Replacing a weathertron bay28x139 or bay28x141 with a

Customer Question
Replacing a weathertron bay28x139...

Replacing a weathertron bay28x139 or bay28x141 with a white-rodgers 1F86-244. after matching all colors from the old weathertron to the new white-rodgers I have two extra wires. (black that it was connected to x2) and (brown that it was connected to T) system isn't working, not sure if this thermostat is compatible or if those two wires need to be connected. or if the whole wiring is wrong. I pull up the instructions for the new thermostat and is very confusing.

Contractor's Assistant: I'll do all I can to help. Is there anything else important you think the HVAC Technician should know?

System was working with the old thermostat but not with the new one

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 45 minutes by:
2/29/2016
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,024
Experience: Furnace, A/C and heat pump specialist.
Verified

Tell me what color wires went to what terminals on old and where you put them on new.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

If you connected the blue wire from B on old to B on new, you most likely blew a small fuse in the air handler .That B will have to go to C on new.Let me know and we will go from here.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Give me a few moments to look over

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

OK after looking over the manual on the new thermostat I see that it is not designed to work with your heat pump with backup heat .It will work with the heat pump, but you will not have the electric backup strips if you choose to use this thermostat.It is considered a single stage heat/single stage cool thermostat.You need a 2 stage heat/1 stage cool thermostat.

If you chose to use this thermostat and sacrifice the backup heat ,

You will wire as follows:

Red to RC with jumper to RH (24v power)

Orange to O (Reversing valve)

Green to G (Fan)

Yellow to Y (AC contactor)

All others taped off. Let me know and we will go from here.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Nordyne Furnace Model GL1RA 090C-16B with a serial
I have a Nordyne Furnace Model GL1RA 090C-16B with a serial # XXXXX GLA020805917. I have a problem with the furnace as it is blowing only cold air. I have cleaned the heat sensor, and replaced the air… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem heat pump with electric auxillary heat and a
I have a Rheem heat pump with electric auxillary heat and a Honeywell RTH7500 thermostat. The aux heat does not activate when in the system is set to HEAT although the display indicates the aux heat i… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I am working on a Lennoxgas furnace model # G1603/4-100-1,
I am working on a Lennoxgas furnace model # XXXXX SERIAL # XXXXX Heater burners ignite, main blower comes on, unit heats for about one minute then gas valve loses power, flames go out and five seconds… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
I have a Honeywell HZ322 and zone 1 is blinking yellow on
I have a Honeywell HZ322 and zone 1 is blinking yellow on the controller board and is sending no power to the thermostat … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Our HVAC is behaving strangely. It's a split system with the
Our HVAC is behaving strangely. It's a split system with the compressor outside and the evaporator and air handler inside. When our AC cycle begins, everything is fine. But when it ends, the air handl… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
My thermostat has no power and I have no heat, gas, steam
My thermostat has no power and I have no heat, gas, steam Utica boiler 24v . … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a large hot water heat system with 8 zones using
I have a large hot water heat system with 8 zones using wired thermostats all connected to 2 Caleffi ZVR104 relay panels. Each wired thermostat is connected via 2 wires (R and W) on the ZVR's thermost… read more
hvacdave84
hvacdave84
53 satisfied customers
My son removed his old mercury thermostat without taking a
My son removed his old mercury thermostat without taking a picture of the wiring. He is trying to replace his old thermostat for a new digital one. What can we do to determine what each colored wire r… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a new job where I have to replace the outside
I have a new job where I have to replace the outside condenser which is located on the roof. As you can imagine, there are multiples of condensers on the roof. What is the best way to be absolutely ce… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have an innovator series mod g32q3 that when heat is
I have an innovator series mod g32q3 that when heat is called for the exhaust fan starts, you hear a click, then it stops. it has the right light flashing slow (pressure switch open or open rollout sw… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am installing zone valves and can find no wiring diagram
I am installing zone valves and can find no wiring diagram for my very old Aquastat relay type L8048a … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Rick, The thermostat terminals on the ZVC404 Zone Valve
Hi Rick,The thermostat terminals on the ZVC404 Zone Valve Control are marked as 24 VAC. Does this mean that when the terminals on the thermostat are closed, the circuit is completed and energized with… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Rheem Criterion II gas furnace and when we moved
I have a Rheem Criterion II gas furnace and when we moved in the furnace did work via the t'stat. Well I bought a new t'stat and hooked up the wire per the labels on the curcit board, B,G,W,Y,O etc. t… read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
I have a Totaline P374-0300 thermostat the wiring is W,O,G,R,C,Y
I have a Totaline P374-0300 thermostat the wiring is W,O,G,R,C,Y I need to know which wire color goes w/ which letter I have a White, Green, Red, Yellow, Blue and Brown wire.… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Getting code alternating fast flash on both lights ,
Customer: I'm Art - getting code alternating fast flash on both lights … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an old Goodman gas furnace. The induced draft relay
I have an old Goodman gas furnace. The induced draft relay is clicking in and out every few seconds. Of course the draft blower shuts off as soon as this happens then cuts on then off. Etc. Every once… read more
airheatman
airheatman
HVAC Technician
9,024 satisfied customers
My Bryant 383kav furnace wont heat. It is not trying to light,
My Bryant 383kav furnace won't heat. It is not trying to light, it does nothing. The blower works if set to on, there are no codes flashing on the control module, a component test shows everything fun… read more
caleb
caleb
63 satisfied customers
Good Morning, I have a honeywell TH8320U1008 thermostat on
Good Morning, I have a honeywell TH8320U1008 thermostat on a brand new seer 16 heatpump with a three stage electric furnace for aux heat. I would like to absolutely minimize the use of the aux heat. I… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x