I have recently had installed your 2E728 ventilation control

Customer Question
in my greenhouse. The...
I have recently had installed your 2E728 ventilation control in my greenhouse. The fan only works when the control is less than 30 degrees. When I turn the knob to a higher number the fan shuts down. There must be an adjustment that I can make in order for the fan to turn on and off . This my second message to you.
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
7/30/2016
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 year ago
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 348
Experience: hvac technichian at performance plumbing and heating
Verified

hi i am dan i can help you with this. is it a new control or existing? what is the temperature it is sensing?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
The control was just installed and has never been used before, therefore I consider it new, but I have had it in its box for several years.
The greenhouse exhaust fan turns on when the control reads less than 30. IE: when the dial has been turned to the extreme left. When I turn the knob to the right and the temperature numbers start to go higher, then the fan shuts off. I assume there must be an adjustment some place on the unit in order to set the dial at the required temp. and it will then turn on and off accordingly.Bruce.
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 year ago

ok what terminals do you have in the control and which ones do you have the wires connected to?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
The electrician did it, I have no idea. Do you want me to do something?
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 year ago

i would pull the cover off and check the wires. make sure the power is off first. if there are three terminals they will be labled as C, NC, NO. you want the wires on C and NO

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Please tell me where the wires should be connected. I can't understand if the fan works, why doesn't the controller? I think the same wire (black ?) comes and goes through the controller (?)
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 year ago

as i said the wires should be connected to C and NO are there 3 or 2 terminals in the control?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Can you send me a wiring diagram since one was not in the box with the controller and the electrician had to work his way through on his own?
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 year ago

this is a very simple switch. there is no wiring diagram. are there 2 terminals or 3 terminals?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
There are 2 terminals. Today I reversed them and had no change in its operation. Plan to go to an electrical store for them to examine the controller. The problem remains the same.Bruce Hausser
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 year ago
Ok if there are only 2 then it is just a single pole switch. That means that it is bad. It relies on the pressure of the refrigerant in the bulb to operate the switch based on temperature. Since it only works at 30* that means the bulb has list its pressure and it leaked out somewhere. The switch will have to be replaced
Ask Your Own HVAC Question
Customer reply replied 1 year ago
what is the next available control that you would recommend as a replacement and how much would it cost?
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 year ago
Any line voltage cooling thermostat will work as long as it is rated for the lra ratting of the motor. They usually cost anywhere from $15 to $50
Ask Your Own HVAC Question
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 year ago
If you have any more questions about this please let me know. If not I would appreciate it if you could rate me on my service by selecting one of the 5 stars. And thank you for using just answer
Ask Your Own HVAC Question
HVAC Technician: Daniel Plourde, HVAC Technician replied 1 year ago

did you have any more questions about this or did I answer everything for you?

Ask Your Own HVAC Question
Ask Daniel Plourde Your Own Question
Daniel Plourde
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 348
348 Satisfied Customers
Experience: hvac technichian at performance plumbing and heating

Daniel Plourde is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a tank less hot water heater that will not come on. It
Have a tank less hot water heater that will not come on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a GE power vent gas water heater that will not stay
I have a GE power vent gas water heater that will not stay on. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Why do we have warning signal showing on our panel also wot
Why do we have warning signal showing on our panel also wot is w 42 h mean … read more
travis webb
travis webb
tech.
2,153 satisfied customers
I have a 80uhg that when i call for heat the gas burner
I have a 80uhg that when i call for heat the gas burner doesnt light and the blower comes on … read more
travis webb
travis webb
tech.
2,153 satisfied customers
I have a York Diamond 80 and I am getting the 4 flashes code
I have a York Diamond 80 and I am getting the 4 flashes code for open high limit switch. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My recirculation fan does not shut off ony good man natural
My recirculation fan does not shut off ony good man natural gas furnace and the trouble light shows normal operation … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Why is the supply connection at the header 1 1/2” do i have
Why is the supply connection at the header 1 1/2” do i have to run 1 1/2” to the pumps? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Americian standard freedom 80 single stage natural gas
americian standard freedom 80 single stage natural gas furnace won't light … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have Philco furnace Model G6RC 100C-16 - furnace runs for 4
Have Philco furnace Model G6RC 100C-16 - furnace runs for 4 minutes, then shuts off for 10 minutes. Red light blinks twice. Checked to make sure drain is operating, which it is. Checked the flame sens… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier Model 58MVP 120 blinking error code. 13.
I have a Carrier Model 58MVP 120 blinking error code … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennox airhandler cbx32mv-048-230-6-07 I have no
I have a lennox airhandler cbx32mv-048-230-6-07 I have no heat and this unit has heat strips. I have had techs out here and they have changed the 3 relays and today the mother board. lasts week the ma… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 1989 vintage Vaillant boiler that continues to
Hi, I have a 1989 vintage Vaillant boiler that continues to ignite and then shuts off. What would cause this problem? … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a Nordyne 3.5 Ton heat pump that a acted up and
I have a Nordyne 3.5 Ton heat pump that a acted up and wouldn't heat last week. It has small leak in coil that seems very slight. R 22 imstalled , unit holding 40psi for twenty minutes the repairman (… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The red emergency on/off switch was accidentally turned off.
The red emergency on/off switch was accidentally turned off. After turning it back on, checking the breakers, and turning the thermostat off, then on and resetting it, I still have no heat. What else … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I changed my thermostat and then put the original back nd
I changed my thermostat and then put the original back nd not it will not light up at all … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
Thermostat keeps returning to 70 degrees even tho I cancel
Thermostat keeps returning to 70 degrees even tho I cancel present temp by pressing run and put a new lower temperature in and it still returns to apparently a programmed 70 which comes in during the … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have 4 honeywell rlv4305 thermostats. they are all hot on
Hello, I have 4 honeywell rlv4305 thermostats. they are all hot on the top right corner. they are all in standby mode. Is this an issue, or are they hot, because they are not calling for heat right no… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I recently had a bosch geothermal CE035 installed in my
i recently had a bosch geothermal CE035 installed in my home. i am wondering how do I change the setting to keep the auxiliary heat off longer ? … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x