I'm no HVAC expert so I need some insight from the experts.

Customer Question
I have a problem with...
I'm no HVAC expert so I need some insight from the experts. I have a problem with a fairly old. late 1990's model, Trane 50 ton air cooled chiller. The chiller cools the glycol in a closed circuit glycol circulation system through two air handling units to condition a large volume of air inside a building. The chiller has two cooling circuits with two compressors each. It incorporates hot gas bypass (HGBP) in circuit 1 to limit the cooling capacity at low loads. The problem is that the chiller trips intermittently reporting error code 8A, evaporator entry water temperature, when in HGBP mode. It is my understanding from studying the chiller manual and online literature that error code 8A means the evaporator entry water temperature dropped more than 2 deg F below the leaving temperature while in HGBP. Today I observed it's behavior under low load by turning off the air handling units so the chiller would just have to chill the glycol to the set point and then go into HGBP. As far as I can tell, without pressure gauges on the discharge and suction lines, it behaved as expected, no trips. The water temperature differential over the evaporator never exceeded 1 deg F while in HGBP. Tomorrow I plan on hooking up pressure gauges and run it under different load conditions to see whether I can catch it in the act. We had a Trane tech out a month or two ago but the chiller still trips on exactly the same error code. I can see with the hot gas being dumped in the evaporator that it would warm up the water in the evaporator. The question is why this temperature differential would intermittently exceed the 2 deg F limit. I suspect an intermittently misbehaving HGBP metering valve or maybe the valve just needs fine tuning to reduce the amount of hot gas being bypassed. Any suggestion on what I should be looking at or measure to pinpoint where the problem lies. The facility is located in a remote area so it is not easy (expensive) to get a Trane tech, or any HVAC tech, out here to track down a problem that may or may not occur while the tech is on site. Thank you for your help.
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 12 minutes by:
8/16/2016
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 15,666
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

No start a cycle and unplug the interface cable to the main board.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
No idea what you mean with "No start a cycle" and what interface cable to the main board? This system is so old, all we have is a serial comms link to send it the required temp set point. We don't get any info back from it. But not sure what this has to do with my problem.
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago

Hello and thanks for using this service! If you are a JA Member I would like to personally thank you and welcome you back! I am HVAC Guru an extremely experienced tech on the site and I try to get to as many customers as I can. NOTE it takes time for me to type research and add links so please wait for me to respond back I can only do this so fast. Secondly, I do not know your skill level so please try and let me know if I am going beyond your knowledge or comfort zone thanks! I strive for a 5 star rating from everyone especially our JA members.

That was not meant for you the site messed up and sent you that sorry. Now for your issue I think you may be on the right track, but I would install a new sensor at the water entry and see if that solves it often the sensors give issue for that problem and it may just be a defective sensor on the unit. Let me know what you find out.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Thank you, ***** ***** about the temperature sensors and will certainly check them out. I have not seen any spurious changes in temperature readings while monitoring at the chiller. But then the chiller refuses to trip when i stand there watching it. I read somewhere that the evaporator entering and leaving trmperature sensors are a matched pair. Is that true in which case I will replace both sensors. That may take a week or two to order and install so if you don't mind, can we keep this conversation open that long?
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago

Yes they are a pair same sensors. If you will not get back to me for a couple weeks and need to just rate my service and you will get a link to get directly back to me so the question will not close itsefl out and then you would have to restart.

All I ask is please use the Star Rating Link at the top of your page before leaving, that is the only way I am paid anything through the site and that will also get you a DIRECT LINK emailed to you to get back to me!.....tips are greatly appreciated so thank you very much for using this service. If you have any other questions just post back to me here anytime!

