I have a Rheem model RCBA manufactured in 2003. The fan

Customer Question
I have a Rheem...

I have a Rheem model RCBA manufactured in 2003. The fan blows however the inducer fan does not kick on. when the furnace is resent the Modulating Control Board goes from 8 to 2 to blinking 4. Once on 4 it continuously blinks four two times.

Contractor's Assistant: I'll do all I can to help. Are you ready to speak with the HVAC Technician now?

Yes

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
2/25/2016
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago
Kcrand36
Kcrand36, HVAC Mechanic
Category: HVAC
Satisfied Customers: 80
Experience: Owner at Advantage Repair
Verified

good morning, I am Kevin, on one of the Tech's here on JA.

I understand you are having a problem with your Furnace?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
can you help me?
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

I am going to try my best. I am looking up your furnace right now, if you could though, grab the entire model number which you can locate on the nameplate label in the burner compartment.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
3765gg17xiinducer blower part number: 70-24206-01-04
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

the furnace is a RCBA 3765gg17xi?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I do not have volt meter. I am hoping you can tell me what the blinking 4 means.
I have been working online on this for nearly 3 hours this morning trying to find the answer.
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

that is exactly what I was looking for, did you pull off the cover of the blower panel just below the burner panel?

Sometimes they include a "legend" to the failure.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
it only addresses number of blinks. It does not reference numerical readings.
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

I think you may be reading the cased coil number instead of the furnace number....... RCBA refers to a coil.......

Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok, I am not sure where to get the model number at.
However I just figured out how to read the 4 blink 4 it is 44 and 82
44 is "Contacts closed - inducer off"
82 is "Supply air sensor - out of range"
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

I think we can ignore the 82, I'm assuming that is 8 meaning "lockout" for flame failure. To determine if you have a defective inducer, you will need a volt meter to test the voltage being supplied to the inducer during a call for heat. If you do not have power there, then most likely the board is defective and not sending the power to the inducer.

Ask Your Own HVAC Question
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

you can purchase an inexpensive meter at a Home Depot or Lowes, some hardware stores even have them.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Where do I find my furnace model number.
Customer reply replied 2 years ago
I am guessing based on my research I should see 24volts?
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

to your inducer motor, you should have most likely 120V.... your HSI if like a glow coil should also be 120V, your other control circuit through limits and pressure switches most likely 24V.

That model number should be on a name plate sticker, it is usually located in the burner compartment, should list voltage, Input btu's, ect....

Ask Your Own HVAC Question
Customer reply replied 2 years ago
thanks, ***** ***** Lowes now in the snow storm for voltage meter and a space heater.
Your assistance is much appreciated.
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

I will be here for a little while, if you can find that model number, I may be able to pull up a wiring diagram.

Ask Your Own HVAC Question
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

I did find a schematic for two different type of controls, and also a trouble shooting guide. when you get that volt meter, you may need to check pressure switch for continuity as well.......

Ask Your Own HVAC Question
HVAC Technician: Kcrand36, HVAC Mechanic replied 2 years ago

I will be back in 30 min......

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I am at a loss as how to use this meter.
I still can't find any plate with Model number.
Customer reply replied 2 years ago
Do I have to take wires apart to measure the volts?
Customer reply replied 2 years ago
Ok, I took the connection apart and stuck the prob ends into the connector (white black and red ready snap to the blower) I get .78 volts on the red and black leads.Also I should share that my zone controller is a Honeywell universal mini zone. The purge light has always flashed, I have no idea why?
Customer reply replied 2 years ago
Photos
Customer reply replied 2 years ago
Are you still able to help me?
Customer reply replied 2 years ago
Kevin, are you there, I am without heat.
Customer reply replied 2 years ago
I was able to figure it out, heat is running again.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,365
Experience: Furnace, A/C and heat pump specialist.
Verified

