I have a rheem prestige super quiet 2 stage 80 and a heat…

Customer Question
hi...i have a rheem prestige...
hi...i have a rheem prestige super quiet 2 stage 80 and a heat pump. had it about 7 years a never worked the way i wanted it. the furnace never seems to run on first stage. i have been digging and digging. it is the rpgr model. so what i think i know is. gas is now cheaper where i live and i don't like the heat pump heat. i have raised the lock out temp on the tsat as high as i can so now furnace runs most of the time, which is what i want, but it still runs at full speed, even though the tstat honeywell is set for 2heat/1 cool. (i have tried every setting on the tstat and no low speed ever kicks in.) one of the installation manuals says set jumper 7 for this feature, my board does not have a jumper 7. it only has 4 dips on main board and 12 on board that controls the fan. then i read that this furnace with a heat pump requires a fossil fuel kit which i have verified is installed, and in the instructions for that kit it says once heat pump is locked out furnace will only run as if it only has one stage. if i am reading that right, that sucks because i want it to run quietly at a low speed in the background so i don't hear the damn thing. so then i thought i could just over ride the fan settings but that would not reduce the burner and it might get too hot. then i thought well maybe i can just wire it like a straight a/c and not use the heat pump function and then it would work? (btw i can't find a drawing anywhere that matches my control board) help
Submitted: 2 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 hours by:
2/22/2016
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,077
Experience: Furnace, A/C and heat pump specialist.
Verified

Tell me what thermostat you are using and if you have it set to conventional or heat pump.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
vision pro 8000t...i have tried every setting. so right now, i disconnected the heat pump and wired it just 1 to 1, i.e. w to w, r to r, and furnace is working the way i want...but come summer? if you want me to rewire it back to try something i can do that too! thx
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Here is what I would do if you do not want the heat pump to work in heat mode.

At thermostat

Connect R to R and RC

Connect G to G

Connect Y to Y

Connect C wire to C

Connect the O/B wire to W

Connect the AUX wire to W2

The go to setup menu and select 9 (2 heat/1 cool multistage conventional) for function 0170 system type.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

At furnace connect the wire from W at thermostat to W and wire from W2 at thermostat to W2.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Let me know if this works for you.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
great, i will try that tomorrow...thank you have a great night!
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Sounds good.Let me know.

If you have further questions, please let me know.

Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.

To rate answer, please select one of the stars below.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
hi..so i wired per instructions...couple questions. 1. when i turn the fan on via the tsat it does not come on. 2. right now there are no wires from the heat pump connected to the furnace and thus not connected to the tsat. 3. blower still seems to be running on high. i read the installation instructions and they say i have to make sure jumper p7 is set correctly. here is link http://globalimageserver.com/fetchDocument.aspx?id=8277a916-c0da-4dcc-8496-54e49b68c6famy control board does not have a p7.
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

1. Set function 0180 to 0 and see if it makes a difference on fan.

2. The only wires that should be connected to heat pump right now are C(Common) R (Power) and Y (Contactor control)

3.The link you sent is for a later year of the same model furnace.In those furnaces, they combined the fan and main board together.I am attaching a link for the manual for your furnace.

The board should recognize you have a 2 stage thermostat and operate accordingly.If not, you may have to add an isolation relay.See page 21 for instructions and details.

http://www.mediafire.com/view/yj2drtaxytcs4l4/Rheem_GPR_GLR.pdf

Ask Your Own HVAC Question
Customer reply replied 2 years ago
thx...so i verified setting 180 is set to 0...no go.thanks for sending me the right manual.on the isolation relay, is that something i can go buy at Home Depot? I understand the wiring diagram just not sure where i get one
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Probably an appliance parts or hvac supply house.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
thx...what about the fan?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

That may solve that issue also if the 8000 is not communicating with the control board.I would think as long as you have an R and G at thermostat connected to R and G at furnace it should work, but those variable speed communications are a bit iffy. I know the Nest , which is one of the best on market, will not even work with a variable speed fan.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
ok, thx i will try that
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Let me know if this helps.

Ask Your Own HVAC Question
Customer reply replied 2 years ago
could you find what type of relay i need on the web and send me the link?
HVAC Technician: airheatman, HVAC Technician replied 2 years ago
Ask Your Own HVAC Question
Customer reply replied 2 years ago
thx hope this fixes it
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

Me too.Let me know

Ask Your Own HVAC Question
Customer reply replied 2 years ago
good afternoon super expert...so the isolation relay came in, the one you sent me the link on. i connected if per instructions of furnace. nothing was working, so i changed the tstat setting under 170 to 9. furnance started good thing, what i am trying to figure out now is how do i know the furnace is running on stage 1? blower sounds as loud as usual...AND when i try to turn on fan using tsat i get nothing. thx in advance
HVAC Technician: airheatman, HVAC Technician replied 2 years ago

You should see a difference between first and second stage.See pages 23 and 24 for explanation of how it should be doing

