Low head pressure and slightly high suction pressure on a…

Low head pressure and...

Low head pressure and slightly high suction pressure on a rtu gas pkg

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Today

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

R22

Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
8/11/2016
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,819
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, so far it sounds like the valves inside the compressor might be going bad. Tell me about how old the gas pack is, and the numbers on the name plate spot welded on to the compressor.. and the brand, copeland or techumseh

We can go from there

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Tennessee Rooftop Gas Package R22 Unit Model = GCS16-090-200-2Y Serial = 5602D-00678
First Action was acid test on circuit #1 and #2 negative for acid. Diagnosis Circuit 2 mechanical compressor failure ZR45KC-TF5-235 removed and installed ZR48K5ETF58OD with new C163S filter/drier. Pressure at suction port 70# ***** high side port 275#. outdoor ambient last two days 90's. Circuit #1 is off pending further troubleshooting.

Close the liquid line valve on circuit #2, then force the compressor to run and let it run until it gets to 0 psig on the suction side, then put your hand on the compressor suction line and tell me if it heats up real fast when you shut the compressor off, and if you hear a gushing sound, and tell me how fast the suction pressure rises.

We can go from there

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I did see that on circuit #1 before I replaced the filter drier and the freon. it isnt pulling in the contactors for circuit #1. But I did check it by manually holding the contactors in and charged it up about 150 # on the high side and then abandoned it for the moment. Seemed to be charging fine. The gauges are still connected on the circuit #1 and the static seems to not be equalizing over time. Im not sure how much only running one circuit affects performance in extreme temps
Customer reply replied 2 years ago
Im not sure this model is equipped with shutoff valves??

Send me 5 or 6 photo's of the unit with the service panels off, taken from about 8 feet away, and very well lit and focused... I will point out the various valves if they exist to you.

Use the paper clip icon on the right end of the tool bar, or the paper clip icon at that left of your send button to attach the pictures

We can go from there

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,819
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Phone call session started
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,819
9,819 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,819 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have two air conditioner units cooling my home, one 2-ton
Have two air conditioner units cooling my home, one 2-ton Goodman one 3.5-ton Goodman both installed 04/1999. I just installed in the two-ton unit a new fan motor and blades, a new evaporator coil and… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,819 satisfied customers
Can you explain me more about expansion valves? What if
Can you explain me more about expansion valves ? What if subcooling is normal ( 10 ) & superheat is high ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have walkin cooler, the high pressure switch trip when the
I have walkin cooler, the high pressure switch trip when the pressure goes 160psi, is there a way i can jump it to see if indeed the pressure switch is bad?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,819 satisfied customers
Certified and just finish HVAC school. I have issues with my
Hi, I'm EPA certified and just finish HVAC school. I have issues with my unit now. Compressor overheats and shuts off. Cooling is bad. I'm getting 5 degree between return and supply registers an the h… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
have a rheem heat pump rpne-030jbz 2007 r22 extremly high head
have a rheem heat pump rpne-030jbz 2007 r22 extremly high head in heat and low suction in cool. possible reversing valve problem?… read more
type2technician
type2technician
253 satisfied customers
what causes a high suction pressure and a normal head presssure
what causes a high suction pressure and a normal head presssure on an r22 system besides low air across the evaporator coil? Can air in the system cause this situation? TD is 17f. otd is 91degrees liq… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
have a/c only 1year old unit froze up filter ok coil clean
have a/c only 1year old unit froze up filter ok coil clean unit freeze at compressor on suction side first is compressor bad or is txv bad? Freon was reclaimed & reinstalled by scale r22 system tec. s… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I an Hvac system with low performance. Suction pressure is
I an Hvac system with low performance. Suction pressure is 10 psi and 125 on the hi side. the suction line is iced over from the unit to the a-coil and the a-coil itself. please advise… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, I have some theoretical questions for you since I
Hello, I have some theoretical questions for you since I am not an EPA certified tech. My dad has been an auto certified tech for many years and with much of that knowledge I have been able to do alot… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My condenser will run for 2 to 3 days with no problem and then
My condenser will run for 2 to 3 days with no problem and then stop working. I turn the ac switch off and then on and the condenser starts working. What is up ?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, I have a 3.5 ton Goodman packaged unit and i hooked up
Hi, I have a 3.5 ton Goodman packaged unit and i hooked up the gauges on it today and it gave me 55 psig on the low side and zero on the high. What does it mean? Outside was around 90 degrees… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello What should the pressure be on low and high side of
Hello What should the pressure be on low and high side of a goodman ck30-1a. It running but no cool air. Return from condenser not hot low side not cold… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My coil is clean and the filter is changed. My air flow is
My coil is clean and the filter is changed. My air flow is at 45 degree, and 18 degrees on the suction line 2 foot from the A coil, at the unit outside the liquid line is at 92 degrees. My PSI are 145… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hey Im looking at a lg split ducted unit, model lbuk4260bl
Hey I'm looking at a lg split ducted unit, model lbuk4260bl and it runs on r22. It's only giving medium load, on hot day really struggles. The head pressure is195psi and the suction is 95psi. Why is m… read more
Jerry M.
Jerry M.
Senior HVAC Technician
High School or GED
133 satisfied customers
TRANE XB13 R22 HEAT PUMP (SPLIT SYSTEM) COOLING MODE
TRANE XB13 R22 HEAT PUMP (SPLIT SYSTEM) COOLING MODE LOW SIDE = 66 PSIG HIGH SIDE = 148 PSIG, LINE TEMP 75 AMBIENT TEMP = 70 COMPRESSOR PULLING 7 AMPS HEATING MODE* LOW SIDE = 0VER 120 PSIG (OUT OF GA… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
When charging a air conditioner I have seen differant methods
When charging a air conditioner I have seen differant methods used, I was always taught to use superheat if the system uses a fixed orifice metering device or subcooling if it;s a txv. now I was also … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
i have 2 ductless split units {38hdlo24}that are not cooling
i have 2 ductless split units {38hdlo24}that are not cooling properly the high pressure side is around 150 psi and the suction side is around 80psi what should i check next ?these are r22 units… read more
freon
freon
Owner
High School or GED
214 satisfied customers
On my Yellow jacket manifold a/c gauges the low side at ithe
On my Yellow jacket manifold a/c gauges the low side at ithe condenser r22 is high @ about 110 while the high side is normal about 120 with the outside temp at 90 degrees. Why is the low side so high?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x