Why is the heat pump PH13NR024-F not coming on?

Customer Question
Why is the heat pump...

Why is the heat pump PH13NR024-F not coming on? I have a split unit with and installed 2 new RTH6500 Honeywell thermostats. Have been heating the home with no issues until we had a warm day and I switched to AC and the outdoor unit would not come on. I discovered the outdoor unit was not coming on for heat either.

I am not sure if this was happening before the new thermostat or not because it was winter and I didn't notice if it was Aux heat or not. The other unit is working fine inside and out. I know that it is hooked up correctly and the settings are correct. Last year I replaced the board in the outside unit (HK32EA001) and a capacitor. I tried to jump by connecting the O wire with R, G and Y and the fan in the Air Handler came on but not outside unit. I have 24 V in the outdoor unit (while running heat) on the Y, R, W and no voltage on the O and C wire. Checked the fuses and breaker. What can I/should I do next?

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
2/26/2016
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,643
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello and thanks for using this service,

Did you check the fuse on the board in the airhandler?

There should be a 3 amp fuse on the board itself, let me know

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I did and it is good
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Ok is the LED light on the board? Also on the outside unit is the board powered?

Ask Your Own HVAC Question
Customer reply replied 2 years ago

There aren't any LED lights.

HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Can you check for power to the board on it? or press the contactor button and see if the unit fires up manually?

Ask Your Own HVAC Question
Customer reply replied 2 years ago

Outside or in the air handler? I don't think there is a button. The air handler works and there is power on the board in the air handler.

I tried to jump by connecting the O wire with R, G and Y and the fan in the Air Handler came on but not outside unit.

HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

You dd not connect them all together did you?

Only R to Y

R to G

R to W

Ask Your Own HVAC Question
Customer reply replied 2 years ago

Do I just touch them or connect them?

HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Touch them together R to G should run the air handler. R to W should start the unit for heat, it sounds like an outside board issue though on the unit.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I replaced the board in the outside unit (HK32EA001). The outside unit does not cut on when I put these together.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

OK can you check the thermostat wiring then to the outside unit it could have a break in it.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I have 24 V in the outdoor unit (while running heat) on the Y, R, W and no voltage on the O and C wire.
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Do the wires get spliced anywhere?

Ask Your Own HVAC Question
Customer reply replied 2 years ago

Only splice is down from the thermostat to the out door unit and to the air handler. No other splices. This is all in the air handler.

HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Yes but you have somelow voltage thermostat wires that go to the outside unit as well I am saying they may be broken. Now secondly have you checked the outside unit for any tripped limits that may have tripped and need to be reset as well?

Ask Your Own HVAC Question
Customer reply replied 2 years ago

I checked the wires coming from the Air Handler to the outdoor unit, in the outdoor unit. I had 24 V on the Y, R, W wires and no voltage on the O and C wire.

There are no reset buttons or switches that I found. Is there something specific I need to look for? The heat was running when I checked the voltage.

HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Can you upload a picture of the wiring diagram here?

Ask Your Own HVAC Question
Customer reply replied 2 years ago

From outside, thermostat or air handler?

Here they are from manual and picture

Attachment: IMG_6691[1].JPG

Attachment: IMG_6690[1].JPG

Attachment: IMG_6689[1].JPG

Attachment: IMG_6688[1].JPG

HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

It shows 2 over temp limit switches have you checked them at the outside unit?

Ask Your Own HVAC Question
Customer reply replied 2 years ago

Do I check to see if they have voltage? What do I check on them? Can you give me some guidance on what they are, this is where I am unfamiliar.

I dont see any limit switches on the outdoor unit.

Here is the wiring diagram for it: Attachment: Outside Heat Pump Wiring.jpg

HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Yes there are several safety devices on yours that can cause this issue...Low Pressure Switch, High Pressure Switch and Discharge Temp Switch

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Are you waiting on me? I was hoping you could tell me what to check or do
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,080
Experience: Furnace, A/C and heat pump specialist.
Verified

Hello my name is ***** ***** a different expert. Sorry for all the run around. Lets start fresh.

