I have an Aprilaire 8463 thermostat. When I set the cooling

Customer Question
HI, I have an Aprilaire...
HI, I have an Aprilaire 8463 thermostat. When I set the cooling temperature, it forces the heating temperature to change so that the cooling temperature is no less than three degrees warmer than the cooling temperature. I understand the need to prevent systems triggering too frequently, but this creates a problem. During crossover periods of the year, the temperature can get hot during the day and then cold at night. Dealing with a three degree differential between heating and cooling will require that I go into the thermostat each day to manually adjust, defeating the purpose of a programmable thermostat. Is there any way to adjust an Aprilaire thermostat so it would allow a differential between heating and cooling temperature settings of two degrees instead of three? If not, are you aware of any other brand that either has a lower differential between cooling and heating settings, or that allows me to set one myself to two degrees?
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
5/9/2016
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 15,824
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified
Hello and thanks for using this service, if you have been waiting do not worry or get upset. I am Appliance Guru an extremely experienced tech on the site and I try to get to as many customers as I can. I just picked up your question now. NOTE it takes time for me to type research and add links so please wait for me to respond back I can only do this so fast. Secondly I am not paid anything until you rate my service good using the STAR RATING LINK at the top of your page, the money is paid to the site not me directly. That one can not be changed, however an older one like the 8353 would allow for that differential setting 1-3 degrees. All I ask is please use the Star Rating Link at the top of your page before leaving, that is the only way I am paid anything through the site.....tips are greatly appreciated so thank you very much for using this service. If you have any other questions just post back to me here anytime!
Ask Your Own HVAC Question
Customer reply replied 1 year ago
Take your time. But note that the old 8353 allows you to adjust the differential between the temperature you set - either hearing or cooling system - and the temperature the austen kicks in in response to your setting. This is not the same as the differential minimum between heating and cooling temperatures, which is what I'm asking about.
Customer reply replied 1 year ago
Sorry, by "austen" I meant "system."
Customer reply replied 1 year ago
I just saw that justanswer charged my card for the full amount even though you said you had to do research to answer my question and the discontinued model you referred me to provides a setting that's different than the one I was asking about. Please confirm you will answer my original question.
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago
All of these thermostats are going to be accurate within 1-1.5 degrees without adjustments. I understand what you are saying, but I have found nor know of any that can do what you want it to do the most I found is an older one still but it only is adjustable by 1.5 degrees.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
I'm not sure what you mean by "can do what you want." I asked if there are any out there that are "either" adjustable or ALREADY have a minimum differential between cooling and heating temperature settings of less than three degrees. To confirm, are you BOTH that there are none that have such a minimum differential that can be adjusted AND that there are none with a minimum differential that is less than three degrees?Separately, I'm not sure why you refer to accuracy, it's not part of my question and it makes me ask whether you understand the question. In addition, I checked the manual for the discontinued model you referred to (Aprilaire 8353) and, again, it has NO settings for changing the minimum differential between cooling and heating temperature settings.A reply responding clearly and comprehensively to my question would be appreciated.
HVAC Technician: HVAC Guru, HVAC TECH replied 1 year ago
Let me see if another expert can assist you on this please stand by
Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,520
Experience: Furnace, A/C and heat pump specialist.
Verified
You should be able to make this adjustment in the setup menu.That is considered the deadband differential. Let me know if you have instructions on entering setup menu and you can adjust the deadband (Function 14) to 2 degrees.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
But my question was WHAT ARE the models that have or allow a differential of less than three degrees,Customer Neither you nor HVAC guru have said which thermostats have that feature. That was my question. The justanswer website said I wouldn't be charged until I received a "satisfactory" answer, but I've been charged and I haven't gotten a responsive answer. Thanks trying to help out, but justanswer charging my card without me getting a responsive answer is BS.
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
My answer as for the thermostat you currently have. If 2 degree is sufficient for your need, why would you want to replace it.Simply set the differential according to the instructions. If you are determined to replace thermostat, let me know what brand you prefer and features and I can suggest one as there are literally dozens of good ones available,
Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
Your question was " Is there any way to adjust an Aprilaire thermostat so it would allow a differential between heating and cooling temperature settings of two degrees instead of three" You can make that adjustment in the setup menu function 14. Since your thermostat offers that feature, I did not reply with other models as your question said "If not, are you aware of any other brand that either has a lower differential between cooling and heating settings, or that allows me to set one myself to two degrees?