Your expert had left.If you still need help let me know .Otherwise you should have a drop down menu on your page to request a refund of your deposit so you are not billed.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Rheem gas furnace that is showing a 4-blink "OK"
Hello!I have a Rheem gas furnace that is showing a 4-blink "OK" light on the control board. Model is RGRA-12ERAJS (Classic 90 Plus AFUE High Efficiency Upflow 120K BTU Gas Furnace) … read more
airheatman
airheatman
HVAC Technician
9,365 satisfied customers
2003 Rheem 90 Plus classic. Power and gas good. Unit powered
2003 Rheem 90 Plus classic. Power and gas good. Unit powered up, Tstat sending signal to unit. But it doe snot turn on blower or ignite burner. Two green LED indicators. One solid, second one flashing… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a Rheem Model RCBA-2457GG14XI gas furnace which is going
I have a Rheem Model RCBA-2457GG14XI gas furnace which is going into soft lockout. I have changed filters, cleaned out hoses, and still have the problem. Any other suggestions as to troubleshooting th… read more
airheatman
airheatman
HVAC Technician
9,365 satisfied customers
I have a luxaire gm9s100c16up11k the induced fan turns on but
I have a luxaire gm9s100c16up11k the induced fan turns on but the burner or the main blower do not start.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman GMT090-4A furnace that will not fire up. I
I have a Goodman GMT090-4A furnace that will not fire up. I see 3 blinking lights on main board. I checked ignitor ok at 80 ohms but thought to replace so did that. Unit is eleven years old replaced f… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My name is Kevin. I spoke with Tim H. and he helped me earlier
My name is Kevin. I spoke with Tim H. and he helped me earlier this year to diagnose some trouble with my Rheem Heat/AC unit. We replaced the blower motor and fixed the problem. Now wouldn't you know … read more
type2technician
type2technician
253 satisfied customers
amana air command high efficiency 95 IIQ GUAVA gas furnace
My amana air command high efficiency 95 IIQ GUAVA gas furnace variable speed blower won't advance to high stage. I've replaced the integrated control module.… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
hi, I have a goodman gmpe 100 furnace. It will sometimes come
hi, I have a goodman gmpe 100 furnace. It will sometimes come on and the gas will also come on. If it does, then within a minute, it will shut off. Also, sometimes there will only be a clicking noise.… read more
airheatman
airheatman
HVAC Technician
9,365 satisfied customers
I have a Gibson, GL1RA, forced air furnace. It is about 7
I have a Gibson, GL1RA, forced air furnace. It is about 7 to 8 years old. For the last year, I had intermittent problem when it would not light up. When I turned off the power fully and turned on, it … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My 10 year old Heil furnace (HEIL QuietComfort, Deluxe Two-Stage
My 10 year old Heil furnace (HEIL QuietComfort, Deluxe Two-Stage Gas furnace 80%) will not ignite. The blinking light suggests that 'Low pressure switch stuck closed' based on 2 flashes. So after look… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
I Have Rheeme Criterion II Model RCBA-4882AS24. The burners
I Have Rheeme Criterion II Model RCBA-4882AS24. The burners won't light. It sounds like it is going through the motions, but the elctric pilot light does not come on? What can I do?… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
Hello, I was away this weekend and came back to find that
Hello, I was away this weekend and came back to find that our furnace was not working. Model 072C-12A. The problem is that it does not ignite. Gas flow does not start. The igniter appears to work as I… read more
airheatman
airheatman
HVAC Technician
9,365 satisfied customers
Hi There! Im hoping you can help me w/ an issue that has
My Heil furnace (model NUG5125BKB1)won't kick on to start blowing warm air even though the thermostat is set to several degrees above the ambient temperature. If I set the thermostat Fan setting to On… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Rheem RGDG-10EBRJR It is not working properly 1.
I have a Rheem RGDG-10EBRJR It is not working properly: 1. CALL FOR HEAT 2. THE SMALL EXHAUST FAN TURNS ON 3. NORMALLY THIS WILL RUN FOR 30 SECONDS AND THEN TRIAL FOR IGNITION BUT INSTEAD AFTER 4-5 SE… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Turned the heat on the first time today and it wont run. The
Turned the heat on the first time today and it won't run. The fan works when set to on. Model is lennox c33-43c-2f-3. Troubleshooting lights are red - off and green blinking.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Rheem Furnace Model - FGPJ-10EBRJR Serial - EB5D307F199900304 I
I have a Rheem Furnace: Model - FGPJ-10EBRJR Serial - EB5D307F199900304 I have replaced the igniter, flame sensor, and the IFC board. Furnace will still not heat. Induced draft blower motor starts, 5 … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
We are looking for the status codes for the control board for
We are looking for the status codes for the control board for a Rheem model RGBG12 EARJR. Do you have them. We are in the process of replacing the board.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an Amana Air Command gas heating system with a White-Rogers
I have an Amana Air Command gas heating system with a White-Rogers controller. Some time during the night last night the burner stopped igniting (I live in northern Indiana. It's -4 outside.). Now it … read more
Accurate Appliance Service
Accurate Appliance Service
Business Owner
Vocational, Technical or Trade Scho
114 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x