DynaChem has a 1967 Kewanee, 250 HP, gas-fired, fire-tube boiler with an E-type burner.We need an electrical schematic for the gas fired system. Since the Kewanee is older than 1970,Are any manuals, drawings or schematics available for this unit. The boiler name plate is as follows:The serial number : NB-23335.The Order Number: 416840AManufacturing year: 1967

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

Jim Hartman, EngineerThe boiler will not go to automatic fire from low fire. When manually put into automatic fire, the boiler operates OK. There are some changes that need to be made . The boiler tuner recommended a new 135 ohm pot and a L91A controller. The wiring is in poor condition. That is why we need the wiring schematic.

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
3/2/2016
HVAC Technician: Phil, Mechanical Engineer replied 2 years ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello Jim, I do not have a wiring diagram for that boiler, it is almost 50 years old. However very few experienced large scale boiler contractors will have any trouble at all sorting out how it operates and and what is needed in the line of wiring etc.

98% of those used off the shelf fire eye ignition and aquastat controllers (by Honeywell mostly), so far it sounds like you may have found such an experienced man judging by his recommendations so far. These boilers can be a safety hazard, especially fire tube and steam applications over 15 psig, for that reason and to keep your building owners liability insurance properly in force whomever you hire should be a licensed boiler contractor, with full liability insurance. Such boilers when rated over 15 psig steam pressure need regular pressure vessel inspections. These generate hydrogen in the water which embrittles the tubes but more dangerously the pressurized components.

If you have the full model number of the boiler you might be able to find a diagram for it at this link http://www.kewaneeparts.com/literature.html

That is a bit of a long shot, but it is not likely you will find a wiring diagram elsewhere. However as I said, those were controls were straight forward, not electronic and are generally not difficult to sort out for an experienced tech on the job site.

We can go from there if you feel I can be of any further assistance.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
How do you test the supply sensor and what i UI.39 error.
how do you test the supply sensor and what i UI.39 error … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
older tempstar furnace is short cycling. Model #NUGE075AG01/serial#
older tempstar furnace is short cycling. Model #NUGE075AG01/serial# ***** No wiring diagrams on service door to run tests. Seems like faulty flame sensor but I dont see one. How does this set up measu… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have a weil-mcclain gas boiler. Model CGM-6 Series 10.
I have a weil-mcclain gas boiler. Model CGM-6 Series 10. There are two thermostats. One upstair and one down. We use the upstairs thermostat but seldom turns on the heat since heat rises. The heating … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My furnace will sometimes kick on and run a few minutes and
My furnace will sometimes kick on and run a few minutes and shut off... it is inconsistent. It just shut off a minute ago but did not reach the temp set at Thermostat. Changed batteries in thermostat … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I AM A TECH FROM DEAD RIVER CO. AND HAVE F18 AND FO9 ERROR
I AM A TECH FROM DEAD RIVER CO. AND HAVE F18 AND FO9 ERROR CODE . ANOTHER TECH SAYS THERE IS TURBOLATOR FOR LACK OF A BETTER TERM BTWEEN GAS VALVE AND INDUCER TO CHECK.GOOD GAS PRESSURE INTAKE AND EXH… read more
V12Tech
V12Tech
252 satisfied customers
air heating boiler american standard model #:GUB-75 serial
air heating boiler american standard model #:GUB-75 serial # XXXXX Problem: fan blower auto is not working,manual is working… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
On an ecoTEC 618, Im getting F.61, described as "Gas-valve
On an ecoTEC 618, I'm getting F.61, described as "Gas-valve control defective" with a cause of "Short circuit/earth (ground) leak in cable harness to gas-valves, gas valve assembly defective (earth/gr… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
Installed a Hunter 44377 programmable thermostat for a Rudd
Installed a Hunter 44377 programmable thermostat for a Rudd heat pump. Cooling worked okay but heat does not turn on the outside unit. Wires are connect as follows: Red to R Yellow to Y,Green to G, Wh… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
Hi, Wish I could say model . plate is gone is about 25 yr old
Hi, Wish I could say model . plate is gone is about 25 yr old unit blows one side fuse on 220. It is heater and air unit rooftop, anywhere 1.5T-5T. Using heater at time fuse blows when not around. Wou… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a pair of Trane 36C03 furnaces. Neither is coming on
I have a pair of Trane 36C03 furnaces. Neither is coming on when I apply power to the white wire. I know that there is power on the wire, as hooking it up to the fan turns the fan on. Please advise. T… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
i just put a new honeywell RTH 7600 thermostat in and set it
i just put a new honeywell RTH 7600 thermostat in and set it to cool but the heat pump always comes on. folloed instructions on installation book but nothing changes it from heat. screen sys COOL -- b… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
ive got a potterton prima 50f boiler .it stopped working i
ive got a potterton prima 50f boiler .it stopped working i found fan not operating so have replaced it .but the boiler still wont fire up. the fan runs the pilot lights but the electrode continues to … read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
model 58ssb furnace inop. replaced induction motor (im) one
model 58ssb furnace inop. replaced induction motor (im) one month ago , run fine. Now inop again. removed wires from im and connected 127v. motor runs and furnace fires. replaced im board. installed i… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
HI I have a Baxi 35/80 Wall mounted gas water bioler. Lately
HI I have a Baxi 35/80 Wall mounted gas water bioler. Lately When the timer sends a singal to start the boiler 'CH or HW' it starts the circulating Pump as normal as you can hear and feel it running w… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
My Burnham Boiler won't fire. The pump is circulating
My Burnham Boiler will not fire. The pump is circulating and the pilot is lit but the the ignition isn't happening. Is there anything to try? Optional Information: Make : Burnham Model : P-206-W Alrea… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am installing a Heatmor wood fired boiler in my home. The
I am installing a Heatmor wood fired boiler in my home. The heat exchanger will be installed in an older Ruud gas fired hot air furnace, immediately above the A-coil. Is there a simple way to have the… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an older Burnham gas furnace that heats water that is
I have an older Burnham gas furnace that heats water that is circulated thru three zones. There are three thermostats and 3 Comfort-Trol zone valves. A Vizlogic board has LEDs to indicate status. The … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an American Standard Empire 4-GA-E gas fired boiler.
I have an American Standard Empire 4-GA-E gas fired boiler. Can't get the burners to fire. I tried to manually actuate the Detroit Lubricator V-574 to no avail. Is there a way to test this valve or th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x