connected;MV2 - Red wire going to gas valve transformer
TR - White wiring going to pressure switch / induction fan and ties to W on 24v thermostat board
GND - Light green wire going to ground
TH - Light purple wire going to B/C on 24v thermostat board
MV1 - Light blue wire going to gas valve
L2 - Ground to frame via pigtail included in replacement board kit
HS2 - Not used
FP - White wire to flame Sensor
L1 - Large red wire going to limit control
HS1 - Large blue wire going to Igniter
Customer reply replied 1 year ago
I have the manual. With the wires connected as stated in my previous text it throughts the breaker on the main house panel.
Customer reply replied 1 year ago
Pretty sure I have something crossed somewhere.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

the terminals you have connected are all low voltage and would not trip the breaker except for L1 and L2

Your white wire from power...that needs to go to L2 on the board

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Ok. Let me check.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

and Hs2 should have a wire from ignitor on it

Ask Your Own HVAC Question
Customer reply replied 1 year ago
L2 is green going to grounding on furnace cabinet based on note "e" listed at bottom of the table you sent me.
L1 is Large Red Wire going to black wire that goes to main power coming from on/off switch on side of the furnace.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

the note E is if there is NO l2 terminal available. But on this control board there is a L2 terminal.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Ok. I am removing the the green ground to furnace jumper wire I added.
Customer reply replied 1 year ago
Removed.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

You said hs2 was not used...where is the other wire from the ignitor?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Nothing attached to L2 and still throws the breaker.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

where is your white neutral wire that comes into furnace with the black power wire?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
White wire from igniter goes to netral in juction box built into furnace.
Black wire from igniter goes to HS1
Customer reply replied 1 year ago
Power comes in from furnace juntion box to L1
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

ok that is a problem

The white wire from ignitor goes to hsi2

The white wire from neutral box goes to L2

Ask Your Own HVAC Question
Customer reply replied 1 year ago
OK. Let me check.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

standing by

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Purge fan is running. No hot ignitor. The ignitor is new. No flame. Purge fan is still running though. I have noting connected to HS2 or TR
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

the white from ignitor that you had in neutral box...that goes in hsi2

And previously you said the white wire from pressure switch was on TR.

Did you move it off

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Purge fan continues to run constant but no hot ignitor. Again. I do not have any wires to blades HS2 or TR
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

the white from ignitor that you had in neutral box...that goes in hsi2

And previously you said the white wire from pressure switch was on TR.

Did you move it off

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

Ok this was mentioned earlier but lets make sure.

White wire from ignitor goes to HSI2

White wire from neutral box goes to L2

White wire from pressure switch you said was on TR but is not now?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I only have two white wires;One from Ignitor that is currently on L2
One from Flame sensor that is on FP
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

The furnace needs 2 main things from the home power system

a black 120v and a white neutral. Both of these have to be on the board...L2 has to have a wire from the incoming white neutral to furnace

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

the ignitor goes on HSI 2

Before doing anything right now...

Put the white from ignitor on HSI2

we will go one wire at a time.

Once again put the white wire fromignitor on HSI2

Ask Your Own HVAC Question
Customer reply replied 1 year ago
OK. I am giving you exactly where the the white ignitor wire goes.1. From the ignitor itself it goes up into the funace juction box.
2. It pigtails to a 24V converter.
3. It pigtails and goes to the white wire on the purge motor
4. It pigtails and goes to the incoming white neutral white.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

We do not want the white ignitor going anywhere except HSI 2 on the board.

Before moving forward...move the white ignitor wire to HSI 2

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Black wire from ignitor goes directly to HS1.
Black main power goes directly to L1
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

the 2 blacks are fine.

Move ignitor white to HSI 2

Attach neutral to L2

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Roger-
Moving ignitor white to HSI 2
Attach neutral to L2I have to go to the garage and get a new blade to put on the wire to attach it.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

no problem.

I have to leave for 15 minutes. If you have another question I will respond as soon as I can.

