I installed a Carrier Cor...
I installed a Carrier Cor WiFi Thermostat today and followed the exact same wiring as the previous HoneywellThermostat that was connected to my Carrier Furnace and AC Units. I have a two zone system so I installed two of the COR thermostats. Set my cooling point to 74 for at night and my heat point to 68. The thermostat when into cooling mode when the house reached 75 after a while. It showed cooling on the thermo and the app but only heat was coming out and the house shot up to 84. Had to turn off the system and open windows to cool house. What did I do wrong?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 19 minutes by:
3/8/2016
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, is your system a heat pump with gas or electric furnace back up heat, or does the unit that sits outside run only in the summer when cooling is required.

I ask that because some thermostats have to be programmed for heat pump operation, and if not programmed, will heat when calling for cooling etc.

Tell me if that is what it seems to be doing or not, and if you want me to spend a few hours coaching you on all this or not.

We can go from there.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have carrier two stage electric Furnace in the attic and two carrier AC units outside. My wires on the original thermostats was as follows: Rh jumped to RC with main red wire in RH, Y, C, W, G, W2. I photographed them and them connected it to the COR smart thermostat except instead of plugging the R wire into Rh I plugged it into Rc. The system detected all of the wires and it seemed like installation was all good.
Customer reply replied 2 years ago
My system is zoned for upstairs and downstairs too. with two thermostats. I have replace both honeywell with Carrier CORs
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Thanks, ***** ***** a straight forward type of system and wiring set up, the problem is most likely related to the zone controls... so far however, the wiring errors if any are not obvious.

Is there a jumper between Rc and Rh... if so that is how it should be.

I need the full model number of the COR thermostats, just 'COR' is not enough. Meantime look at the programming instructions, you may have selected 'heat pump' as the system type instead of 'conventional system'

If I miss you tonight I will pick your response up in the morning.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
COR model is TP-WEM01 and I was told that the unit is internally jumped so no need to put a jumper between Rc and Rh on the new COR Thermostat.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Thanks, ***** *****'t see any potential problems with the way you wired the thermostats.... can you give me the brand and model number of the zone controller these connect to? Or a photo of the thermostat connections to the zone controller.

Use the paper clip icon at the right end of the tool bar to attach the photo's please.

We can go from there.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Calling it a night for now. Can resume in the morning. Thanks.
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Thanks, ***** *****'t see a problem with your thermostat wiring, there is must likely some conflict at the zone control box, get me those pictures I will look them over tomorrow please.

Locate the zone control box by finding the thermostat wire connections in the furnace and following that wire back to its source.

See you in the am or whenever you get back.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Phiil, I have a comfort zone ii carrier thermostat and it
Hi Phiil, I have a comfort zone ii carrier thermostat and it operates a 4 zone carrier system. Was wanting WiFi without upgrading everything. Is it possible to just change out thermostat and keep zone… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
We have a Carrier Infinity System Thermostat Model #
We have a Carrier Infinity System Thermostat Model # SYSTXCCUIZ01-A and the plastic "heat" and "zone" buttons are broken. We are looking for a new unit with this model number to replace our current un… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
The screen on my Carrier COR thermostat went blank, is there
Hi, the screen on my Carrier COR thermostat went blank, is there any other reason that an interruption in the power supply that could cause this i.e. dead batteries? … read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
Dear Phil: Please find my thermostat and furnace info in the
Dear Phil:Please find my thermostat and furnace info in the pictures attached. I would like to update my thermostat (which is very old and basic) to a new one, with if possible the zones control and t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Attempting to replace my downstairs (main level) thermostat
Attempting to replace my downstairs (main level) thermostat with a Nest. I have wires on O&B but do not have a heat pump. Cannot find anywhere that this scenario would be possible. I do have a humidif… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier ComfortZone II system three zone as well,
Hey - I have a Carrier ComfortZone II system three zone as well, which includes AC. Looking to switch over that allows remote access. Previously you suggested (three years ago) to use the Honeywell Tr… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a carrier comfort zone 2 thermostat and it works well
I have a carrier comfort zone 2 thermostat and it works well through out the day but around 5 pm the temperature starts rising in area it controls even when I turn 5he temp retire down to 70, it rises… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a new Lennox system that uses the Lennox iComfort S30
I have a new Lennox system that uses the Lennox iComfort S30 thermostats, and the iComfort3 iPhone app set up so that I can control them remotely. I have a cabin up in the mountains that I would like … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a carrier comfort zone II with 3 zones. Is it
I have a carrier comfort zone II with 3 zones. Is it compatable with any wifi thermostats?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
We have a new home that was just built and we have a single
We have a new home that was just built and we have a single unit with 2 thermostats(one upstairs and one downstairs). I know heat rises. However, with both set on 75, it stays 75 upstairs and like 68/… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier Comfort Zone system which was installed in
I have a Carrier Comfort Zone system which was installed in 1994 when we built the house. My problem is that there is something wrong with the preprogrammed controls. I can set the AC from 68-72, but … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Carrier heat pump system is a dual fuel system installed
My Carrier heat pump system is a dual fuel system installed in 2009. During every between seasons when auto should change to heat or cool, it has failed every season. The thermostat malfunctions as ex… read more
N4IEA
N4IEA
Customer Service
Associate Degree
227 satisfied customers
i have put in carrier central ac system, performance condenser
i have put in carrier central ac system, performance condenser with infinity handler and 2 infinity thermostats with 2 zones, up and down stairs with dampener for the zones in the attic. problem is: t… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an 21 month old Carrier 16 Seer Puron Infinity H/P 25HNA648A003
I have an 21 month old Carrier 16 Seer Puron Infinity H/P 25HNA648A003 system in a three zone configuration. we have an intermittant problem (about every six weeks) of the furnace doing runaway heatin… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a 1996 (install date) carrier confort zone 4 zone AC/
I have a 1996 (install date) carrier confort zone 4 zone AC/Heating system. I have the orginal homeowners manual but it does not tell me how to program the "options" on the zone dial. I guess what I n… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a T3QC-042K 3.5 heat pump with a E2EB-017HA furnace.
I have a T3QC-042K 3.5 heat pump with a E2EB-017HA furnace. I have noticed this winter with temps in the low 20 at night and highs only around 36 that my heat pump runs continously with the inside tem… read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
I have a carrier split zone system for ac/gas heat. I want
I have a carrier split zone system for ac/gas heat. I want to install a programmable thermostat unit to allow us to control temperature based on time of day and day of week. Most controllers I see at … read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
my 4 zone carrier will not follow the hold button and maintain
my 4 zone carrier will not follow the hold button and maintain tem i have it set at 68 it is 75 in the house now… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x