Hi Billy, I've got a Trane XV 80 Model TUD100R9V5J1 that has had intermittent gas valve problems for years. Problem was at Molex connector to gas valve. I found if I pulled it to one side with wire ties, it worked. Recently, that stopped working. But there were times when I could jiggle the 3 wires and get the gas valve to come on/off. While debugging, I measured 24VAC from P.M. (red) to Hi (brown) and 24VAC from P.M. to C (light blue?). I took the module with the switch/connector off and found cracks around the 3 pins. Soldered them so they made good connections. Still no joy. Can't measure 24VAC anymore during firing cycle. Igniter lights up nicely, inducer is running well, red LED flashing fast so calling for heat. But after igniter is on for a while, it just shuts off. Lockout happens after 2 cycles. Any ideas? Thanks, Brian
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
4/15/2016
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,501
Experience: Furnace, A/C and heat pump specialist.
Verified
Are you getting any error codes when burners fail to ignite?
Ask Your Own HVAC Question
Customer reply replied 1 year ago
No. Red LED continues to fast flash (call for heat) and then goes to slow double flash after two cycles (locked out). Yellow LEDs on bottom of Intell-Ignition board: DS3-allways on, DS4&DS5-never on, although DS4 may be on dimly. Green DS6 is on with some flickers off. I think this refers to air flow.
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
If we are not getting 24 volts to the valve after igniter lights and no error code, this is going to be a bad board.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
Well, I was figuring it might be that. But why would it go bad just after I fixed the intermittent connection? Doesn't make sense. And the overall 24 volts is good.
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
Not sure of the relation, but as soon as igniter lights, board should send 24v to valve.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
Yes, of course. I knew that but was hoping you would be able to provide some specifics regarding the board, such as what the yellow LEDs are indicating, does DS4/DS5 always being off indicate a problem (and what problem), perhaps ways to isolate if it is indeed the board vs something else, and so on. Also, as an aside to trying to solve this problem, my experience with Just Answer has been, well, a little weird. I found the site while googling solutions to this problem and was reading people's posts and the answers, and they were pretty good. I kept getting this pop-up from "Billy" asking details about my problem. Finally, after getting frustrated, I submitted a detailed description of my problem, expecting "Billy" to just respond. Instead, I get passed off to "Phil" and I learn that payment is expected (surprise!). But "Phil" seemed to have good credentials and is an older mechanical engineer, as am I. So, OK, even though I don't normally do this kind of thing (paying for internet interaction), I need to get this fixed and I'm out of things to try. So I agree, and then get passed off to "Airheatman" and endless solicitations to buy premium service, buy monthly subscriptions, etc, etc. It reminds me of the ugliness of used car salesmen. OK, I'll get off my soapbox now. Sorry to go on, but I'm frustrated and getting hit up to spend more and more money, in different ways ($24 to talk on the phone?), is not helping my frustration.
Customer reply replied 1 year ago
Well, I just checked my email and I see that because you had written something to me, I was being billed the additional $40, as if your response was an answer I was 100% satisfied with. It was not, hence my additional exchanges with you. *IF* we can come to some conclusion that satisfies me (even if it does mean buying a new board), then I'll pay. But so far, I'm not there. Can you provide me the kind of information that I expected to get from this consultation?
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
Sorry for the confusion and the way website operates. If you start a new question and mention a specific expert, the expert is sent an email and has 15 minute lock on question.If expert is not available,the question is open to all experts.We do not want your money if we are unable to help. The phone call offer is an automatic offer from website and only should be billed if you accept the offer and prefer to talk by phone.I am going to open this back up and see if perhaps Billy is available now since he was the original expert you requested.Please do not rate or respond as that will send back to me and delay even further getting Billy.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
OK, thanks for the response. After working on it some more, I decided to order the upgraded replacement board. I suspect I have two unrelated intermittent electrical problems. I may have fixed the one caused by three cracked solder pads on where the pins in the molex connector attach to the circuit board in the black switch module on the gas valve. But there seems to be an intermittent something bad on the Intel-Ignition board. Generally, there's no 24VAC coming to the gas valve. But sometimes, rarely now, it does come on and the furnace lights for a while.
Customer reply replied 1 year ago
Oops, sorry about responding. I had read your comment about not rating, but missed the part about not responding. Oh, well.
HVAC Technician: HvacmanSean, HVAC Technician replied 1 year ago
HvacmanSean
HvacmanSean, HVAC Technician
Category: HVAC
Satisfied Customers: 222
Experience: Owner HVAC company
Verified
Hey brian are you needing help ? I have seen this ticket open for a day or so now
Ask Your Own HVAC Question
Customer reply replied 1 year ago
No, I don't need help. I need to say that I was extremely disappointed and unimpressed with what transpired during my interaction with Just Answer. Assuming this is someone not familiar with my experience, please see the previous posts. I received exactly nothing useful to me, yet despite your promise, it appears that I have already been billed for this, and kept getting pushed, pushed, pushed, to buy more "services". I am not satisfied and expect there to be no charge. Please rescind the charge if it has been made. I see I have an email, likely for a survey, and I'll likely fill it out. I really expected a better experience.