If you are all set after the switch just rate service at top of page.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I have wired everything as you stated. Purge fan runs but no ignition. No light comes on the new board either. This is exactly what it was doing in March. I went on justanswer in May and was told the board was bad. Now I replaced the board and nothing has changed. What else could be causing this do you think?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

if you turn thermostat off does purge fan stop?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Turned off the thermostat off completely and purge fan continues to run!
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

ok, this is commonly a tripped safety or open safety.

When this happens is the main blower running?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
OK here is the deal. Purge fan is not running the main furnace fan is running. The AC worked perfectly all through the summer and shut on and off including the furnace. Now I flip to heat and the damn thing has gremlins. If I which it back to AC it works perfectly again.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

Prior to this swap...did the exhaust fan run?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Scratch that. Now the furnace fan runs continuously regardless if the Cool / Off or Heat is picked at the thermostat. It did not do that before replacing the board.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

is there a fuse on the new board?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Not that I see. It is a sealed unit.
Customer reply replied 1 year ago
Shit. The manual switch for the fan was on. Pulled it out now it is on auto. Fan has stopped.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

ok,

so where are we at now as far as operation

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Ok, I switched the thermostat to heat and nothing. No purge fan no light on the control board. Nothing. If I switch it to cool it kicks the furnace fan on and the condenser outside runs.
Customer reply replied 1 year ago
Do I need to check the thermostat for a jumper?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

Thank you. Do you mind removing the top section of thermostat?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
sure. One minute.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

we want a jumper from r to rc........and then we want to cross 2 wires so let me know when you are ready

Ask Your Own HVAC Question
Customer reply replied 1 year ago
OK. There is no jumper. Just the red wire on R. Nothing jumped to R to RC. Should I add a jumper?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

before we do that...take the red wire and the white wire on W terminal and cross them together. Tell me if the exhaust fan starts

Ask Your Own HVAC Question
Customer reply replied 1 year ago
at the thermostat or on the furnace?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

thermostat

Ask Your Own HVAC Question
Customer reply replied 1 year ago
OK. One minute.
Customer reply replied 1 year ago
Nothing.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

ok,

now red to green...

tell me if blower starts, and then we will go to circuit board for more testing

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Nothing. No blower or purge fan. Nothing turns on at the furnace.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

I thought with the fan setting in "ON" the blower ran?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
There is a manual/auto button inside the furnace. When I was tracing wires I bumped it in to manual mode and it ran all the time. I have sense pulled it back out to auto mode so that it only operates when the AC or heat calls for it.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

the issue is..

touching red wire to green wire starts the blower even in ac mode.

but your saying the red wire touching the green wire does nothing, so I am at a bit of a loss.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
sorry I didn't see red to green wire. Let me do that now.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

standing by

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Red to green furnace fan starts!
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

Ok good,

so we know power is right

transformer works

Now put thermostat back together.

We go to the furnace next.

Door off and pop out safety switch (if present) taped down.

Then with a U shaped wire....we want to put one end on r and other end on w on the board.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
ok. need a minute to put the thermostat together.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

standing by

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Ok. Done by the furnace. Ready to go
Customer reply replied 1 year ago
No safety switch on upper cabinet door. I will next jump the r and w
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

Ok....

Ask Your Own HVAC Question
Customer reply replied 1 year ago
R to W = Nothing. R to G = fan runs. this is at the furnace. is the thermostat bad?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

R to W at board eliminates the thermostat.

Is there a chance you could take a pic of the furnace with doors off and post here so I can mark test spots

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Will attach as soon as I finish taking them
Customer reply replied 1 year ago
2 of 2. let me know if you need any more pictures
20160925_181959.jpg2016092...jpg20160925_181950.jpg2016092...jpg20160925_182041.jpg2016092...jpg20160925_182150.jpg2016092...jpg
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

Thank you.

