Replacing a weathertron bay28x139 or bay28x141 with a

Customer Question
white-rodgers 1F86-244. after matching all...
replacing a weathertron bay28x139 or bay28x141 with a white-rodgers 1F86-244. after matching all colors from the old weathertron to the new white-rodgers I have two extra wires. (black that it was connected to x2) and (brown that it was connected to T) system isn't working, not sure if this thermostat is compatible or if those two wires need to be connected. or if the whole wiring is wrong. I pull up the instructions for the new thermostat and is very confusing.
JA: I'll do all I can to help. Is there anything else important you think the HVAC Technician should know?
Customer: system was working with the old thermostat but not with the new one
JA: OK. Got it. I'm sending you to a secure page on JustAnswer so you can place the $5 fully-refundable deposit now. While you're filling out that form, I'll tell the HVAC Technician about your situation and then connect you two.
Submitted: 1 year ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 45 minutes by:
2/29/2016
HVAC Technician: airheatman, HVAC Technician replied 1 year ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,805
Experience: Furnace, A/C and heat pump specialist.
Verified

Tell me what color wires went to what terminals on old and where you put them on new.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 1 year ago

If you connected the blue wire from B on old to B on new, you most likely blew a small fuse in the air handler .That B will have to go to C on new.Let me know and we will go from here.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 1 year ago

Give me a few moments to look over

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 1 year ago

OK after looking over the manual on the new thermostat I see that it is not designed to work with your heat pump with backup heat .It will work with the heat pump, but you will not have the electric backup strips if you choose to use this thermostat.It is considered a single stage heat/single stage cool thermostat.You need a 2 stage heat/1 stage cool thermostat.

If you chose to use this thermostat and sacrifice the backup heat ,

You will wire as follows:

Red to RC with jumper to RH (24v power)

Orange to O (Reversing valve)

Green to G (Fan)

Yellow to Y (AC contactor)

All others taped off. Let me know and we will go from here.

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Rick. 1 day. I have a taco sr506 switching board, all my
1 day. I have a taco sr506 switching board, all my thermostats ar on, but there is no red lights on the board … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a rheem classic 90 plus that has no heat, no fan
I have a rheem classic 90 plus that has no heat, no fan blowing for heat or air. The diagnostic leds are as follows flame=not lit, the next one=constant green, the next one=constant green. I have chan… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an AO boiler with a triple aquastat,I have a three
I have an AO smith boiler with a triple aquastat,I have a three zone system and need know the correct way to connect the end switch to the system thx GA … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am installing 22 Venstar T1700 to control my 2 Zone
I am installing 22 Venstar T1700 to control my 2 Zone hydronic system. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have to reset my furnace every couple days to get it to
I have to reset my furnace every couple days to get it to come on. The led light doesn't flash any error code. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Is the york diamond 80 compatible with a Honeywell Lyric T5
Is the york diamond 80 compatible with a Honeywell Lyric T5 wi fi thermostat? … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Thermostat question: I replaced the thermostat myself. I
thermostat question: I replaced the thermostat myself. I turned the furnace off and connected the wires myself. I can't remember exactly but one of the wires was originally connected to the wrong colo… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Trying to rewire a thermostat rth6350. What happened is a
what happened is a friend of mine disconnected the wires and doesn't remember where the wires go … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a question about my furnace. New filters recently. I
I replaced themotherboard about 3 weeks ago and disconnected the humidifier… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I came home from a 3 day trip to find that my heat is not
I came home from a 3 day trip to find that my heat is not working. I believe the problem to be the thermostat partly because it is at least 12 years old. It is a HUNTER 44100 programmable heat/cool th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have a 1f58-58 bought a1f58-72 do they wire the same? Now
have a 1f58-58 bought a1f58-72 do they wire the same? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Rick, The thermostat terminals on the ZVC404 Zone Valve
Hi Rick,The thermostat terminals on the ZVC404 Zone Valve Control are marked as 24 VAC. Does this mean that when the terminals on the thermostat are closed, the circuit is completed and energized with… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an TACO SR502 that controls 2 pumps one for zone1 for
Hello, I have an TACO SR502 that controls 2 pumps one for zone1 for Hot water loop and the other for zone2 for baseboard heat and I also have a new TACO ZVC406 that control one other pump that supply … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My Taco SR 504 switching relay is powered up ( light is on),
My Taco SR 504 switching relay is powered up (green light is on), but none of the zones are working (red lights off). The thermostats upstairs are all brand new and working, and the digital valves see… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I had a taco sr504 that one zone was not working. I switched
I had a taco sr504 that one zone was not working. I switched thermostats from other zones , jumped out that zone, switched contactor relays etc. I called taco and they said it was probably a bad board… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My honeywell thermostat dose not have a rh inlet only an r.
my honeywell thermostat dose not have a rh inlet only an r … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How to wire up wilo wzc universal zone control two zone to
how to wire up wilo wzc universal zone control two zone to boiler … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Replaced old ignition control -Rodgers Model 50A50-405,
Replaced old ignition control White-Rodgers Model 50A50-405, D340035P01, CNT1309 with 50A50-405.Now I have 5 flash,then pause which represents open rollout switch. Checked rollout Switch and it is not… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x