i have a Nordyne furnace in my manufacture home that will not fire. It has a standing pilot that stays lite and i got 24 volts at the gas valve that has a slight buzzing noise until i pull one of the leads. my line of thought is if i have power at the gas valve then all my other switches are good and the gas valve is bad
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
4/1/2016
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,325
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.I agree with your assessment. If the pilot is lit and you have 24 volts to the gas valve but no main burner ignition then you need a new gas valve.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
but shouldnt the induction fan start before power is supplied the the gas valve
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago
Yes but that doesn't have anything to do with the gas valve issue. If you have 24 volts to the valve then the valve should open and the main burner should fire. The draft inducer not running is a separate issue.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
i thought that the fan running should be the first step in the sequence of operation
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago
Of course I'm assuming you have gas to the gas valve
Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago
Again, the inducer not running is a separate issue. Yes the inducer starting up is the first thing that should happen with a call for heat. Do you have power to the inducer?
Ask Your Own HVAC Question
Customer reply replied 1 year ago
i havent checked that and in i dont know if the inducer is part of the motor or a stand alone component
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago
For our purposes they're the same thing. Do you have power to the inducer?
Ask Your Own HVAC Question
Customer reply replied 1 year ago
ill have to check that but if thats not running would i still get 24 volts to the valve
Customer reply replied 1 year ago
i would think it would try to open the vale without the fan runnig
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago
You said you had 24 volts at the valve.
Ask Your Own HVAC Question
Customer reply replied 1 year ago
yes
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago
The draft pressure switch would have to be stuck closed to get 24 volts to the valve if the inducer isn't running
Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 1 year ago
Do you have any more questions?
Ask Your Own HVAC Question
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,325
22,325 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Changes the inducer motor on our furnace and it fired but
GOOD AFTERNOON, changes the inducer motor on our furnace and it fired but stopped about 30 seconds giving me an error code that low fire pressure switch is stuck closed. Removed try to check if there … read more
HvacmanSean
HvacmanSean
Owner
HVAC
219 satisfied customers
I have a year-old Goodman furnace, and while the thermostat
I have a year-old Goodman furnace, and while the thermostat says it's heating, the fan doesn't come on and no heat is coming through the vents. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Callman forced air gas furnace won't light reading is to
Callman forced air gas furnace won't light reading is to flashes says pressure switch stuck closed I don't know where the pressure switch is… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
My unit is flashing 1 what are my options. What about the
my unit is flashing 1 what are my options JA: Did you double-check the thermostat? And what about the unit's filters? Customer: yes what about the thermostat the air works fine JA: Do you plan on doin… read more
Elliott Oxton
Elliott Oxton
NVQ Level 2
4 satisfied customers
Have a lennox cbx26uh-048-230-1 blower otor just hums, put
have a lennox cbx26uh-048-230-1 blower otor just hums, put new capacitor on, motor turns free when off. is the motor bad? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I believe that the fan relay on my furnace controller is
I believe that the fan relay on my furnace controller is stuck closed. What can I do to confirm that, and is it reasonable to believe that it will open if I tap it?… read more
Rick
Rick
HVAC Supervisor
22,325 satisfied customers
Roof top york dl10n24ataaa3c. Bolwer motor wont shut down
bolwer motor wont shut down even with termostic removed … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I've a GMP 125-5 furnace. will not light,what is the inches
I've a GMP 125-5 furnace. will not light,what is the inches of water required to operate psi sw. the guide on the door says the sw is stuck closed. I made a manometer with tubing and only get about 3/… read more
Rick
Rick
HVAC Supervisor
22,325 satisfied customers
I believe we have a flap that is stuck closed on our unit.
I believe we have a flap that is stuck closed on our unit. We are having the same problems we had a few months back, with lonely a small amount of warm air blowing through out system. We tried switchi… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
On the top floor, cool air is coming from the vents only on
On the top floor, cool air is coming from the vents only on one side of the house. The other side of the top floor is not getting any air from the vents.I have a 2 story house with each floor having i… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Heil HVAC system. Trying to run AC. Outside unit
I have a Heil HVAC system. Trying to run AC. Outside unit runs, returns cold refrigerant. Blower fan runs, but there is no flow thru to the ductwork. This is a sudden onset problem. Is there a damper … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My aquastar burner decided to stay on. Hopefully I caught it
Hi, my aquastar burner decided to stay on . Hopefully I caught it in time. Could you tell me what i need to fix … read more
Rick
Rick
HVAC Supervisor
22,325 satisfied customers
I have a Lennox model g61mp-48c-110-09 and it does not
Hi I have a Lennox model g61mp-48c-110-09 and it does not appear to be igniting showing a red light error code of either 2+4 or 4+2, I believe it is the 2+4, the furnace is also controlled by a Honeyw… read more
Rick
Rick
HVAC Supervisor
22,325 satisfied customers
My furnace fail to ignite the burners. Motors comes on,
My furnace fail to ignite the burners. Motors comes on, igniter lights up, I have power coming to the gas valve, but burners fail to ignite. I think it may be a faulty gas valve but how can I make sur… read more
Tim Ohms
Tim Ohms
HVAC Journeyman
31 satisfied customers
Ruud furnace. error code says pressure switch stuck closed
ruud furnace. error code says pressure switch stuck closed (4 blinks). I was trying to find out where that switch is. We have had high winds and at least one note suggested that might have tripped the… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My furnace will not shutoff automaticly it is electric.
my furnace will not shutoff automaticly it is electric … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a Rheem gas furnace model #RGDG 10EAMER...will not
Have a Rheem gas furnace model #RGDG 10EAMER...will not start. Have a blinking green light on the circuit board. … read more
Rick
Rick
HVAC Supervisor
22,325 satisfied customers
Amana GUCA070AX30 P1239302F model. No heat. Blows cold air.
Amana GUCA070AX30 P1239302F model. No heat. Blows cold air. Code 4= limit switch primary or secondary. Replaced limiter switches, parts people say there are two but we could only find one. According t… read more
Rick
Rick
HVAC Supervisor
22,325 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x