Billy, I contacted about my second floor theromstat no

Customer Question
Hello Billy,I contacted about my...
Hello Billy,I contacted about my second floor theromstat no functioning about 6 months ago. We believed it was a bad thransformer because the transformer to my 1st floor unit had a slight him to it with a 27.8 volt reading with a Greenlee tester. The second floor transformer was silent with power coming in to the transformer but it did not have any reading on the other leading out.I finally replaced the bad transformer with an identical transformer. I still do not have any power to the thermostat and the thermostat in question, functions on the first floor unit.I have reset the breakers to the ac/forced hot air system and I still do not have any power to the thermostat. The board the thermostat attached to is also dead. Thanks Steve
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
8/23/2016
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the humm is common in transformers and is not a sign of failure. These cannot be diagnosed by humm,. only by measuring the primary side voltage and the secondary side voltage.

Have you replaced the transformer that you think was bad, be very explicit please.... even it it is obvious. (first floor or second floor and which thermostat on each floor)

what was the primary side voltage reading on that transformer, what is the primary and secondary side voltage on the new transformer...

and what reading to you get on the new transformer from each side of the secondary side to ground (bare threads on the gas line).

What reading do you get from R on the thermostat where the same wire connects at the thermostat terminal strip in the furnace to ground.

We can go from there.... be unnecessarily explicit please. Pointedly explicit, that will help a lot.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
The unit is a Carrier AC that also uses forced hot air here in South Carolina. My thermostat on my second floor does not have any electric reading from R. It is completely dead and is a snap on electrical type that does not use batteries. I used a Greenlee DM-20 multi-meter to confirm this. It should be noted that I have two units in the attic. One for the 1st floor, the other for the 2nd. The 1st floor functions fine. Also, I tried the 1st floor functioning thermostat on the 2nd floor and it does not function on the 2nd floor, but functions perfect on the 1st floor. Because it has electricity to it.I was advised to install a new transformer (Carrier HT01CN241) in my second floor air handler because power, 27.8 V? was going into the old transformer and there was not any reading coming out. Therefore, I was told to change the faulty transformer.I changed the transformer and installed the new one. Again 27.8 going into the transformer and something like 24-25 volts? coming out.The is a 5amp fuse in the air hander which I observed was ok. I reset the garage circuit breaker for the unit, but this did not help. The a/c electric box outside at the outside unit on the side of the house is live. Any help you may give me at this point would be appreciated until I can get an HVAC Professional here by the weekend. Thank YouThank You.
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago

27.8 vac from the second floor transformer is fine and quite common, (that is because the primary voltage varies by 5 to 10% daily, and also the specification might be 230 volt transformer and a 240v primary transformer is not available....)

Some of the counter men at the wholesale houses are quite new to the business without any hands on experience.. those get paid about a quarter of what an experienced high quality tech gets... taking their advice will often get a person in trouble.

Regarding your comment:

"I changed the transformer and installed the new one. Again 27.8 going into the transformer and something like 24-25 volts? coming out."

That is now how we measure it, the one and only measurement that counts is **between** the two poles on the secondary side. no reading from either pole (in and out to use your terms) are valid to prove transformer output...

a reading from each pole to ground is used only to prove if a transformer reads below 10vac or so, that is quite rare. we replace in that case.. there is no IN and Out on the secondary side of the transformer, that is AC current it alternates 60 times a second.

The only IN reading that counts is between Line1 and Neutral on the PRIMARY side of the transformer, the only OUT reading that counts is between the two poles on secondary side of the transformer.

Regarding power to the outside unit, it is *not live unless you get 230v **between** line1 and Line2... readings from either line to ground showing 120v do not count.

