I have a Bonaire unit the supply temperature does not go

Customer Question
above 29deg C JA: Did you...
I have a Bonaire unit the supply temperature does not go above 29deg C
JA: Did you double-check the thermostat? And what about the unit's filters?
Customer: Already checked all good
JA: Do you plan on doing the work yourself?
Customer: I am a technician
JA: Anything else we should know to help you best?
Customer: Discharge pressure is 275psi suction pressure is 53 psi
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 hours by:
7/25/2016
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,889
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, tell me the approximate age of the Bonaire unit, and its application (though the wall or ducted etc) I need a lot of details, Bonaire made systems of all types for 40 years.

We can go from there.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
The age of the unit is 8 yrs. Its a ducted reverse cycle ac..model is BO12RS..
Offcoil temp 34degC
Return Air 15.6degC
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago

are those temperatures in heating mode?

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago

I am not finding the manual in my files, is this a water cooled or air cooled unit.

So far it looks to be doing well at at a 19C temperature rise in heating mode. What problems are you having with it?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
This is a reverse cycle heat pump.
All the temperatures are in heating mode.
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago

Hello again, so far with the temperatures and pressures you have given it sounds like it working about like any heat pump should with 34C supply air temperature. (when not in electric booster heat mode).

Tell me why you have mentioned 29C off coil (supply) air temperature, you would see that only if the house were in the 10C range, OR if the outside air temperature was going much below zero C and the electric booster heaters were not installed, or if installed were not coming on for one reason or the other.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
The 29deg temperature is the air coming off the supply vents whereas the 34 deg temperature is off the coil.
This is where the confusion. The customer advised that the unit was working fine when it was installed. If there was any issues when installation was done then that would mean its a design issue. I had the customer on the phone and the unit tripped,thus reset coming on the ir remote controller. The fault was F1 04.
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago

Hello, you can save an hour on this by telling me what the code read out for F1 04 is.... these codes are helpful indeed, about 30% of the time, the other 70% of the time they can be misleading or in more than a few cases, entirely bogus.

------------

Regarding the temperature loss in the supply air ducts from 34C to 29C... the duct is either not as well insulated as it should be, OR... its leaking badly...OR its very long, and it is very cold outside and the velocity is so low that the air is cooling off.

There is another factor, thermometers are all 1 or 2 degrees C off either way, high or low, if you are using two different thermometers, one could be reading high, the other low, and that would give you a bogus result.

When measuring the air at a register the thermometer must be placed inside the register, not outside where the room air mixes with the supply air and gives a false read.

Let me know, we can go from there.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
The thermometer probe was placed inside the register.the ducts are long.The airflow from my point of view is ok..Since the ducts are under the house i was not able to go to all places to check the ducts.
So if say just because the length of the is long and the temerature drops due to this what can be done to solve this. By the way what does F1 04 mean....
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago

Hello, you can go under the house with a roll of 1 inch thick fiberglass duct wrap, and first look for air leaks, and repair those, then wrap the duct with at least one more layer of this duct wrap.

Fault codes

http://www.bonaire.com.au/-/bonaire/lib/images

/pdfs/owners%20manuals/Bonaire-Multi-Appliance-Manual-Control.pdf

I didn't see that fault code listed in the manual, in that case it is usually on a sticker next to or on the unit wiring diagram.

Some reports have it as an 'over temperature error, fan kept running on high speed due to a furnace over heat situation, but that is just someone elses opinion, I have not seen any reference to my self.

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,889
8,889 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,889 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have 78 low side 231 high side r22 is this due to over
i have 78 low side 231 high side r22 is this due to over charge? … read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
Billy, I have had the Fedders (remember them) 15K Split HP
Hi Billy, I have had the Fedders (remember them) 15K Split HP for a few years. Last year I had only an 8F inside temp spred so I put a little R410a in to match the gauge outside temp. Inside temperatu… read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
I have a Nor norlake walk-in cooler / freezer and the
Hello! I have a Nor norlake walk-in cooler / freezer and the freezer is currently reading 22 deg. And doesn't seem to be kicking on to cool down It's usually at or below zero … read more
Don T.
Don T.
President
Associate Degree
179 satisfied customers
I am an HVAC contractor in Southern DE. I have a performance
I am an HVAC contractor in Southern DE. I have a performance issue with a York system that another contractor installed and after going through a few things I believe they mismatched the outside and i… read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
Have 50HJ066 acutrol metering device changed refrigerant to
Have 50HJ066 acutrol metering device changed refrigerant to 407c unit takes 10 lbs on label but had to charge 16 lbs but metering device freezing … read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having trouble getting more that 10 degrees of cooling between the return and the vent. I've adjusted the charge to the spec in the manual for a pi… read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
If the reversing valve has a internal short like you said is
if the reversing valve has a internal short like you said is that why my suction psi is ;low… read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
Three ton goodman spiit pressures are great everything
three ton goodman spiit pressures are great everything runing but not cooling unit is 7 yrs old … read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
Is the head pressure & discharge pressure same thing? And
Is the head pressure & discharge pressure same thing ? And what about back pressure & suction pressure !… read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
Is the head pressure & discharge pressure same thing? And
Is the head pressure & discharge pressure same thing ? And what about back pressure & suction pressure !… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a reem 2.5 ton unit. The head pressure is 300 PSI. It
I have a reem 2.5 ton unit. The head pressure is 300 PSI. It is now cooling fine but the head pressure seems too high… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a HVAC question. Phil the retired mechanical engineer
I have a HVAC question. Phil the retired mechanical engineer helped me the other day an I would like to talk with him. The suction line is icing up at the compressor.… read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
I'm an HVAC Tech in Tennessee and was replacing a scroll
I'm an HVAC Tech in Tennessee and was replacing a scroll compressor in a 1.5 Ton Rheem Heat Pump.After brazing up my compressor and filter dryer, I performed a leak check.After which I pulled a vacuum… read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
Low head pressure and slightly high suction pressure on a
low head pressure and slightly high suction pressure on a rtu gas pkg … read more
Phil
Phil
Mechanical Engineer
8,889 satisfied customers
My suction pressure is 125 and liquid line pressure is 275.
My suction pressure is 125 and liquid line pressure is 275. This is after I replaced a bad compressor. Outdoor ambient is 95 degrees. Indoor temp was 85 degrees. The indoor coil wet on the lower part … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have low suction pressure and the head pressure is running
hello, I have low suction pressure and the head pressure is running high Checked liquid line temp and it was running very hot Cleaned both coils and checked filter W HAT MIGHT BE THE PROBLEM … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x