I have a Thermocore 3/4 ton mini-split about a year old.

Customer Question
After a community power outage...
I have a Thermocore 3/4 ton mini-split about a year old. After a community power outage the unit started up at first normally. (Run light on inside unit, fan blowing...outside unit fan blowing.)
After about 5 minutes unit shut down and Error code is: EC with 7 flashes on the inside unit panel. Outside compressor lines show no differential temperature for inlet and outlet. Felt about ambient temperature.
How do I fix this? I do have a set of gages and MANY years ago I was the HVAC consultant for Amoco Oil company for industrial units. I have routinely check the charge on my old central air unit but have had little experience with mini-split units.
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
7/15/2016
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 15,852
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello and thanks for using this service, if you have been waiting do not worry or get upset. I am HVAC Guru an extremely experienced tech on the site and I try to get to as many customers as I can. I just picked up your question now. NOTE it takes time for me to type research and add links so please wait for me to respond back I can only do this so fast. Secondly I am not paid anything until you rate my service good using the STAR RATING LINK at the top of your page, the money is paid to the site not me directly.

What is the complete model number?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Thermocore T125S-H109C
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago

Sorry for the delay, that is a communication error, go to this link and go through the troubleshooting steps to rectify the error.

CLICK HERE

All I ask is please use the Star Rating Link at the top of your page before leaving, that is the only way I am paid anything through the site and that will also get you a DIRECT LINK emailed to you to get back to me!.....tips are greatly appreciated so thank you very much for using this service. If you have any other questions just post back to me here anytime!

Ask Your Own HVAC Question
Customer reply replied 1 year ago
The unit I have does not have any LEDs on the IPM board. The only light indicator is on the front panel of the air handler. On that panel there is a constantly lit "EC" and a led flashing 7 times followed by a long pause and then flashes another 7 times, etc. The EC stays on all the time. There are no leds of any kind on any circuit board of the air handler nor outside compressor unit. Your diagnostic flow chart does not apply as written for the Thermocline unit I have.
Please try again.
Thanks
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago

The code is the same whether or not yours has leds on the board or not you have a board failure on the unit

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I'm sorry it is not a sufficient to say that even though I do not have what you told me to look for that i have a bad board does not fill me with confidence as to your familiarity with Thermocore min split units.
You gave me a specific sequence including leds that are not even there.
You have not identified what the specific code on my Thermocore unit means.
Apparently you either have not had experience with my Thermocore unit or do not have access to the repair diagnostic manual that applies to it
To send me a repair procedure that does not even specifically apply to my machine is not an answer.
Anyone can say it is not working and to keep on changing out about $800 worth of boards on a unit until it works.
With all due respect to your years of experience, you apparently can't adequately answer my question. If you can't find the answer specific for my machine, please direct my question to another expert who does know Thermocore machines and can answer.
Thank you.
HVAC Technician: Phil, Mechanical Engineer replied 1 year ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, just to let you know, Thermocore is not common at all, a less than 1/10th of one percent brand. most of such type units are made in china and often with no parts support. Neither the brand name nor the model number is ***** on Google... This is not the answer you need, just a comment. Even if you get a good diagnosis somehow, getting the part would most likely turn out to be an insurmountable problem. I wish that I could be more helpful. Thanks for trying us at Just Answer!

