Gabrielson--I have an Optima-30 gas insert. I cleaned the intake area & now the blower stopped. With the switch on, it makes a busing noise.

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

AS stated, all I did was vacuum the dust from the lower area, Now the blower will not run & the switch just makes a humming noise

Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
2/22/2016
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,748
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello and thanks for using this service, if you have been waiting do not worry or get upset I am just one of the techs on here and I try to get to as many customers as I can and I just picked up your question now.

Can you see what is buzzing?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
The buzzing is only when I turn the fan on, now.-- Prior to cleaning, all worked well-the fan was blowing just fine as I was just removing the dust build up.I always have the fan on & when it gets hot enough, the fan would automatic start, etc! Now, when I turn the fan on or it gets hot enough, the fan switch is buzzing & the fan will not start blowing out the heat!
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Hello and thanks for using this service, if you have been waiting do not worry or get upset I am just one of the techs on here and I try to get to as many customers as I can and I just picked up your question now.

It sounds like the fan is stalled or seized can you check it to see if it is turning?

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Not without tearing the entire unit apart. Where can I find a manual or I will just cancel this site by calling my Credit Card ! The fan is under the logs and cannot be seen or turned unless I tear it off! Please advise
HVAC Technician: HVAC Guru, HVAC TECH replied 2 years ago

Let me see if another tech has the manual wait for their reply

Ask Your Own HVAC Question
Customer reply replied 2 years ago
Just forget all this as I just called a local tech. to find the problem and fix!
Customer reply replied 2 years ago
please cancel this service as I will pay the $23 and that is all.
Please respond.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
25-PDVC/55-SHP10 upper auger not feeding. cleaned burn area
25-PDVC/55-SHP10 upper auger not feeding. cleaned burn area and hopper. Checked fuse in control switch and vacuum switch port. Upper auger not feeding. Lower auger turns. … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
74 satisfied customers
Goodman furnace mdl# gmh950904cxac combustion blower runs
Goodman furnace mdl# ***** combustion blower runs but will not close pressure switch. I have replaced the pressure switch. There are 2. 1 is -1.2 and connected to the heat exchanger. 1 is -.6 and conn… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My 8 year old furnace stopped working. its a dual zone
my 8 year old furnace stopped working. its a dual zone located in the upstairs attic space. i replaced the blower motor as it was making a loud clanking noise, not producing heat and giving a error co… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,748 satisfied customers
I have a ~10 yr old Natural Gas Forced air furnace that is
I have a ~10 yr old Natural Gas Forced air furnace that is stopping intermitantly. The code on the led it a code 3. This should mean combustion blower DP switches. Her ie is what I have checked. I che… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
my Armstrong gas furnace works fine ,recycles properly, except
my Armstrong gas furnace works fine ,recycles properly, except when the panel is closed over the burner area. Then it cuts out and goes into a short cycle mode and never gets heat over 68 degrees. Are… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
So I changed the fuse and got my furnace going, or at least
So I changed the fuse and got my furnace going, or at least power to it again. Back to my original problem. Igniter not working. Code blinking prove switch problem. Cleaned out flue, cleaned tube from… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Bryant 340MAV Furnace. It stopped working and was
I have a Bryant 340MAV Furnace. It stopped working and was flashing a 14. I can see that ignition actually takes place, and cleaned the flame sensor. Here is what happens: - Switch Power on. - Blower … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
the blower fan on my ao smith power vent water heater will
the blower fan on my ao smith power vent water heater will not turn on. It is an AO Smith Power House Power Shot Power Vent Water Heater. Model Number: FPSH 50 260. About 6 months ago it stopped worki… read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
I have a Lennox Merit series furnace (G40 I believe) that is
I have a Lennox Merit series furnace (G40 I believe) that is not heating. The thermostat is sending the signal and the furnace powers up after this, but after just a few clicks only the fan turns on. … read more
hvacdave84
hvacdave84
53 satisfied customers
Goodman GMNT100-4. 3 lights blinking error "Pressure switch".
Goodman GMNT100-4. 3 lights blinking error "Pressure switch". Vent blower will run for about two minutes, then turns off - furnace never ignites/heats. Tested Pressure Switch and is operable at least … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Re 2005 Frigidaire (Nordyne) 108 K forced hot air furnace.
Re: 2005 Frigidaire (Nordyne) 108 K forced hot air furnace. Model No. FG6TA100C-VB A Serial No. FGD050306885. Works fine but making 'humming' noise when blower door switch is depressed. When released … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Payne furnace with LED code of Pressure switch open
I have a Payne furnace with LED code of Pressure switch open when it should be closed. What do I need to do to fix and reset?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi - I have a c23-26 furnace and would like to clean it - how
Hi - I have a c23-26 furnace and would like to clean it - how would you recommend I go about doing this - I am fairly handy.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have Bryant 340MAV (90+ condensing) with a recurring problem
I have Bryant 340MAV (90+ condensing) with a recurring problem that is getting worse. It would start normally - induction motor start for 20-30 seconds then glow plug start, then gas valve opens and b… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
we have a heil furnace and when the blower turns on we hear
we have a heil furnace and when the blower turns on we hear a high pitch noise - what is that?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
HI, My mother inlaw has a free standing gas fireplace[Archguard..Optima
HI, My mother inlaw has a free standing gas fireplace[Archguard..Optima 45].The blower on this unit will not stop running regardless of whether or not the burner is on,could you tell me what the probl… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have Ruud Silhouette 2, 75,000 B.T.U. Natural Gas Furnace
I have Ruud Silhouette 2, 75,000 B.T.U. Natural Gas Furnace that will not turn on but makes a buzzing sound coming from the motor area. Could this be a bad startup capacitor or do I need to look into … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a Carrier Model 58SSC Upflow unit. Friday the fan wouldnt
I have a Carrier Model 58SSC Upflow unit. Friday the fan wouldn't work so I had no aircon. A local HVAC company put in a new capacitor and said my furnace was quite dirty - I should carefully dust the… read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x