I have a Rinnai R94LSi that's been installed and working

Customer Question
great for several years....
I have a Rinnai R94LSi that's been installed and working great for several years. A couple months ago we started getting water that was about 30 degrees colder than the temp set on the Rinnai. Flushed the system and cleaned the flame rod which didn't help. Finally cleaning the outgoing water thermistor did the trick, as it wasn't reporting the correct temps.
Now, it's doing the same thing (water 20-30 degrees colder than normal), but this time the thermistor seems to be acting correctly based on testing the resistance against values in the manual. What should I try next? Both times this has happened, there has been no error code given by the unit. It acts like everything is great, and it advertises that the outgoing water is the correct temperature (as checked with the down arrow-off/on button trick).
Any ideas of what to try next?
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 hours by:
5/23/2016
HVAC Technician: Gaztech, HVAC Technician replied 1 year ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 511
Experience: Owner at Gaztech
Verified
Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue.If my initial response doesn’t answer your question then let me know and we can continue our conversation.NOTE: I can only get paid for assisting you if you click FINISHED and RATE ANSWER after you are satisfied with answer.Are you ready?
Ask Your Own HVAC Question
Customer reply replied 1 year ago
Sure
HVAC Technician: Gaztech, HVAC Technician replied 1 year ago
I had that issue with a Rinnai last month and resolved the issue after replacing the main control, it did not read the correct resistance of the thermistor, I confirm that with a different sensor with .45 k oms differential
Ask Your Own HVAC Question
Customer reply replied 1 year ago
is the thermistor the only thing controlling the outgoing temp, or is flow control related? I ask because I noticed last night that the reported flow control numbers don't appear to be accurate either.
HVAC Technician: Gaztech, HVAC Technician replied 1 year ago
the flow switch does not control the temp. it will shut off system
Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 1 year ago
OK?
Ask Your Own HVAC Question
Customer reply replied 1 year ago
Can you be more specific about how to confirm I need a new PCB? I need a new thermistor first? I'm not sure what differential I would be measuring, since I would assume the new thermistor would have the same resistance levels as the current one.
HVAC Technician: Gaztech, HVAC Technician replied 1 year ago
If the resistant of thermistor is to spec,as you said there is no need to replace it, the pcb is not reading as it should.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
When you said, "I confirm that with a different sensor with .45 k oms differential" what did that relate to? That you tried a different sensor and the pcb read it differently when it should have read it the same as the first one? Is there any other test I should do to confirm that replacing the pcb is the only fix?
HVAC Technician: Gaztech, HVAC Technician replied 1 year ago
That is what I am saying, other than that there Might be several volt tests that could be done with a good service manual.I will let another expert share their knoledge
Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 15,809
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified
Hello and thanks for using this service, if you have been waiting do not worry or get upset. I am HVAC Guru an extremely experienced tech on the site and I try to get to as many customers as I can. I just picked up your question now. NOTE it takes time for me to type research and add links so please wait for me to respond back I can only do this so fast. Secondly I am not paid anything until you rate my service good using the STAR RATING LINK at the top of your page, the money is paid to the site not me directly. Answer: Replace the PCB based on what you have done nothing else will cause that. All I ask is please use the Star Rating Link at the top of your page before leaving, that is the only way I am paid anything through the site.....tips are greatly appreciated so thank you very much for using this service. If you have any other questions just post back to me here anytime!
Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 1 year ago
I am sorry but there is nothing different in your answer than what I previously explained to customer, Same answer.
Ask Your Own HVAC Question
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 511
511 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Weil-McLain CGa boiler. The pilot is lit and it
I have a Weil-McLain CGa boiler. The pilot is lit and it sounds like it is switching on and off (when the thermostat is on) but we're getting no heat. Is there something I should be checking? Thanks. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My unit is not operating correctly. I have it set at a temp,
my unit is not operating correctly. I have it set at a temp, and it doesn't come on when the temp goes below the set heating temp. I have to manually hit the set button and it comes on, but then it do… read more
HVAC Guru
HVAC Guru
HVAC TECH
15,809 satisfied customers
My Trane TUE080A936K2 furnace isn't heating the ignitor
my Trane TUE080A936K2 furnace isn't heating the ignitor never glows, but the fan spins up … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Looking for replacement blower motor for an old RUUD gas
Looking for replacement blower motor for an old RUUD gas furnace model HN-175JD blower # RL10-9DUH … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a York central heat unit. The problem is it wants to
I have a York central heat unit. The problem is it wants to turn on to give heat but shuts off after about 2 seconds and keeps on doing the same thing. Had this problem 3 weeks ago. Unplugged limit sw… read more
Gaztech
Gaztech
HVAC Technician
511 satisfied customers
I am replacing a RUUD 3aat86b9a1 with a Honeywell
I am replacing a RUUD 3aat86b9a1 with a Honeywell RTH2510/RTH2410v series. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Just inherited my grandparents house. Built in 1972. They
Just inherited my grandparents house. Built in 1972. They have a closet that is 50 by 70 inches that used to house a gas water heater and a gas furnace, below the closet is the intake air. The gas fur… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have the same problem with my code 33 I followed your
I have the same problem with my Bryant code 33 I followed your instructions as described here and it worked so I need a new limit switch, with one caveat, I let the wires touch metal and now I get not… read more
HVAC Guru
HVAC Guru
HVAC TECH
15,809 satisfied customers
I have a Heat-N- Glo gas fireplace. Fire starts, when I turn
I have a Heat-N- Glo gas fireplace. Fire starts, when I turn switch on, burns for a few minutes, then go out & in a few minutes start burning again … read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
I have a Trane XE90. When the cover, covering the chamber
I have a Trane XE90. When the cover, covering the chamber containing the gas tubes, igniter, heat sensor, flame sensor rod, etc. is off the system runs perfect. If I put the cover on the system will i… read more
HVAC Guru
HVAC Guru
HVAC TECH
15,809 satisfied customers
I have a leak in the water supply pipe right at the
I have a leak in the water supply pipe right at the connection where the pipes are welded together … read more
HVAC Guru
HVAC Guru
HVAC TECH
15,809 satisfied customers
My temperature gage is stuck on Hold 67. How do I clear the
how do I clear the program so I can regulate the temp… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I want to know if I can on a F 45 Greenville jotul
I want to know if I can cook on a F 45 Greenville jotul woodstove. … read more
Webb-Guy
Webb-Guy
tech.
77 satisfied customers
Our furnace is no heating. I just changed the filter. It
I just changed the filter. It doesn't seem to be lighting. The red LED is flashing 1 + 3 which indicates "Flame Sense out of sequence". … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Heater blowing cold air, Just replaced the filter, and I
Just replaced the filter, and I think that was the problem, but it still won't heat … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 5 ton package unit. the first time i turn on the
i have a 5 ton package unit . the first time i turn on the heater its creating a large amount of sut in the exhaust … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a electric furnace. The heating elements come on but
I have a coleman electric furnace. The heating elements come on but the fan does not run. The fan runs when you run it manually or with the A/C turned on. What sencer needs changed? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an Englander MDL 13-NCH 6" pipe. I have always been
I have an Englander MDL 13-NCH 6" pipe. I have always been confused about the connection on the top of the stove to the black pipe. It doesn't seem to fit tight inside it and I get some blow back smok… read more
Paul the Plumber
Paul the Plumber
Vocational, Technical or Trade Scho
21 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x