Look at this picture

Take the 2 wires off the switch and connect the wires direct together metal to metal. Then try R to W jumper again

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Doing now. one minute.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

If same with no operation see HERE

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I attached a jumper between the two connectors for the limit switch and jumped the R and W. Nothing.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

put those back...and try the next switch I showed you...also it would be a good time to see if the exhaust motor gets power but does not run.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Nothing changed but there is 120v going through them.
Customer reply replied 1 year ago
I have a simple multi meter and voltage finder. let me know what you want to test.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

Excellent.

go back to the r,w,y,b/c termonals (furnace)

set thermostat to heat and turn up temp...

then test terminal B/C to W and tell me if 24v

Ask Your Own HVAC Question
Customer reply replied 1 year ago
OK. There is no power to the purge fan.. I will go back to the r,w,y,b/c termonals (furnace) DONEset thermostat to heat and turn up temp...DONEthen test terminal B/C to W and tell me if 24v 27.6 volts.
Customer reply replied 1 year ago
tested terminal B/C to W and mutimeter reads 27.6 volts.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

Attached is a close up of a relay in top section.

With an insulated handle screwdriver or a pencil I want you to move the points I hav an arrow at...by move I mean press until it makes contact with other points

See Here

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Understood.
Customer reply replied 1 year ago
Ok. Main furnace fan comes on until I release it.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

please tell me where the purge fan wires come from

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 1 year ago

and I apologize but I have to go offline for a while but will respond as soon as I can

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I will take a picture to show you what they attach to.
Customer reply replied 1 year ago
Black wire (600V printed on it) on picture goes to black round relay? Power coming in but nothing coming out to the purge fan. White wire goes into furnace junction box and pigtails to white ground. Pictures won't go through but round relay? says;Potter & Brumfield
S87R1A2B1D1-24
20 Amps
9041Could this be a bad relay? It's the only thing that is attached to the fan other than the white to neutral.
Customer reply replied 1 year ago
OK I took the relay off and pushed the plunger up and the purge fan started. Still no ingnitor. There is a wiring gremlin in this furnace on the heat side. I am calling it quits. Thank you for all your help.
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,888
22,888 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a GSZ130421AE condensing unit and ARUF486016CA air
I have a GSZ130421AE condensing unit and ARUF486016CA air handler. The heat pump intermittently comes on and may operate a few minutes. When it stops operating, the air handler continues to run until … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm installing a condensation pump for a friend, he has dual
I'm installing a condensation pump for a friend, he has dual zones and the condensation pump has a after switch. The thermostat has ABCD connections. I need the common and normally open connections an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I replaced my defective Condenser fan. The 3 wiring hookup
I replaced my defective Condenser fan. The 3 wiring hookup on the defective is black to power, purple to defrost board and brown to dual capacitor. The replacement fan a MARS 10728 has four wires. Uns… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Can a condensate pump be used on a 100 gallon a o water
can a condensate pump be used on a 100 gallon a o smith water heater with a pvc horizontal vent system it is a 1/2" outlet at the bottom of heater … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat pump condenser coil are freezing up during this
my heat pump condenser coil are freezing up during this latest cold spell, can I thall them by using my aux mode … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,888 satisfied customers
I have aTrane XE 1200 AC and as of yesterday the condenser
I have aTrane XE 1200 AC and as of yesterday the condenser fan and compressor won't shut off. … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,888 satisfied customers
All my windows have condensation. Can I turn off the water
All my windows have condensation. Can I turn off the water to my G3203-75-2 to lower the humidity? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Gianni tankless water heater error 25-condensed trap full. 1
Gianni tankless water heater error 25-condensed trap full … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL
I HAVE A 5 TON CONDENSE UNIT MODEL #M0H40D72C SERIAL #702H02997 THAT THE COMPRESSOR WAS RECENTLY REPLACED BUT i STILL HAVE A ISSUE WITH IT IT CRANKS BUT IT STOPS AFTER 45 SECONDS NEED HELPWITH THIS IS… read more
R G
R G
44 satisfied customers
I have a heat pump condense unit and it has made this loud
I have a heat pump condense unit and it has made this loud tat tat tat tat tat tat noise (when in heat mode) when it turns on or off. It goes from the condenser unit all the way to hearing in the blow… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,412 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,888 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x