Its time to locate the "finish and rate" link now, I will appreciate that, and in exchange will hold the question open for any follow up you need in the event the tech you called is not one the more fortunate ones in the top 20% of his field.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
OK, I'll wait for the HVAC tech seeing that I was informed here that when I replaced my faulty transformer, I should be "Good to Go". Obviously I have a bigger problem than a faulty transformer that is causing me not to have power to my thermostat. Maybe it is a bad wire somewhere, but the thermostat is fine in itself. But thanks anyway.
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago

Hello again, yes indeed it is a more complex issue, it will be interesting what the tech has to say, if you can get that to me verbatim I can assess the veracity for you.

Its time to locate the "finish and rate" link now, I will appreciate that since i work at my own expense here and loose money if you do not rate, in exchange will hold the question open for any follow up you need

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Tech replaced a 50 amp breaker in the box and kept the transformer I installed. First thing he did was check the breaker in the box in the garage. Thank you anyway
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,824 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My Carrier Furnace goes on but will not stay on,the red
My Carrier Furnace goes on but will not stay on,the red blinking code is 3blinks and pause,3 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My carrier thermostat shut off and is showing a battery
My carrier thermostat shut off and is showing a battery image that is blank, thought it was direct wired. Checked circuit breaker and is good. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Trying to identify thermostat wires from an old Carrier
Trying to identify thermostat wires from an old Carrier Comfort Zone to review options for upgrading the thermostat. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Just bought a Nest, but it's incompatible with my Carrier
Hi Hi. Just bought a Nest, but it's incompatible with my Carrier Infinity system. what to do? Rewire? Or find a different thermostat? If so, which one? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I HAVE A CARRIER HVAC WITH A SYSTXCCUIDO1B THERMOSTAT THATH
I HAVE A CARRIER HVAC WITH A SYSTXCCUIDO1B THERMOSTAT THATH NEEDS TO BE REPLACED. DO YOU RECOMMEMD A ONLINE PART. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND IT RESET FOR A TIME THEN DISPLAY CAME BACK UP … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Is there a battery on my carrier infinity thermostat? The
Is there a battery on my carrier infinity thermostat? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Heil CA5536VKD2, circuit breaker trips when it
i have a Heil CA5536VKD2, circuit breaker trips when it turns on compressor runs for like a second then trips bad compressor? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I turned the circuit breaker off to my AC to replace a
I turned the circuit breaker off to my AC to replace a thermostat with a NEST thermostat. When finished, I turned the CB back on. No power. I put the old thermostat back on and still no power at therm… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Will a weak capacitor trip the circuit breaker. Today only
well I can tell you I took off a fan motor that had 3 wires and replaced it with one with 4 wires… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
I woke up this morning to a tripped furnace circuit breaker,
I woke up this morning to a tripped furnace circuit breaker, I reset it and went up to the furnace and also noticed a burning smell and a humming noise.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My HVAC is not working. The AC circuit breaker trips as soon
my HVAC is not working. The AC circuit breaker trips as soon as the, I guess, the outside unit try to start … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,198 satisfied customers
The circuit breaker keeps shutting off when the Rheem
The circuit breaker keeps shutting off when the Rheem furnance/air conditioner tries to come on. What is our problem? We just had a new capacitor put in about two weeks ago. … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
What size amp circuit breakers needed for lennox heat pump
what size amp circuit breakers needed for lennox heat pump 14hpx-036-230-21 and Lennox air handler cby25uh-036-230-10? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,708 satisfied customers
On my Model 213C A/C, I have: Reset the circuit breaker,
On my Bryant Model 213C A/C, I have: Reset the circuit breaker, Replaced the fuses, Replaced thermostat batteries, Replaced the capacitor, Replaced the circuit board. Our A/C unit is less than five ye… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
The circuit breaker that I plugged my window unit into
The circuit breaker that I plugged my window unit into wasn't labeled so it got too much voltage when I plugged it in and it seems to have blown an internal fuse. I'm trying to figure out which compon… read more
Phil
Phil
Mechanical Engineer
8,824 satisfied customers
Circuit breaker cutting off no ac or ac will not run,
circuit breaker cutting off no ac or ac will not run … read more
HvacmanSean
HvacmanSean
Owner
HVAC
219 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x