Ask Your Own HVAC Question
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,520
8,520 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I got a new Honeywell programmable thermostat in April and
I got a new Honeywell programmable thermostat in April and connected to wifi. We departed for 4 months this summer and had to turn off the wifi, which meant I had no connection. Now I am ready to prog… read more
airheatman
airheatman
HVAC Technician
8,520 satisfied customers
My Honeywell programmable thermostat shows bat lo. I changed
my Honeywell programmable thermostat shows bat lo. I changed to new batteries but still get bat lo message. thermostat is still working and house is heating but I cannot program it … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am trying to replace a Honeywell programmable thermostat
I am trying to replace a Honeywell programmable thermostat with a Totaline P474-1100 RF thermostat and P474-1100REC receiver. The thermostat will only be controlling heat via a gas-fired steam boiler.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I replaced a non-programmable thermostat with a Honeywell
I replaced a non-programmable thermostat with a Honeywell RTH2300/RTH221. … read more
airheatman
airheatman
HVAC Technician
8,520 satisfied customers
I have a Carrier Programmable Thermostat and the AC keeps
I have a Carrier Programmable Thermostat and the AC keeps running. Can I reset it somehow or could there be another problem? … read more
HVAC Guru
HVAC Guru
HVAC TECH
15,824 satisfied customers
I'm swapping out a Honeywell non-programmable thermostat
I'm swapping out a Honeywell non-programmable thermostat with a Honeywell programmable one. Wires don't quite match. … read more
HVAC Guru
HVAC Guru
HVAC TECH
15,824 satisfied customers
I have a Rodgers 1F90-51 programmable thermostat. Came home
I have a White Rodgers 1F90-51 programmable thermostat. Came home tonight to a very hot house and a display that showed "BATTERY" solidly (not flashing). Went out and bought a brand new pack of AA bat… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
0 satisfied customers
I have a Chromotherm III programmable thermostat that now
I have a Chromotherm III programmable thermostat that now shows -AC and does not turn on the the air conditioner. I changed the three AAA batteries for new, but no luck. … read more
airheatman
airheatman
HVAC Technician
8,520 satisfied customers
I have a -Rodgers programmable thermostat 1F82-261,
I have a White-Rodgers programmable thermostat 1F82-261, purchased last year. I also had the electric pump serviced at that time, which needed some new parts. I have been using the heat, programmed, a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I changed my batteries in the Aprilaire thermostat because
Hi, I changed my batteries in the Aprilaire thermostat because the backlight no longer lit and when I put in the new batteries the only thing that I read is the word OFF. It was a new pack of batterie… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I am interested in getting a programmable thermostat my
I am interested in getting a programmable thermostat my current one is water furnace model TA32E12 … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
MyCT2800 Programmable Thermostat blinks battery low after
myCT2800 Programmable Thermostat blinks battery low after installing new ones??? … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I have a Carrier TP-PRH01-A programmable thermostat but it
I have a Carrier TP-PRH01-A programmable thermostat but it is not WiFi capable. I would like to replace it with a Honeywell WiFi programmable thermostat. Can you tell me which model(s) you would recom… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an old honeywell two wire programmable thermostat
I have an old honeywell two wire programmable thermostat that I would like to replace with another honeywell thermostat RTHL2310 RTHL221 ....can I do this with only the two wires? Marie … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Just purchased programmable thermostat RTH2410B connected
Just purchased programmable thermostat RTH2410B connected wires furnace is not responding … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Linstat Setback programmable thermostat,serial #
I have a Linstat Setback programmable thermostat,serial # 038731, model # TH101 A-40. It runs electric heaters on 240 vac. Somehow, it switched over to Celcius display and I can't figure out how to ge… read more
airheatman
airheatman
HVAC Technician
8,520 satisfied customers
I have a Honeywell touchscreen programmable thermostat that
I have a Honeywell touchscreen programmable thermostat that is just over 10 yrs old and the light feature has stopped working. The thermostat is very similar to the current model RTH8500D. How do I ge… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a 8466 aprilaire thermostat and when I took the
I have a 8466 aprilaire thermostat and when I took the batteries out the whole system shut off… read more
airheatman
airheatman
HVAC Technician
8,520 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x