My unit is Trane XV80. TUD080R9V3J1Heat Mode: Furnace works fine, fan runs at low speed.Problem:
In AC mode, fan runs at very low speed, not enough to circulate air through coils to cool. The fan used to run at high speed in AC mode.
FYI: Outside AC unit kicks on and cools coils, but I know it will freeze up coils if there is not adequate air flow.The unit uses the Trane Programmable Motor : D341313P04. Mod 00819. It has a wire harness coming from the Intell-Ignition board, 16 white wires.How can I get the fan to operate at high speed when in AC mode ?
Thankyou
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 hours by:
7/14/2016
HVAC Technician: Tim H., HVAC Professional replied 1 year ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified

Hi, I'm Tim and I'm an HVAC expert here to assist you with your questions. Please provide all information I request as it makes it more difficult to troubleshoot something when I'm not there onsite. Essentially, you become my eyes and ears. Thanks for the opportunity to help. At the end of our dialog, you will have a chance to rate my service, but please wait until we are finished and you're satisfied you have all the information you need. Please be patient as many times we work with several customers at once.

Did you change any dip switch settings on the board? What position are dip switch settings 1,2,3, and 4 in?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Hi Tim, thank you for your reply and help.
- . I have never changed the dip switches.
There are 2 dip switches, the positions are as follows:1. ON. 5. ON
2. OFF. 6. ON
3. ON. 7. OFF
4. OFF. 8. OFFCan you please send the matrix of switch position for desired fan speed for AC mode and Heat mode?Does dip switch "one" control the fan speed in AC mode alone ? What does dip switch"two" control ? Fan speed in Heat mode?
Thank you
Larry
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

I've attached a manual. On page 11, it shows cooling dip switch setting. So first you determine the tonnage of outdoor unit, then you set the switch positions as shown for either low, medium or high speed. Dip switch 2 has no special function, it is just part of the total setting for speed.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Thank you for the manual. My outside unit is a 2 1/2 ton,. as it is a Trane XE1200, TTP030D100AO
According to the manual, switch setting for Normal operation should be :. OFF. ON. OFF. OFF I'm assuming the manual refers to board dip switch labelled " S3 " ?My board actually has three dip switchesS1. Only a two switch dip:... 2,3
S3. A four switch dip:... 1,2,3,4
S4. A four switch dip:... 5,6,73Does manual refer to Switch 3. "S3" settings?Where is setting chart for Switch 4 ? And Switch 1 ?My Switch S3 is set to On,Off,On,Off .....which is not even listed in manual.Can you give description/diagram of each terminal wire/color connection on the IFC board, as to what they should be connected to? Also, what terminals should be jumpered for operation? My IFC board is :. D341420P01. Rev B.. I believe I have the multi-speed programmable motor, it is D341313P04,. ...Mod 00819My System:.
IFC board terminals:
Blk/Twin, W2, W1, R, G, B/C, Y, Ylo, O......9 terminals total.Wires coming into IFC board from:Thermostat: ....Red, White, Green, Yellow
.
Outside AC unit,
....- Red, Wht. (I believe start relay)
....- Green, Blue ( I believe Temp sensor)Humidifier Selonoid
.....Red
......White:. (Goes to 24VAC transformer)I have a 4 wire Hunter Programmable Thermostat about 2 years old.
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,503
Experience: Furnace, A/C and heat pump specialist.
Verified

My name is ***** ***** a different expert.Your problem is most likely going to be in the bell control on the end of the motor if you have not changed any dip switch stings prior to this conversation.

Issue is either bell control or board but 90 per cent of time it is in bell control.You can not trouble shot these motors with a standard volt meter as the motor is high voltage powered but low or dc voltage controlled,

Testing requires the tool below.

If you want to get this tool I will guide in troubleshooting.

The bell is about 450 bucks if t is out of warranty, so we really need to know before just replacing parts.

https://www.grainger.com/product/6PFG9?gclid=CjwKEAjwk6K8BRDM3aCSkdCtzSQSJAA3Vf38UyKlRx58LavZwsDVgke4gJare-gLhFhyPvtidK4AoRoC7Wrw_wcB&cm_mmc=PPC:GOOGLEPLAA-_-Motors-_-Motor%20Supplies-_-6PFG9&AL!2966!3!50916701757!!!g!82128731277!&s_kwcid=AL!2966!3!50916701757!!!g!82128731277!&ef_id=VznGnAAAAG7Thv3w:20160715234927:s

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I received your response and suggestion, however , you not answer all my questions? If I follow the suggestions of the first expert, my configuration does not make sense. I would have expected to follow that string first. I prefer to go about troubleshooting in a logical manner so I cover all bases. At this time, I will take another avenue for advice. Thanks anyways.
HVAC Technician: airheatman, HVAC Technician replied 1 year ago

Totally understand. The proper steps in troubleshooting this issue is to start by attaching the tool described.If you do not have or want to aquire the tool, your best bet is to call in a technician.

AS far as logical troubleshooting the tester mentioned is quickest and best solution.

The fact that you have not changed any settings or dip switches causing the change in operation indicates that either motor controller bell or circuit board is failing.

