Customer Question
I had a brown out...
I had a brown out that caused caused my honeywell aquastat on my slantfin boiler 100 series to not let power to circ. pump. I replaced taco pump thinking it went bad. The pump worked periodically for a minute then not at all. I then found out ot was the honeywell L8148 control box, mind you the burners were firing fine the whole time. I got a new L8148 labeled my wires removed the old box and couldnt get the bulb sensor out of the copper well housing so i took the housing out. And preceded to try to remove bulb. No dice i damaged the copper on the housing on a saturday with no supply store open. So i Drilled out copper from brass fitting flared a 3/8" i.d. x 6" length copper pipe and seated it thru brass fitting closed and soldered un flared end and soldered flared end to brass fitting. Basically made my own well. Re installed well (which is a little longer and wider than the correct one that i couldnt buy that day) packed with provided grease inserted sensor bulb from back of box, wired control box exactly as the previous one was, repressurized system and flipped the switches. Pump works as it should!! But now the burners wont fire for anything even at 90° therm setting. Everything was done just right theres 120v to L1 L2 C1 C2 but no voltage to boiler. Could it be my makeshift well housing? Are they that sensitive to not let the boiler burner kick on even on a cold system?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 56 minutes by:
3/6/2016
HVAC Technician: HvacmanSean, HVAC Technician replied 2 years ago
HvacmanSean
HvacmanSean, HVAC Technician
Category: HVAC
Satisfied Customers: 238
Experience: Owner HVAC company
Verified

Brown out please explain to see if I'm capable to help you

Ask Your Own HVAC Question
HVAC Technician: HvacmanSean, HVAC Technician replied 2 years ago

Bulb sensors are critical...... Damaging them can cause a system to not work.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
but could it cause the boiler to not heat at all? Whatsoever?
HVAC Technician: HvacmanSean, HVAC Technician replied 2 years ago

Pretty sure, is possible for you to send photo.... Just so I can make sure I know what I'm talking about

Ask Your Own HVAC Question
HVAC Technician: HvacmanSean, HVAC Technician replied 2 years ago

Wish we could help you

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 2 years ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,835
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Do you still need help? It seems my colleague has opted out. Do you have a multi-meter?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a brand new Aquastat L8148A, that will not run my
I have a brand new Aquastat L8148A, that will not run my circulating pump, no 120 across C1 and C2. the boiler fires up and the relay closes. … read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
I have a Vaillant GA92-140 boiler in my home and it will not
I have a Vaillant GA92-140 boiler in my home and it will not start up this fall. The thermostat is calling for heat but no ignition cycle is started. I tried the ignition modual reset procedure posted… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
Need help wiring a honeywell L6006 aquastat, the boiler
need help wiring a honeywell L6006 aquastat, the boiler control, circ pump, and tstat to a honeywell RA832A relay … read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
I have a Honeywell R8182D that is tripping the red safety
Customer: Hello Doug, My name is***** have a Honeywell R8182D that is tripping the red safety button. What is interesting is that it does not trip when the boiler is running. It only trips after the b… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
I am trying to troubleshoot a Honeywell Aquastat Relay Type
I am trying to troubleshoot a Honeywell Aquastat Relay Type L8148E. I have 24v at TV and T. Also have 112v at L1 and L2. When I take a reading at C1 and C2 I a 48Ω reading. My thermostat in thr house … read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
I have a boiler heating system and the Combination Limit control
I have a boiler heating system and the Combination Limit control relay needs to be replaced. The contacts get stuck at times and it shuts down and does not come on until I reset it by turning off elec… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
Is it possible to control a boiler consisting of (one burner
Is it possible to control a boiler consisting of (one burner Motor and two separately zoned circulator pumps) with two separate thermostats? Boiler has an L8148A Aquastat relay, and a standard relay t… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
I have a Honeywell aquastat relay type l8148e. I am trying
I have a Honeywell aquastat relay type l8148e. I am trying to get the circulator pump for the zone wired in properly, not the boiler circulator. Currently the outside zone circulator is wired into C1 … read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
Hi, I have a problem with no heat to my 2 heating zones.
Hi, I have a problem with no heat to my 2 heating zones. The boiler runs for the domestic hot water. I have a aquastat L8124a relay. Any suggestions?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Hey Guys, I have a utica boiler about 2 yrs old. For the
Hey Guys, I have a utica boiler about 2 yrs old. For the past few weeks the circulator pump would switch on about every 3 or 4 heating cycles and randomly in between. The times when it didnt I could f… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
I replaced my Taco 007-F5 circulation pump and Honeywell aqua
I replaced my Taco 007-F5 circulation pump and Honeywell aqua stat L8141J, last year. The circulation pump wasn't coming on. There was no voltage from the Honeywell. After 22 years I though it was abo… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
I have an oil fired boiler that is only a few years old and
I have an oil fired boiler that is only a few years old and has been cleaned and serviced. Lately it seems to be short cycling, running only a few minutes at a time (3-5 min). It used to run more like… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
I have L8148E Aquastat Relaty on a Gas boiler (hot water baseboard
I have L8148E Aquastat Relaty on a Gas boiler (hot water baseboard heat) that is just over a year old (upgraded to a new boiler). The problem is that the circulation pump is not running. I disconnecte… read more
Rick
Rick
HVAC Supervisor
24,835 satisfied customers
boiler starts for a few minutes then stops, pipes either side
boiler starts for a few minutes then stops, pipes either side of pump hot but rads not heating up, any idea why? I cannot hear the pump running.… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
I just installed a slant fin oil fired boiler and the boiler
I just installed a slant fin oil fired boiler and the boiler goes on but when the pump is wired it doesn't go on and it doesn't tell me what number to put my wires on to get the pump connected to the … read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
What would cause an oil burner to leak fuel from the housing?
What would cause an oil burner to leak fuel from the housing below the ignition transformer whenever the furnace runs? This is a new installation and works well but there is a small puddle under the h… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Burnham Independence, gas fired steam boiler, with
I have a Burnham Independence, gas fired steam boiler, with EZSQ Control. This unit has 2 zones, one steam for the upper floor, and a second hot water circulation loop, for the basement. The boiler is… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hi, ive got a wallstar boiler which cuts out every few days.
hi, ive got a wallstar boiler which cuts out every few days. It had air bubbles in the clear oil supply pipe, more than usual. I replaced the fire valve/non return valve and checked the oil supply pip… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x