I have a carrier 410A heat pump model 25hcb324a300, equipped

Customer Question
with a txv at the...
I have a carrier 410A heat pump model 25hcb324a300, equipped with a txv at the evaporator coil and im charging by subcooling by liquid only and my recommeded subcooling for the unit is 12. As I add refrigerant to the unit my sibcooling stays at 3 to 4 degrees no matter how much refrigerant i out in it. I tried changing out the txv at the evaporator but still the same. Please help.
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 hours by:
7/1/2016
HVAC Technician: Tim H., HVAC Professional replied 1 year ago
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
Experience: Experienced in all aspects of HVAC, both residential and commercial.
Verified

Hi, I'm Tim and I'm an HVAC expert here to assist you with your questions. Please provide all information I request as it makes it more difficult to troubleshoot something when I'm not there onsite. Essentially, you become my eyes and ears. Thanks for the opportunity to help. At the end of our dialog, you will have a chance to rate my service, but please wait until we are finished and you're satisfied you have all the information you need. Please be patient as many times we work with several customers at once.

Low subcooling can be caused by excessively dirty condenser, poor airflow through the condenser, or undercharged.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Well from the looks of things the condenser coil looks ok. And my head pressure was around 265 normallybits around 350 on a normal hot day. My suction pressure was around 107 kind of high, and no matter how much freon I add my subcooling does not change. I havn't tried to clean the coils but im certain there may be something s else. Perhaps the outdoor txv thats build into the condenser coil. Im at a 234 unit apartment building and I have two unit doing the same exact thing. I service manybof these units already but for some reason i cant get pass this issue.
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

Make sure TXV is the proper one for unit. Otherwise, low subcooling can be caused by some of the things I mentioned previously.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I replaced the indoor txv with the exact same txv and still the same issue. Could it be the outdoor txv be the problem. Also just a reminder my subcooling does not goes pass 4 no matter how much freon I add. If it was a dirty coil would my subcooling at least move pass 4 after i add the freon. Im still stuck on the outdoor txv and how it functions. Could the reversing valve be partially sticking.
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

You should always charge a heat pump system in the cooling mode. I assume you are doing that. It's possible that the reversing valve could be malfunctioning, yes. Remember a slow turning condenser fan and a dirty coil (outdoor) can also cause low subcooling. Have you rinsed out the condenser thoroughly with a stream of pressurized water?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
No im doing it in a few. Just dont get why my subcooling stays the same
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

Low subcooling is caused by the refrigerant not giving up it's heat as it passes through the condenser. What could cause this? Dirty condenser coils. A fan that is not working properly, etc.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Ok now i get it
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

Also, we should look at other factors. What is the TD (temp difference) across the indoor coil? What kind of pressures do we have? High and low side. And what kind of day is it? Hot, humid? Is the device you're using to measure sub cooling making good contact with the liquid line so we are getting an accurate reading?

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Ok
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

Thanks. I have to leave for a bit, but when I return, Ill look at your readings and respond.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
I just be damn. I blew the coils out with the hose and my subcooling is now rising.
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

Great! Sounds like we're on the right track! Let me know if you have additional questions. Otherwise, good luck! Thanks for using Just Answer and please don't forget to rate my service as that's how experts get paid (thanks in advance for any bonus left). Otherwise experts work at their own time and expense. Even though the Just Answer site has your money on deposit, it does not get transferred to me until you (positively) rate my service. Feel free to post back with any more questions. Remember, you can rate question at any point and still ask more questions (related to the same thing) later on. Experts prefer if you rate question at the end of our first chat.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

Did you have additional questions? I notice you had not rated question yet.

Ask Your Own HVAC Question
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

Please understand, even though the Just Answer site has a deposit from you, money is not credited to your expert until you (positively) rate the question. Thank you!

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Well i still having trouble getting subcooling. But i think i may be on to something. Im in a 12 story building, and all my lower units are having subcooling problems. I evacuated the system and out the vacuum on it for a couple of hours. Charged the and still having trouble getting subcooling. But I notice it fluctuate alot meaning there still impurites in my in system. All units are roof top units and and the line set rins 12 stories long down to the first floor. My vacuum pump is only 1 stage and i believe this may be my issue. Meaning I will need a 2 stage pump.
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

Yes, most likely. Also, always install a filter-drier close to the evaporator coil whenever you open a system up.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Well I never did install a filter drier. I know inhave one old one on the liquid line.
HVAC Technician: Tim H., HVAC Professional replied 1 year ago

It should be installed.

Ask Your Own HVAC Question
Ask Tim H. Your Own Question
Tim H.
Tim H.
Tim H., HVAC Professional
Category: HVAC
Satisfied Customers: 3,971
3,971 Satisfied Customers
Experience: Experienced in all aspects of HVAC, both residential and commercial.

Tim H. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Carrier 58SX gas fired condensing furnace that will
I have a Carrier 58SX gas fired condensing furnace that will not start. The pilot flame comes up upon the thermostat calling for heat but the flame is a bit lazy and it goes out after about 5-7 second… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Question for you regarding wiring a carrier infinity with a
Question for you regarding wiring a carrier infinity with a Honeywell lyric. I have a gas furnace and an AC condenser. Today the terminal with the abcd wires connected in the furnace has 2 sets of wir… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a carrier condenser outside and the relay keeps on
I have a carrier condenser outside and the relay keeps on popping I want to know if I can bypass until I can get a new one … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an old R-22 hybrid Comfortmaker/Carrier system that
I have an old R-22 hybrid Comfortmaker/Carrier system that has been changed to R-410AA local AC shop replaced my evap with a carrier FB series. They left the condenser system alone and replaced the TX… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has run without problem for the last two years. Lately, it has begun to shut down and then restart on its own after about an hour or more. The l… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Evaporator water flow too low alarm keeps happening.
Evaporator water flow too low alarm keeps happening. Recently cleaned coils now this. The pumps are running fine. The pressures are good on the approach. The water strainer is clean. What is this a ca… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
My Carrier is 4 years old. My problem is the condensate
Hi my name is Dave. My Carrier is 4 years old. My problem is the condensate drain is stopped up. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Carrier condenser Model#: 38HDC060321. Relay opens after
Carrier condenser Model#: 38HDC060321. Relay opens after about 1 minute of running. I've replaced the capacitor (usually burns out about every two years) and the main fuses (1 blew, replaced both). Go… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Have trouble with unit suction pressure rise but discharge
Have trouble with unit suction pressure rise but discharge don't … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a carrier furnace (1990') with a Heil Condenser. The
I have a carrier furnace (1990') with a Heil Condenser. The furnace blower doesn't shut off and the thermostat appears to be inoperative meaning the controls don't seem to have any effect on the syste… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Rheem Model number RCFA – HM3617AC, Suction pressure 68
Suction pressure 68 discharge pressure 92 why is my discharge pressure low. Outside temperature around 85 . … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a Carrier Condenser Model 38CK036320 I need to know
I have a Carrier Condenser Model 38CK036320 I need to know how to connect the new type S1-DP130024 Contasctopr… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x