Ask Your Own HVAC Question
Customer reply replied 2 years ago
i have read that, so do i just sit at the furnace an hope it cycles through from 1st to 2nd? Also, what about the fan? And which is controlling which stage? seems like it's the tstat? which i am wondering if that is the problem with the fan etc...i replaced batteries but same results
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,077
9,077 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
amana air command high efficiency 95 IIQ GUAVA gas furnace
My amana air command high efficiency 95 IIQ GUAVA gas furnace variable speed blower won't advance to high stage. I've replaced the integrated control module.… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a rheem classic 90 plus w/ contour comfort control.
I have a rheem classic 90 plus w/ contour comfort control. it is being controlled by 41-24312-04 contour modulating 7 day thermostat. it has no light and is difficult to program! what can i replace it… read more
airheatman
airheatman
HVAC Technician
9,077 satisfied customers
I installed a Rheem RGGE07EMCKS down flow 2 stage gas
I installed a Rheem RGGE07EMCKS down flow 2 stage gas furnace ,the furnace is new but 5 years old , with a non communicating 2 stage thermostat , upon firing it up I get a d1 code ," No shared data " … read more
airheatman
airheatman
HVAC Technician
9,077 satisfied customers
I have a new ac unit 2 c 2 h. The installers didn't have the
I have a new ac unit 2 c 2 h. The installers didn't have the right 2 stage thermostat so they put in a temp and sent me the Braeburn 5220 later. They kind of burned me so I had to install it myself. I… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have trane gas fired furnace 2 stage I'm assuming. Old
I have trane gas fired furnace 2 stage I'm assuming. Old American standard thermostat 606 for ac/heat wiring at star is r w1 w2 g1 y1. I would like to change it because it does not follow the set poin… read more
airheatman
airheatman
HVAC Technician
9,077 satisfied customers
A couple days ago you helped me identify a bad heat pump
A couple days ago you helped me identify a bad heat pump sequencer, but now I need some help deciphering the model number. It is a Lennox heat pump with 3 sequencers. 2 are original and I want to just… read more
airheatman
airheatman
HVAC Technician
9,077 satisfied customers
A HON T874D 1074 & INSTALLING A HON RTH111. WHHERE DOES THE
i AM REMOVING A HON T874D 1074 & INSTALLING A HON RTH111 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a lyric t6prowifi 2 stage thermostat that is lockedin
I have a lyric t6prowifi 2 stage thermostat that is lockedin at the screen in the cool mode .I am unable to unlock the screen to change it to the heat mode. I am unable to unlock the screen.can you he… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Goodman furnace code F3, thermostat was broken have replaced
Goodman furnace code F3, thermostat was broken have replaced but furnace won't fire … read more
airheatman
airheatman
HVAC Technician
9,077 satisfied customers
I have a Armstrong furnace gas converted to propane. I have
I have a Armstrong furnace gas converted to propane. I have a 140000 btu hot water coil in the hot air duct above the furnace. I just installed the furnace but have not got to all the hookups yet and … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
E. Lennox thermostat 49m series problem. Heat setting cannot
lennox thermostat 49m series problem. Heat setting cannot be changed upward, set at 51 degrees, can be changed lower, but not higher. Arrow icon on screen points downward. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a question. I was sold a Lennox 4T Variable speed
Hello, I have a question. I was sold a Lennox 4T Variable speed 2-stage gas heating and cooling system with 2-stage thermostat to support. That is the wording from my proposal and agreement … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
What should the cycles per hour setting be for a trane xl802
What should the cycles per hour setting be for a trane xl802 thermostat that is only wired for single stage heating on a trane xl90 2 stage furnace? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
What do I have to do to change a communicating thermostat to
what do I have to do to change a communicating thermostat to a regular thermostat. the unit is two stage heat and two stage cool… read more
airheatman
airheatman
HVAC Technician
9,077 satisfied customers
I have a Trane XL1200 model nr YCY030F1M0AA SER. L443YSH1H
I have a Trane XL1200 model nr YCY030F1M0AA SER. L443YSH1H date of MFG. 10/96. Combination heating and cooling unit. I can not get the unit to run in Auto and no heat comes out. It is an outside unit.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We recently installed an outdoor boiler system. How can we
We recently installed an outdoor wood boiler system. How can we set up our themostat to run blower only for the wood system, then kick to our electric furnace/HP if it gets to cold (wood runs out)? It… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a carrier MVP58 furnace. I would like to have it always
I have a carrier MVP58 furnace. I would like to have it always in low-heat nmode (i.e. not adaptive heat mode). I have set the proper dip-switch (#2) in the on position but there is no change in behav… read more
DennisMooreAC
DennisMooreAC
Service Engineer
Associate Degree
76 satisfied customers
can I use a Carrier edge TP-PRH, TP-NRH performance series
can I use a Carrier edge TP-PRH, TP-NRH performance series thermidistat for a carrier comfort 92 forced air gas system?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x