The name is Serguei. I have a York furnace. yp9c080c16mp12ca…

Customer Question
Hello. The name is*****...

Hello. The name is***** have a York furnace. yp9c080c16mp12ca I get 3 flashes error code. Cleaned the tubes, made sure they click. The 3 flashes code happen "before" the ventor motor even begins, not after. But if I disconnect the pressure sensor (a 3 wire sensor that connects with tubings between ventor motor assembly/pressure switch/pressure sensor. Then Ventor motor at least starts. changed control board as well. Same thing is happening

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

3 flashes error code. Which means pressure switch stays open. But error code comes before the ventor motor even starts. Pretty much within 2-3 seconds of beginning operation. Changed Control Board. Same problem. If I disconnect the Pressure Sensor. The Ventor Motor 'does' start, giving me a 3 flashes code after a few min of trying to make things close.

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 hours by:
3/7/2016
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,344
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Serguei .. Problem is pressure switch. Common problem on this unit. Weak diaphragm in switch. Replace switch. Russ

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

Contact Supplyhouse.com at(###) ###-#### Part is in stock there. Model and serial number ready. Russ

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I'm given an error that pressure switch fails to close, even before ventor motor starts. And you think it's the pressure switch that's failed?
Customer reply replied 2 years ago
Okey. I've ended up calling York and it's not the pressure switch's problem. One of the wires on the sensor, that 3 wire thingy is broken. You guys have been no help. Sorry.
HVAC Technician: gotoman for ac, HVAC Technician replied 2 years ago

Sometimes it better to be there but flow charts indicated bad air switch. Thanks Good Luck. Nice dealing with someone that ask the right questions. Russ

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
How do I light the pilot on my York furnace?
How do I light the pilot on my York furnace Optional Information: Model : P4HGD12N05001 Already Tried: I think the problem was caused when our main gas line was shut off briefly. I've put the knob to … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Have York furnace with White Rogers controller model 50A51-243. Light
Have York furnace with White Rogers controller model 50A51-243. Light is blinking four times . . . open high limit switch. What does this mean? What can I do?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my york furnace trouble light blinks 11 times telling me a
my york furnace trouble light blinks 11 times telling me a removed jumper or bad ground. when i turn the furnace on the blower motor runs even with all low voltage wires unhooked.… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,344 satisfied customers
I have an old York furnace, we lost power and it would not
I have an old York furnace, we lost power and it would not start back up... I checked the codes and it says “open pressure switch” I blew and sucked on the hose I hear an Audible clicking, tried again… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a York Furnace. It will run for a while and then shut
I have a York Furnace. It will run for a while and then shut off, with four red blinking lights. I check the limit switches and they didn't seem to be open. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
York furnace stopped working and showing 3 red flashes. A
york furnace stopped working and showing 3 red flashes … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a York Furnace Model TG9S060B12MP11A My heater is
I have a York Furnace Model TG9S060B12MP11AMy heater is having problems. It blows hot air for some time, and about 30 minutes or so the air gets cool, it doesn't blow hot air anymore - even if the roo… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Diamond 80 york furnace. Stuck open pressure switch. 3
Diamond 80 york furnace. Stuck open pressure switch. 3 flashing led. Right before Christam Eve...right? Clasdic. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
I have a York furnace flashing 7 times. Little fan turns on
I have a York furnace flashing 7 times. Little fan turns on but ignitor does not turn red. Over the past several weeks same thing has happened 3-4 times. I have turned off furnace several times and wa… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a York furnace. We have no heat. The fan is working
We have a York furnace. We have no heat. The fan is working but the burners will not fire. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
We have a rooftop York furnace model D1NH03N05606C. We
We have a rooftop York furnace model D1NH03N05606C. We recently had to turn the gas off to the house and now the heater is not working. We assume this is a pilot light issue but don't know where to fi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a York furnace Model #P3UCD20N09101A. The thermostat
Good morning Pearl, I have a York furnace Model #P3UCD20N09101A. The thermostat calls for heat and the ventor motor comes on and the igniter lights but I get no flame. Any ideas? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I just replaced my ignition control board S1-33103010000 in
I just replaced my ignition control board S1-33103010000 in my 20 year old York furnace due to my air handler not working. A technician came out and troubleshot this as my problem. Of course it wasn't… read more
lordofbtus
lordofbtus
pres
Vocational, Technical or Trade Scho
1 satisfied customers
York furnace wont light. Ignitor will cycle on, but no flame
York furnace won't light. Ignitor will cycle on, but no flame will light. I smelled gas at the beginning of trying to fix this, but not now. Cleaned the flame sensor... but no luck with that.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
8 year old York furnace shuts off after about 5 minutes. We
8 year old York furnace shuts off after about 5 minutes. We replaced the main filter, Repairman replaced the heat sensor and the board and it still shuts off. He checked the gas flow with a meter and … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
We have a york furnace and it blinking 4 times code says its
We have a york furnace and it blinking 4 times code says its an open high limit. what does this mean and can i fix it myself?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
we have a ctc 43154a thermostat and we had to replace the filter
we have a ctc 43154a thermostat and we had to replace the filter earlier today and the heat is not coming on now… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
5 blinking red lights on a York affinity 9.c. No heat.
5 blinking red lights on a York affinity 9.c. No heat. Thoughts, thanks.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x