I have a 2003 Trane WCZ060 two-stage (2 and 5 ton) 16 SEER

Customer Question
air conditioner/heat pump. The smaller...
I have a 2003 Trane WCZ060 two-stage (2 and 5 ton) 16 SEER air conditioner/heat pump. The smaller compressor is not making much head pressure, and will need replaced. The dual-stage thermostat is programmed with the first deadband at 1 degree (start stage 1 cooling), and the second deadband at 2 degrees (start stage 2 cooling). Will it damage the air conditioner to jump Y1 and Y2 at the thermostat until the small compressor is replaced?
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
5/24/2016
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,527
Experience: Furnace, A/C and heat pump specialist.
Verified
This should not cause any damage all you will be doing is energizing both stages at once to operate at as much capacity as possible.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
Hello, did you get the second part of my question?
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
I do not see a second part of the question ,Please let me know what it was.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
When the thermostat calls for max cooling upon turning the unit onto "cool", the small compressor runs for about 30 seconds or so, then it shuts off and there is a delay of thirty seconds or so before the big one kicks in. WHen I have Y1 and Y2 jumpered, there doesn't seem to be a delay; it seems like the small compressor is running then the big one kicks in without a delay. I don't understand this, as I thought there would be no difference between the thermostat energizing both leads and having them jumpered. That's why I'm a bit concerned that the jumpered state might damage the big compressor.
Customer reply replied 1 year ago
but according to the operating and installation manual for the unit, all of these decisions are made by the boards in the unit, not by the thermostat. The state for high cooling is both signals, Y1 and Y2, from the thermostat.
Customer reply replied 1 year ago
Did you get the 2 parts I sent about 1/2 hour ago?
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,527
8,527 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a tank less hot water heater that will not come on. It
Have a tank less hot water heater that will not come on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a GE power vent gas water heater that will not stay
I have a GE power vent gas water heater that will not stay on. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Why do we have warning signal showing on our panel also wot
Why do we have warning signal showing on our panel also wot is w 42 h mean … read more
travis webb
travis webb
tech.
2,159 satisfied customers
I have a 80uhg that when i call for heat the gas burner
I have a 80uhg that when i call for heat the gas burner doesnt light and the blower comes on … read more
travis webb
travis webb
tech.
2,159 satisfied customers
I have a York Diamond 80 and I am getting the 4 flashes code
I have a York Diamond 80 and I am getting the 4 flashes code for open high limit switch. … read more
airheatman
airheatman
HVAC Technician
8,527 satisfied customers
My recirculation fan does not shut off ony good man natural
My recirculation fan does not shut off ony good man natural gas furnace and the trouble light shows normal operation … read more
airheatman
airheatman
HVAC Technician
8,527 satisfied customers
Why is the supply connection at the header 1 1/2” do i have
Why is the supply connection at the header 1 1/2” do i have to run 1 1/2” to the pumps? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Americian standard freedom 80 single stage natural gas
americian standard freedom 80 single stage natural gas furnace won't light … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have Philco furnace Model G6RC 100C-16 - furnace runs for 4
Have Philco furnace Model G6RC 100C-16 - furnace runs for 4 minutes, then shuts off for 10 minutes. Red light blinks twice. Checked to make sure drain is operating, which it is. Checked the flame sens… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier Model 58MVP 120 blinking error code. 13.
I have a Carrier Model 58MVP 120 blinking error code … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennox airhandler cbx32mv-048-230-6-07 I have no
I have a lennox airhandler cbx32mv-048-230-6-07 I have no heat and this unit has heat strips. I have had techs out here and they have changed the 3 relays and today the mother board. lasts week the ma… read more
airheatman
airheatman
HVAC Technician
8,527 satisfied customers
I have a 1989 vintage Vaillant boiler that continues to
Hi, I have a 1989 vintage Vaillant boiler that continues to ignite and then shuts off. What would cause this problem? … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a Nordyne 3.5 Ton heat pump that a acted up and
I have a Nordyne 3.5 Ton heat pump that a acted up and wouldn't heat last week. It has small leak in coil that seems very slight. R 22 imstalled , unit holding 40psi for twenty minutes the repairman (… read more
airheatman
airheatman
HVAC Technician
8,527 satisfied customers
The red emergency on/off switch was accidentally turned off.
The red emergency on/off switch was accidentally turned off. After turning it back on, checking the breakers, and turning the thermostat off, then on and resetting it, I still have no heat. What else … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I changed my thermostat and then put the original back nd
I changed my thermostat and then put the original back nd not it will not light up at all … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,090 satisfied customers
Thermostat keeps returning to 70 degrees even tho I cancel
Thermostat keeps returning to 70 degrees even tho I cancel present temp by pressing run and put a new lower temperature in and it still returns to apparently a programmed 70 which comes in during the … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have 4 honeywell rlv4305 thermostats. they are all hot on
Hello, I have 4 honeywell rlv4305 thermostats. they are all hot on the top right corner. they are all in standby mode. Is this an issue, or are they hot, because they are not calling for heat right no… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I recently had a bosch geothermal CE035 installed in my
i recently had a bosch geothermal CE035 installed in my home. i am wondering how do I change the setting to keep the auxiliary heat off longer ? … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x