If you are unsatisfied, we can request a refund of your deposit.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Well, let me provide some additional info to explain the reason why I asked for the terminal connections on the IFC board.
- the original multi feature Honeywell thermostat shorted out and needed to be replaced. I replaced with a simple standard 4 wire Hunter Programmable. I don't know if the short on the tstat took out anything on the IFC board...but the furnace seemed to work fine all Winter with new tstat. Again AC compressor starts and cools coils. But fan does not go to high speed.Per my last email, correct wire configuration to IFC board needs to be verified before digging into Motor Bell housing. Thank you.
HVAC Technician: airheatman, HVAC Technician replied 1 year ago

Totally understand.

Red from R on Thermostat will go to R with a jumper to BK on Furnace IFC

White from W on Thermostat will go to W1 with a jumper to W2 on Furnace IFC

Green from G on Thermostat will go to G on Furnace IFC

Yellow from Y on thermostat will go to Y/Y2 on Furnace IFC

AS for the humidifier, do you have a separate humidistat?(the 4 wire thermostat does not offer humidity control)

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Thank you for the Thermostat terminal description. All of these are correctly connected. Yes, there is a Honeywell humidifier on the furnace with a humidity control dial. There is also a temperature sensor outside (two wires) that I'm guessing tells the furnace what stage to be in for heating or cooling depending on outside temp ? Can you see my earlier response in this thread? ( Wires coming from/ going to AC unit outside, temp sensor wires, humidity control wires, ) I have listed all my inputs/outputs that make up the configuration. All these additional wires need to be verified as to proper hookup to the IFC board. Also what jumpers should be installed or removed based on my system described above ( 2 1/2 ton Trane AC Two stage heating/cooling. Thank you
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,503
8,503 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I got a new Honeywell programmable thermostat in April and
I got a new Honeywell programmable thermostat in April and connected to wifi. We departed for 4 months this summer and had to turn off the wifi, which meant I had no connection. Now I am ready to prog… read more
airheatman
airheatman
HVAC Technician
8,503 satisfied customers
I have a Bypass Humidifier, MODEL 445, and this season it is
I have a Bypass Humidifier, MODEL 445, and this season it is leaking water from the water tray. I went to remove the finger nut that secures the tray and it just split in half. could the finger nut be… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
343 satisfied customers
My Honeywell programmable thermostat shows bat lo. I changed
my Honeywell programmable thermostat shows bat lo. I changed to new batteries but still get bat lo message. thermostat is still working and house is heating but I cannot program it … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am trying to replace a Honeywell programmable thermostat
I am trying to replace a Honeywell programmable thermostat with a Totaline P474-1100 RF thermostat and P474-1100REC receiver. The thermostat will only be controlling heat via a gas-fired steam boiler.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I replaced a non-programmable thermostat with a Honeywell
I replaced a non-programmable thermostat with a Honeywell RTH2300/RTH221. … read more
airheatman
airheatman
HVAC Technician
8,503 satisfied customers
I have a Carrier Programmable Thermostat and the AC keeps
I have a Carrier Programmable Thermostat and the AC keeps running. Can I reset it somehow or could there be another problem? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I'm swapping out a Honeywell non-programmable thermostat
I'm swapping out a Honeywell non-programmable thermostat with a Honeywell programmable one. Wires don't quite match. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have an HM512W1005 Direct Injection Humidifier. It
I have an HM512W1005 Direct Injection Humidifier. It currently connects wirelessly to a Honeywell thermostat. I'm trading that out for an Ecobee4 and need help knowing which wires to run from the humi… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Rodgers 1F90-51 programmable thermostat. Came home
I have a White Rodgers 1F90-51 programmable thermostat. Came home tonight to a very hot house and a display that showed "BATTERY" solidly (not flashing). Went out and bought a brand new pack of AA bat… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
0 satisfied customers
I have a Chromotherm III programmable thermostat that now
I have a Chromotherm III programmable thermostat that now shows -AC and does not turn on the the air conditioner. I changed the three AAA batteries for new, but no luck. … read more
airheatman
airheatman
HVAC Technician
8,503 satisfied customers
I have a -Rodgers programmable thermostat 1F82-261,
I have a White-Rodgers programmable thermostat 1F82-261, purchased last year. I also had the electric pump serviced at that time, which needed some new parts. I have been using the heat, programmed, a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am interested in getting a programmable thermostat my
I am interested in getting a programmable thermostat my current one is water furnace model TA32E12 … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
MyCT2800 Programmable Thermostat blinks battery low after
myCT2800 Programmable Thermostat blinks battery low after installing new ones??? … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I have a Carrier TP-PRH01-A programmable thermostat but it
I have a Carrier TP-PRH01-A programmable thermostat but it is not WiFi capable. I would like to replace it with a Honeywell WiFi programmable thermostat. Can you tell me which model(s) you would recom… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an old honeywell two wire programmable thermostat
I have an old honeywell two wire programmable thermostat that I would like to replace with another honeywell thermostat RTHL2310 RTHL221 ....can I do this with only the two wires? Marie … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Just purchased programmable thermostat RTH2410B connected
Just purchased programmable thermostat RTH2410B connected wires furnace is not responding … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Linstat Setback programmable thermostat,serial #
I have a Linstat Setback programmable thermostat,serial # 038731, model # TH101 A-40. It runs electric heaters on 240 vac. Somehow, it switched over to Celcius display and I can't figure out how to ge… read more
airheatman
airheatman
HVAC Technician
8,503 satisfied customers
I have a Honeywell touchscreen programmable thermostat that
I have a Honeywell touchscreen programmable thermostat that is just over 10 yrs old and the light feature has stopped working. The thermostat is very similar to the current model RTH8500D. How do I ge… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x