Our first step is to turn thermostat to heat or cool and then go to outdoor unit. Locate the control wires from thermostat and check for 24 volts between the Y and C wires. (One lead on Y and one lead on C) where they come into the outdoor unit. We will go from here.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,080
9,080 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Trying to wire a rth7560E thermostat but didn't take a
Trying to wire a rth7560E thermostat but didn't take a picture of old wiring. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I am trying to locate the evaporator coil on my ac unit and
I am trying to locate the evaporator coil on my ac unit and I'm reading I should not open the box around the unit unless the breaker for the ac is off, but there isn't a breaker labeled ac on the brea… read more
airheatman
airheatman
HVAC Technician
9,080 satisfied customers
I turned my AC on to cool and I got a message saying System
I turned my AC on to cool and I got a message saying System Wait. The AC doesn't turn on. … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,262 satisfied customers
This is somewhat of a random question but I use window air
This is somewhat of a random question but I use window air conditioners in my home and I've always wondered why none of them have a feature to just pull outside air into the home? It's been raining a … read more
airheatman
airheatman
HVAC Technician
9,080 satisfied customers
What is the flashing red light at the bottom of my lennox
what is the flashing red light at the bottom of my lennox gas furnace? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
We are on a slab and we have a bad musty, moldy smelly every
we are on a slab and we have a bad musty, moldy smelly every time we try to use our ac. what can we do? … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,262 satisfied customers
I'm getting a new furnace. The old metal duct work is being
Hello, I'm getting a new furnace. The old metal duct work is being replaced with 6 inch black Insulated flexible duct material. It's rated R6. Does this meet standard code. The old metal duct work was… read more
airheatman
airheatman
HVAC Technician
9,080 satisfied customers
I have a GE dehumidifier Which was purchased in May of 2015.
I have a GE dehumidifier Which was purchased in May of 2015. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Hot water Gas fueled boiler and just wanted to
I have a Hot water Gas fueled Smith boiler and just wanted to change the Honeywell aquastat, the installation seems straight forward, however the one I bought the temperature limit can only go to 150,… read more
Rick
Rick
Supervisor
24,042 satisfied customers
I have "A LOT" of condensation on my ductwork (crawl space).
I have "A LOT" of condensation on my ductwork (crawl space). I live in Alabama, proper ventilation from outside (crawlspace is approximately 2600 Sq with 14 cinder block vents) 6 mil vapor barrier, me… read more
airheatman
airheatman
HVAC Technician
9,080 satisfied customers
The thermostat is missing one pin the cord one does this
The thermostat is missing one pin the white cord one does this effect my air cooling conditioner. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
The outside ac line has had the insulation deteriorated over
the outside ac line has had the insulation deteriorated over time, and now there is condensation on the line as the ac is working. The line is cold to the touch. Is the condensation just a result of i… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Connecting a NEST thermostat to a Ruud UGDG-1NAMER model
Connecting a NEST thermostat to a Ruud UGDG-1NAMER model heater. Wanting to confirm wiring on heater for thermostat is W-Heat R-Power G-Fan C- common wire … read more
Rick
Rick
Supervisor
24,042 satisfied customers
I purchased LG air-conditioner mode l417 ESRSM - 14000 BTUS.
I purchased LG air-conditioner mode l417 ESRSM - 14000 BTUS. It is installed and has never been used. It still requires lower water tap connection to a shallow container. I live in the apartment build… read more
David Bowden
David Bowden
Owner
999 satisfied customers
Need to know how to check a condensate drain - appears to be
need to know how to check a condensate drain - appears to be clogged … read more
Rick
Rick
Supervisor
24,042 satisfied customers
Tried to change to another brand of thermostat, could not
tried to change to another brand of thermostat, could not get new one to work so I tried to put nest back on and it gives me warning that no power . I have checked and rechecked and looks good,...any … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Why does my Lopi 564 blow out & restart during the course of
Why does my Lopi 564 blow out & restart during the course of a night. Especially so when on for say 2 hours & more. … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
67 satisfied customers
Phil, I'm having problems with my air conditioner. I bought
Hi Phil,I'm having problems with my air conditioner. I bought a Frigidaire 15,100 BTU 115W Window mounted air conditioner from Sears online. Since it's sold through Sears by a 3rd party seller Sears w… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x