HVAC Technician: HvacmanSean, HVAC Technician replied 1 year ago
Brian, I apologize you weren't satisfied, Wish I was able to help but were only allowed one expert to lock on at one time, Ill put in a refund request for you.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
Thank you.
Ask HvacmanSean Your Own Question
HvacmanSean
HvacmanSean
HvacmanSean, HVAC Technician
Category: HVAC
Satisfied Customers: 222
222 Satisfied Customers
Experience: Owner HVAC company

HvacmanSean is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am looking for a gas valve for my Duo Therm Model 708001-2
I am looking for a gas valve for my Duo Therm Model 708001-2 mobile home furnace. The numbers on the valve are TF-555 TM-6 … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,070 satisfied customers
I am trying to figure out why our pilot light won't ignite.
I am trying to figure out why our pilot light won't ignite. Our power went out today and now the furnace is blowing cold. We have reset the breaker and the on/off switch and the gas and the thermostat… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a T.H.E. 90 furnace, model 2970E766. A couple of days
I have a Coleman T.H.E. 90 furnace, model 2970E766. A couple of days ago, the high speed blower wire (black) at the blower relay melted. I replaced it with a new 1/4 female blade terminal. Now the red… read more
airheatman
airheatman
HVAC Technician
8,501 satisfied customers
My boiler flashes red on occasion and says hardware fault
my boiler flashes red on occasion and says hardware fault reset control if problem reoccurs replace sage control … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Honeywell pro 3000 thermostat to install and there
I have a Honeywell pro 3000 thermostat to install and there is only a red and a white wire what wiring diagram do I use? … read more
airheatman
airheatman
HVAC Technician
8,501 satisfied customers
My honeytwell device suddenly shoots up to 90 degrees for no
My honeytwell device suddenly shoots up to 90 degrees for no reason and then none of the controls work to turn it down … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,070 satisfied customers
I have a tempstar DC90 and it is on but is not blowing out
I have a tempstar DC90 and it is on but is not blowing out hot air. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I would like to install a new thermostat with my new hvac
Hi I would like to install a new thermostat with my new hvac and I need some documentation please … read more
airheatman
airheatman
HVAC Technician
8,501 satisfied customers
I have a Central Air BRCQ0301BC system (30,000 BTU)
I have a Coleman Central Air BRCQ0301BC system (30,000 BTU) installed in a 16 x 80 single wide trailer. It has been charged several times, but loses its cooling capacity within 4 days of running. A te… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Trying to install thermostat honeywell rth2510b to a 2 wire
trying to install thermostat honeywell rth2510b to a 2 wire system where should the wires go???… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I purchased a CS-E12RKUAW / CU-E12RKUA heat pump. There was
I purchased a CS-E12RKUAW / CU-E12RKUA heat pump. There was no product manual provided with the units. The unit appears to generally operate well, but I have a lot of questions about details of the op… read more
airheatman
airheatman
HVAC Technician
8,501 satisfied customers
My furnace is a hot water boiler with radiators. It does a
My furnace is a hot water boiler with radiators. It does a great job heating but this last week it only has been raising the house temp from 60 to 66 in the mornings and then cuts out. I have two zone… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Rheem RGDE 07NNMAGR what does a ingniter moduel look like.
rheem RGDE 07NNMAGR what does a ingniter moduel look like … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Heil furnace 1992 year piolt come on burner come on burner
heil furnace 1992 year piolt come on burner come on burner stays for abount 5 minits then gos out turban fan stays running exhaust fan stays running about 2minits piolt coms back on burner come back o… read more
airheatman
airheatman
HVAC Technician
8,501 satisfied customers
I have a York r-22 outdoor split system ac/heater. This
I have a York r-22 outdoor split system ac/heater. This morning, the fan seems to be working but no heat. When I looked into the unit, there is a flashing red light. Can you identify what this issue m… read more
airheatman
airheatman
HVAC Technician
8,501 satisfied customers
Heater code 57. Can you assist with repairing? Couple
Couple weeks....air conditioning worked through the summer. Heating is not. New unit. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,070 satisfied customers
I have a Burnham PV75WC TBWN and the breaker on the ignition
I have a Burnham PV75WC TBWN and the breaker on the ignition transformer blows intermittently. It will operate perfectly for as much as a week then it pops the breaker. My oil supply is good and the f… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Reset gas knob after switching gas tanks Reset gas valve
Reset gas cock knob after switching gas tanks Reset gas valve after changing gas supply … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x