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I hear what you are saying. I am a contractor.
One of my other 5 Thermocore units which I bought together failed within the parts warranty period.
Thermocore supplied all the components to my local HVAC source here in Charlottesville VA.
I would have called them again since the code was totally different but I had hoped that JustAnswer could answer and perhaps save me some money.
I used to work with older design units years ago but not mini splits at all.
My understanding from them was that the compressor is a Toshiba. The other unit lost a compressor pretty quickly after installation which Thetmocore sent a replacement compressor along with another main board under warranty.
I was impressed with the rapid response from Thermocore ....so they did their job. As a consumer I can't be responsible for the rarity of these units but my expectation that a self proclaimed expert HVAC "Guru" should be able to diagnose is a normal response.
Thank you for your candor saying you can't answer.
I don't know how you good folks get paid but I can't justify paying for no corrective answer.
Is it possible totsend this question thread to another expert who might have had Thermocore experience or is JustAnswer at the end of their effort?
Thank you.
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,824 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a tank less hot water heater that will not come on. It
Have a tank less hot water heater that will not come on … read more
HVAC Guru
HVAC Guru
HVAC TECH
15,852 satisfied customers
I have a GE power vent gas water heater that will not stay
I have a GE power vent gas water heater that will not stay on. … read more
HVAC Guru
HVAC Guru
HVAC TECH
15,852 satisfied customers
Why do we have warning signal showing on our panel also wot
Why do we have warning signal showing on our panel also wot is w 42 h mean … read more
travis webb
travis webb
tech.
2,153 satisfied customers
I have a 80uhg that when i call for heat the gas burner
I have a 80uhg that when i call for heat the gas burner doesnt light and the blower comes on … read more
travis webb
travis webb
tech.
2,153 satisfied customers
I have a York Diamond 80 and I am getting the 4 flashes code
I have a York Diamond 80 and I am getting the 4 flashes code for open high limit switch. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My recirculation fan does not shut off ony good man natural
My recirculation fan does not shut off ony good man natural gas furnace and the trouble light shows normal operation … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Why is the supply connection at the header 1 1/2” do i have
Why is the supply connection at the header 1 1/2” do i have to run 1 1/2” to the pumps? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Americian standard freedom 80 single stage natural gas
americian standard freedom 80 single stage natural gas furnace won't light … read more
HVAC Guru
HVAC Guru
HVAC TECH
15,852 satisfied customers
Have Philco furnace Model G6RC 100C-16 - furnace runs for 4
Have Philco furnace Model G6RC 100C-16 - furnace runs for 4 minutes, then shuts off for 10 minutes. Red light blinks twice. Checked to make sure drain is operating, which it is. Checked the flame sens… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier Model 58MVP 120 blinking error code. 13.
I have a Carrier Model 58MVP 120 blinking error code … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennox airhandler cbx32mv-048-230-6-07 I have no
I have a lennox airhandler cbx32mv-048-230-6-07 I have no heat and this unit has heat strips. I have had techs out here and they have changed the 3 relays and today the mother board. lasts week the ma… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 1989 vintage Vaillant boiler that continues to
Hi, I have a 1989 vintage Vaillant boiler that continues to ignite and then shuts off. What would cause this problem? … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a Nordyne 3.5 Ton heat pump that a acted up and
I have a Nordyne 3.5 Ton heat pump that a acted up and wouldn't heat last week. It has small leak in coil that seems very slight. R 22 imstalled , unit holding 40psi for twenty minutes the repairman (… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The red emergency on/off switch was accidentally turned off.
The red emergency on/off switch was accidentally turned off. After turning it back on, checking the breakers, and turning the thermostat off, then on and resetting it, I still have no heat. What else … read more
HVAC Guru
HVAC Guru
HVAC TECH
15,852 satisfied customers
I changed my thermostat and then put the original back nd
I changed my thermostat and then put the original back nd not it will not light up at all … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
Thermostat keeps returning to 70 degrees even tho I cancel
Thermostat keeps returning to 70 degrees even tho I cancel present temp by pressing run and put a new lower temperature in and it still returns to apparently a programmed 70 which comes in during the … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
I have 4 honeywell rlv4305 thermostats. they are all hot on
Hello, I have 4 honeywell rlv4305 thermostats. they are all hot on the top right corner. they are all in standby mode. Is this an issue, or are they hot, because they are not calling for heat right no… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
I recently had a bosch geothermal CE035 installed in my
i recently had a bosch geothermal CE035 installed in my home. i am wondering how do I change the setting to keep the auxiliary heat off longer ? … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less