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Will do. I also read somewhere that in HGBP the goal is to control the suction line pressure so that the temperature of that line remains above freezing with a pressure around 58 psi. I'm not sure whether this is for an HVAC system meant for human comfort. Our chiller is not for human comfort. We want the cooled space cooled to whatever temperature we want to condition everything inside at that temperature, often down to freezing in the winter months. So in the current state of the chiller I do see the suction line freezing just before it goes into HGBP. Does that seem normal? It does not freeze up close to the compressors though, maybe up to a foot or two away from the compressors. If normal then I guess in our case the suction line pressure runs lower than 58 psi. We have R22 in our chiller. What pressure should I expect to see in the suction line when in HGBP?
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago

Did you check the sensors or replace them?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Not yet, my day was a bit hectic today so I did not get any time to work on the chiller issue and I was out of office yesterday. The plan is to check the temp sensors tomorrow and also hook up a pressure gauge to see whether that seems reasonable. I'm still trying to figure out what pressure reading to expect hence my question to you yesterday. To replace the temp sensors we need to identify the correct part number and order them. I have one of the technicians looking into that in between many other tasks we have to accomplish. Thanks for your patience and help so far.
Customer reply replied 1 year ago
Any response to the question above; What pressure should I expect to see in the suction line when in HGBP?
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 15,666
15,666 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
On our heat pump the evaporator blower runs constant even
On our heat pump the evaporator blower runs constant even when set to auto. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am told I have a leaking evaporating pan in a Lennox Model
I am told I have a leaking evaporating pan in a Lennox Model #C16-46-1FF. Iwould like to find a replacement pan. Is this possible, or can I tape crack? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit,
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit, Model MS-A12WA). That recently started leaking a pretty significant amount of water. The water must be building up inside the unit and then at s… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Fault code 26 and 59 at same time. Evaporator frozen
Fault code 26 and 59 at same time. Evaporator frozen condensation drain was blocked now open .blower mother will not run when set to fan only… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has run without problem for the last two years. Lately, it has begun to shut down and then restart on its own after about an hour or more. The l… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Evaporator water flow too low alarm keeps happening.
Evaporator water flow too low alarm keeps happening. Recently cleaned coils now this. The pumps are running fine. The pressures are good on the approach. The water strainer is clean. What is this a ca… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Our evaporative cooler has started leaking apparently so our
Hi there; Our evaporative cooler has started leaking apparently so our A/C is not working. They did a leak test and said that it had to be replaced because that's where the freon was leaking. We have … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a gibson C5BA-T42C- evaporator coil. Had a new
I have a gibson C5BA-T42C- B evaporator coil. Had a new condenser put in. they didn't change the coil. Said it would be ok. They used r410a freon. Case on this coil say r22. Is this coil going to work… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
My Sanyo CH1822 KEEPS ICING UP AND THE EVAPORATOR UNIT SHUTS
My Sanyo CH1822 KEEPS ICING UP AND THE EVAPORATOR UNIT SHUTS OFF BUT COMPRESSOR KEEPS RUNNING … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have questions about evaporative coolers. Just purchased
i would like to know about putting more air thru my Aerocool cooler by .putting a larger motor. … read more
Michael Ferryman
Michael Ferryman
82 satisfied customers
I have a furnace with an evaporator pump that i had to
I have a furnace with an evaporator pump that i had to repace all the relays and also the thermostat. After all is done it worked great for the winter except in order for it to work i had to put the t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I just moved to an old mobile home with an evaporative
I just moved to an old mobile home with an evaporative cooler. The HVAC tech told me I need to have windows open part way at each end of the home to make the cooler work properly. The problem is that … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a mastercooo evaporative cooler mcp44e. I've had it
Hello I have a mastercooo evaporative cooler mcp44e. I've had it for 3 yrs. just cleaned for summer use. My problem is that the pump and the fan will not work together. The pum works fine when filling… read more
Charles Bodenheimer
Charles Bodenheimer
Owner
Associate Degree
78 satisfied customers
Is Rheem Evaporator coils still presenting a problem with
Is Rheem Evaporator coils still presenting a problem with leaks. Thinking of installing Rheem central A/c … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
343 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x