I am working on a york air cooled screw chiller. Both

Customer Question
circuits trip on overcurrent when...
I am working on a york air cooled screw chiller. Both circuits trip on overcurrent when starting shortly after attempting to start up. I replaced the contactors about a year ago because they were heavily damaged from arcing. I've checked the new ones for damage and there is already considerable arcing which I cleaned with a file and emery cloth.
What else would cause both compressors to trip on the same fault?
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
2/24/2016
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi I'm Brian and I'm here to help!

I believe if you look closely at the wiring diagram that the mechanical high pressure switches (not pressure transducers) are in series with the motor overload circuit. I would check for problems with the condenser fans or condenser coils. I'll see if I can find my manual for these models and try to confirm my suspicion but I've experienced this same issue on a few York chillers and it wasn't the motor or motor control at all, it was the high pressure cut out peanut relays.

-Brian

Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago

Click Here for a copy of the York IOM manual for the chiller in question. In detail A on page 76 you can see what I was talking about with the high pressure switch being in series with the motor overload circuit M1-M2. Check the condenser fan starters or contactors, check the condenser fans themselves and check the condenser coils for fouling. I believe you will find your problem there.

Let me know if you have further questions on this subject. Otherwise, please remember to rate before leaving (3 stars or higher please!). Bonuses are always appreciated! Thanks for allowing me to help and thanks for using Just Answer!

Thank you,
Brian

Ask Your Own HVAC Question
Customer reply replied 2 years ago
I see where you are going with that, and I had the same thought. However, the compressors only run for about 30 seconds before shutting down. While watching the display on the controller, It seems like they are starting under load. The inrush current doesn't go down quick enough before the controller shuts them down on overcurrent. It was cool outside when I was troubleshooting like 45 degrees. The water in the evaporator wasn't overly warm, maybe 75 degrees. I can't see why the compressors aren't getting up to speed so the running current falls within the tolerable range. They are at around 110% of full load.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 2 years ago

That sounds pretty odd indeed. Can you give me the FULL model number of the unit please? Do you know if the unit is Xline start or Wye-Delta start? If it's Wye-Delta, are the starters transitioning properly? I would also check the load/unload solenoids. You can dry run them with jumpers. I've not got a whole lot of experience on the smaller York semi-hermetic screw compressors but at 30 seconds after start, they should just be starting to load so that is rather odd unless the unload solenoid isn't working or the slide valve isn't operating. Are you saying both compressors are doing the exact same thing? That in itself doesn't lend itself to a solenoid or slide valve issue. If both compressors are behaving the same way, I would look for some kind of electric commonality. I would test run everything that can be with jumpers at the control output relays (with the exception of the compressors) to see that everything operates properly from the control panel. Have you double checked voltage, amp draw and system pressures to make sure they jibe with the control panel readings? If you can get me the model number info and answer as many questions I've asked above, I may be able to get a clearer picture of things. As I'm sure you can imagine, it's tough to troubleshoot a chiller this complicated remotely but I'll do my best!

-Brian

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
1,024 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a semi hermetic compressor and on a call for call the
Have a semi hermetic compressor and on a call for call the Comp starts to hum won't start … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Mate, i have a chiller mod# 30RA-140-B0884-PEE. ERROR CODE
Yes.. only flow switch however that's rectified. Not sure how old it's in a cinema complex … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Trane CGAD chiller, getting A 70 restart inhibit. Could this
Trane CGAD chiller, getting A 70 restart inhibit. Could this be to low freon levels or is it an electrical issue?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I am a Hvac mechanic having a problem with a carrier 650ton
Good morning.I am a Hvac mechanic having a problem with a carrier 650ton credit.it will start run for about 4 minutes and trips on excessive comp surge.we have flow meters on both chw and cw lines and… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a trane xr13. I replaced the start capacitor, run
i have a trane xr13. I replaced the start capacitor, run capicitor, contactor, fan motor capicitor, and the potential start relay. System will not turn on the condensor. The condesation pan is clear. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have tried this site several times and getting the right
I have tried this site several times and getting the right tech to respond has been problematic. Maybe this time will be different. Please respond only if you have experience in completing this task. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
When installing a T05 hard start kit on a unit that has both
When installing a T05 hard start kit on a unit that has both a run capacitor and a start capacitor w/ a capacitor switching relay, does the start capacitor and capacitor switching relay need to be rem… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a Goodman heat pump about 10 years old. when I turned
i have a Goodman heat pump about 10 years old. when I turned on the heat after it had run for 5 minutes or more I heard what sounded like an electrical short. I removed the cover and saw that both con… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Water cooled chiller CVHF 1060 no startFault code [04] loss
Water cooled chiller CVHF 1060 no start Fault code [04] loss COM with Circuit. do you have a trobleshouting to follow, thanks… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
i have a 2 compressors 30 ton chiller CGWD30 and the 1st stage
i have a 2 compressors 30 ton chiller CGWD30 and the 1st stage compressor is shorted to ground, i disconnect the compressor from contactor and i tried to run the chiller with the 2nd compressor but at… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I HAVE A YORK HOME AC UNIT AND LATELY THE BREAKER HAS BEEN
I HAVE A YORK HOME AC UNIT AND LATELY THE BREAKER HAS BEEN TRIPPING AFTER THE UNIT STAY ON A WHILE. WHEN THIS HAPPENS I USUALLY HAVE TO GO OUTSIDE AND REMOVE THE RELAY PLUG AND PLUG IT BACK IN THEN TH… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a York Ciller Model# XXXXX Compressor has been
I have a York Ciller Model# XXXXX Compressor has been replaced with a copland. I am having a problem with it tripping on high discharge temp, This Sefety is no longer in place with the copland. What c… read more
N4IEA
N4IEA
Customer Service
Associate Degree
227 satisfied customers
I have a Split type room air conditioner Model No C12AWR NEO
I have a Split type room air conditioner Model No C12AWR NEO installed about 18 months ago. The problem is it starts up OK and reaches operating temperature for about 20 minutes or so then stops, with… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Ive an alarm in my chiller panel model 30XA1202 which states
I've an alarm in my chiller panel model Carrier 30XA1202 which states (electrical box interlock or electrical thermostat failure), and as a result the chiller does not start. please advise the necessa… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
york chiller oil temp reading 180 deg.f . found refrig. valve
york chiller oil temp reading 180 deg.f . found refrig. valve closed off of cooler going into evap is this normal? opened king valve and temp dropped to 120.f don;t know why this was closed?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a york ac unit. The fan and compressor outside is not
I have a york ac unit. The fan and compressor outside is not working. It started with the fan not turning and the compressor appearded to be hot and steaming. I poured water on it and it began to work… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Ive got a 6 year old trane xl13i heat pump, used with a backup
I've got a 6 year old trane xl13i heat pump, used with a backup resistance heater (winter time use). The system was turning for cooling yesterday and my circuit breaker trips when the system comes on.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Chiller # XXXXX 30HXA086RZ3561KA Remote Air-Cooled Condenser
Chiller # XXXXX 30HXA086RZ3561KA Remote Air-Cooled Condenser # XXXXX 09DK-084---501 Chiller # XXXXX 30HXA086RZE561KA Remote Air-Cooled Condenser # XXXXX 09DK-084---501 When these were started up, the … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x