Have a 395CAV048111AGJA 80% furnace that runs then shuts…

Customer Question
Have a Bryant 395CAV048111AGJA 80%...
Have a Bryant 395CAV048111AGJA 80% furnace that runs for 24hrs then shuts off. also noticed that when furnace fires off draft inducer stays running is that normal operation?heater, coil,and 30"plentum is 140 degrees and flue pipe is 215 degrees doesn't seem right to me what should i be looking for
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 15 minutes by:
3/5/2016
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the draft inducer should stay running 30 seconds before the burner comes on, and stay running as long as the burner is on.

Those temperatures you gave are normal whenever the burner is on.

Something is not right with the furnace staying ' on for 24 hours then shuts off' however. If the burner stayed on for 24 hours the furnace should be over heating the house severely.

If just the main blower stays on for 24 hours, it could be because you have the 'fan switch' on the thermostat set to 'fan ON' instead of 'Fan Auto'.

Let me know a lot more about that in great detail, remembering that there are two (2) fans in that furnace, the small inducer fan that runs whenever the burner is firing, and the much larger main blower.

We can go from there.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
the heater cycles normal for 24hrs then nothing i pulled a wire off the manual reset limit on the draft inducer and burner shuts off and main blower runs also tried it with hi limit and same i just don't know why its shutting down after working normal for a day and temps on the heater,coil,and plentum never got like this I'm assuming it kicks off on hi limit oil it cools down and by shutting the switch off when it doesn't come back on at call for heat just resets what ever fault is happening then fires normal again for 24hrs was working fine all winter til just the other day
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago

Thanks,

I will need a clear, close up, very well lit and focused photo of the wiring diagram glued to the inside of the blower compartment door in order to coach you effectively on this. Use the paper clip icon at the right end of the tool bar above to attach the photo.

I will mark the photo up with trouble shooting instructions.

If I miss you tonight, I will pick up your response in the morning.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Presidential II gas furnace. Series 1981. Furnace turns on
Coleman Presidential II gas furnace. Series 1981. Furnace turns on and runs o.k. for about 30 minutes then shuts off even though house is not up to temperature and thermostat is still on. The furnace … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My ducane furnace,inducer comes on, it lights, blower comes
my ducane furnace,inducer comes on, it lights, blower comes on. then shuts off after a few minutes. then inducer comes on after a bit but it doesn't stay on long enough to light. seems if I shut off t… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have a problem w/ my furnace. The ignition ignites, but the
I have a problem w/ my furnace. The ignition ignites, but the burners do not start. Is airheatman available?Can any havoc technician help?… read more
Rick Warner
Rick Warner
Zone Manager
Tech 1
12 satisfied customers
My WM HE II boiler starts out in the morning when I turn up
My WM HE II boiler starts out in the morning when I turn up my thermostats The boiler begins to fire and shuts down several times before running for about 10 minutes. It then shuts off and repeats the… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Good Morning. We have a normal 80% Bryant furnace, 10-11
Good Morning. We have a normal 80% Bryant furnace, 10-11 years old. The only oddity is that it vents out the side of the house from the basement, so a power ventilator is required here. The thermostat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi I have a Maytag furnace that has been acting up. Initially
Hi I have a Maytag furnace that has been acting up. Initially the pilot light would ignite and the main burner would burn, but it would not remain on long enough to blow anything other than cool air (… read more
rpen7111
rpen7111
119 satisfied customers
I have a Rheem Criterion RGDJ Upflow that is about 13 years
I have a Rheem Criterion RGDJ Upflow that is about 13 years old, an 80% unit. Late last winter I noticed a white powdery substance on the furnace exhaust vent that eventually turned into a light rust … read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a 2 1/2 year old Bradford White natural gas water heater.
I have a 2 1/2 year old Bradford White natural gas water heater. rust particles are building up on top of the heater below the flue. The flue draft has been checked and is correct. The burner was tota… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a Bryant formula 1000,model 397H older gas furnace.
I have a Bryant formula 1000,model 397H older gas furnace. Sometimes it starts the heating cycle, then suddenly shuts itself down. Other times it goes through the whole heating cycle and brings my hom… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Is there a problem with my TraneXE 80 Flue pipe which is hot?
Flue pipe on my Trane XE 80 furnace is very hot to the touch. Is this aproblem? How do I fix it? MFR… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
The burner on my furnace was going on for a short period then
The burner on my furnace was going on for a short period then off. The fan ran continually and the temp. was 80 degrees coming out of the closest vent. after about three days it was back to normal. Th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a model 58tua furnace and am receiving error code 43
I have a model 58tua furnace and am receiving error code 43 (low-heat pressure, draft safeguard, or auxiliary limit switch open while high-heat pressure switch is closed). I tried resetting the furnac… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Tempstar 75,000 btu 80% furnace getting condensation in vacum
Tempstar 75,000 btu 80% furnace getting condensation in vacum line to pressure switch creating trap. why is this happening?… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
1994 Trane XL80 2-Stage #TDD100R945B1 w/ 1-Stage Honeywell
1994 Trane XL80 2-Stage #TDD100R945B1 w/ 1-Stage Honeywell T-Stat. Runs OK on Low Stage-1. After 10-Min delay fires up to High Stage-2 for 30-seconds, then fire OFF for 30-sec. Then re-starts sequence… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
hi!!! i have a problem with a rheem furnace. 90%, 90000 btu.i
hi!!! i have a problem with a rheem furnace. 90%, 90000 btu.i just installed it and it's running ok for some tome and after that the status led is blinking once: ignition failure...i didn't run a fres… read more
Rick or Nick in Texas
Rick or Nick in Texas
General Manager-Lead Tech
Own and run HVAC business 29yrs
44 satisfied customers
I have a trane xl 90 furnace. The ignitor works, and the main
I have a trane xl 90 furnace. The ignitor works, and the main burner fires up. However it doesn't stay on very long. Yesterday when I asked this question , the tech said to clean the heat sensor with … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hi, I have a protherm 80 E boiler that will not ignite. It
Hi, I have a protherm 80 E boiler that will not ignite. It makes the normal start up noise that will last for about 30 seconds but just does not light i have checked the fan but this moves fine when s… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Trane furnace ignites but won't stay lit. Get error code 3
My Trane XL 80 ignites but won't stay lit. After the flame goes out the indicator lamp flashes 3 times indicating a pressure switch failure according to the diags listed on the control. Where is the p… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x